Question about Carrier XHB123D X/Y Series Heat/Cool Air Conditioner
Slow gas on Carrier 8000 58TUA?
We are getting repeated lockouts from the flame sensor. I've cleaned it well and all the connections are clean and tight. The ignitor is plenty hot, too.
It seems to me that there is QUITE a lag between the gas valve solenoid "click" and the first flash of flame...as if the gas had to travel a long way to get to the burners.
Therefore the flame sensor is almost ready to "time out" as the flame first hits it. It shuts down within a quarter second of the flame wave getting over there. It almost never catches on the first attempt, often does so on the second or third, and sometimes does not at all.
We have an adequate municipal supply, and the furnace gas piping is factory standard.
Can I adjust the flame sensor time to add a couple of seconds?
Can I increase the gas pressure a teensy bit to get it there faster?
Can I adjust the gas valve timing to open a couple of seconds sooner?
Could it ACTUALLY be the flame sensor? Hate to pay to replace it since it seems to work well if the flame hits it for one second.
Thanks!
Saw this happen one other time where the regulator at the outdoors gas meter was faulty and not supply the correct gas pressure. You may need to have the gas company come out and check the pressure at the meter. Also, check to make sure no other gas appliances are running..ie..water heater, gas logs, stove, etc. and then start up the furnace and see if it will start up properly. This would also indicate a problem at the gas meter...ie..gas pressure.
Posted on Dec 21, 2008
My adp cuhn-60a-2 sparks an lights burner ok, burns for only few seconds an shuts down burner, repeats this three times an whole unit shuts down?
You are describing the typical issue for a problem in the 'flame rectification' circuit. Turn the powere off. Find the flame sensor, it will be on the opposite side of the furnace from the spark ignition device. Carefully remove the sensor and clean with fine sandpaper, then clean the wire connector on the end of it if so equipped, then follow that wire all the way to the circuit board, remove the wire connection and clean it and reinstall. Many times that solves the issue.
Some systems utilize the spark ignition electrode as its own flame sensor. IF there is no separate flame sensor, perform the above task on the ignition device instead. Be careful NOT to bend the probe, crack the ceramic insulator or reinstall it malaligned. Its location in the pilot flame is critical. Slight relocation by improper handling will render it unable to ignite the pilot gas.
There may be another issue as there are many things that cause ignition lockout, but this is the first thing to do to eliminate the situation you've described.
If you are unsure of performing this and ANY minor maintenance to a gas fired appliance, abandon the idea and call a qualified service tech to proceed.
Dec 29, 2014 | Heating & Cooling
Furnace lockout
Change the flame sensor, check the connections on the sensor are tight , check pressure switch , check air filter is clean .
Jul 05, 2017 | Heating & Cooling
Ignition lockout on carrier furnace. How to get furnace running again
It locks out because their is a problem with the flame ignition after it tries to light several times it locks out. Could be a flame sensor or bad igniter. Could be other reasons but these are the most likely. You can reset it by turning the power of and back on again
Apr 22, 2013 | Heating & Cooling
Carrier Weathermaker 8000 Furnace Flame Surges on start up
The fuel is controlled by the gas valve, the amount of gas is controlled by the regulator, I would verify that the inlet gas pressure is within the limits of the gas valve/regulator. The surging is likely the fault of the regulator and could be as simple as a spec of something in the orifice that allows gas pressure on the top of the gas regulator diaphragm. With the surge there must be an accompanied change in gas pressure at the gas valve outlet to the burners, use a "U" bend manometer to verify as they are the most simple and accurate and react instantly with no "averaging" software to wonder about.
Mar 16, 2017 | Carrier Heating & Cooling
Rheem Intelli-vent intermittently goes in lockout mode
Rheem does not post service manuals.
However AO Smith has posted relevant service manual:
http://waterheatertimer.org/How-to-troubleshoot-gas-water-heater.html#intellivent
Have you cleaned the air intake located under combustion chamber, and inspected for broken glass vial?
Rheem FVIR system uses glass vial that breaks if combustion air is slowed, and resulting combustion causes slow-moving venting of hot gasses, causing overheating that breaks glass vial.
http://waterheatertimer.org/How-to-repair-Rheem-FVIR.html
Check gas pressure.
Replace gas control valve:
http://waterheatertimer.org/pdf/How-to-replace-water-heater-gas-valve.pdf
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Oct 09, 2012 | Water Heaters
Flame does not always stay on after ignition, sometimes it does and when it doesnt you open and close the door for re- light ?
Opening and closing the door will reset the ignition sequence, do not do this repeatedly as you could cause a build-up of unburned gas in your heat exchanger and damage it. Instead verify that your ignitor is glowing, then see if the burner lights and make sure the flame carries all the way down to the bottom of the burner. If the flame stalls halfway or doesn't make it all the way to the bottom in 4 seconds after 3 attempts you will experience an ignition lockout, a safety feature built into your ignition module. If this is the case your burner needs to be cleaned and serviced, have a professional do it.
If the flame is reaching the bottom of the burner but still going out after about 4 seconds then you have a dirty/broken flame sensor. You can attempt to clean your flame sensor by removing the screw that holds it into the burner. With it removed it will look like a metal rod going through some ceramic, clean the metal rod part with a wire brush or emory cloth (fine sandpaper). Replace the flame rod and try again and see if the burner stays on this time. If it still goes out your burner needs to be serviced by a licensed technician.
Feb 11, 2011 | Baxter BXA2G Stainless Steel Gas Single...
Furnace will start and sequence fine run for five minutes or so then the flame cuts out....miller type furnace put a new board in last year so now it cycles three times and goes into soft lockout.....
Clean the flame sensor.
If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 19, 2010 | Heating & Cooling
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
Goodman Heater kicks on but then it goes off as the burner is trying to ignite. Then come on and goes out after a few times 3 to 5 times, after awhile it will stay on... Then start all over again after it...
the gas furnace has a flame sensor when the flame kicks on and the flame sensor doesn't sense it it will shut off as a safety precaution and try three times to start again and then will lockout what you need to do is find the flame sensor it usually looks like a metal rod about 1'' -1 1/2'' long in a porcelain cylinder. it looks kind of like a mini screwdriver. You have to clean the metal rod with sandpaper or sandcloth the flame sensor actually conducts electricity with a flame cleaning them usually works make sure you check your connections especially ground.
Oct 30, 2009 | Goodman CLQ36AR49 Air Conditioner
Carrier XHB123D X/Y Series Heat/Cool Air Conditioner Logo
219 people viewed this question
Top Carrier Heating & Cooling Experts
Bill Long
Dennis Boxerman
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others