Question about Goodman CLQ36AR49 Air Conditioner
Goodman heatpump. Crazy pressure in heat mode
I have an R410 Goodman heatpump. It works just fine in AC mode. 300 on high side and 105 on low with 70 degrees outside. When I try to turn on the heat pressure on BOTH sides goes beyond 600 and then overload protection kicks in and compressor shuts off. Is it a bad reversing valve? Heat pump is only 6 months old.
  • Stephen Evans May 11, 2010
    Sounds like it. Goodman has a nationwide 5 yr parts and labor warranty and lifetime on the compressor. Call who installed it so you dont void your warranties.
  • Ken Bledsoe May 11, 2010
    Sure sounds like it to me. ken
Check the TXV valve on the outdoor unit, it could be stuck closed. We have been experiencing the same problems with the 410 systems and the TXV was the culprit. Good Luck
Posted on Feb 10, 2009
No suction pressure at condenser test port
i would suspect the valve on suction side not open. if the other system failed on a burn out you could have a blocked dryer or orfice at coil.
Apr 20, 2014 | Goodman CLQ36AR49 Air Conditioner
Low to zero pressure on low side test port
150 is low for high side pressure. may have to add more r-22 to system. if you had a blockage high side pressure should be higher. have you turned both service valves at condensor ccw completely?
Apr 20, 2014 | Goodman CKL42AR42 Air Conditioner
Charging chart missing. Goodman 4-ton AC (model CK 49-18) What are the high and low suction pressures at 90 degrees F?
Hello, if this is a R-22 unit your low side should between 70-75 psig and high side should be between 225-230psig. But keep in mind always measure the superheat if it is a fixed orifice and subcooling if it is a txv unit
Jun 07, 2011 | Amana Heating & Cooling
I am working on a M # GPG13420901AB. This is a 3.5 ton package unit that replaced a 3 ton package unit on 1700sq/ft single level home. Old unit was working fine but was replaced when the home was...
It sounds like you are low on charge. I think you have a thermostatic expansion valve and you need to check the subcooling, you should have 12 to 15 degrees at 95. At 95 degrees your head should be about 280# for a 12 or 13 SEER unit or higher depending on the effeciency. At 78 to 80 degrees indoor depending on the humidity, that is normal. The valve will open to try to fully feed your indoor coil and it sounds like your head pressure is to low to force enough refrigerant thru the coil.
Aug 16, 2010 | Goodman Heating & Cooling
High suction press (98psi), normal head press (140psi); full sight glass;low super heat (10 degrees);normal subcooling (13 degrees) new txv, new evaporator, new condensing unit 70 degree air from vents ...
lower fan speed.....and double check head pressure, sounds very low!!! should be around 250-275.....also make sure the return air grill is large enough.
Aug 09, 2010 | Goodman CLQ36AR49 Air Conditioner
I have a 3 ton Rheem heat pump that calls for about 225# pressure on the high side at about 40 degrees outside with tstat set at 70 degrees indoor.... I am confused as to why both sides of the manifold...
Where are you connecting the gauges? It sounds like you have both gages on the high pressure side. You can't hook the suction gauge to the Big line on a heatpump because that is high pressure in the heating mode. There should be another tap that says low side or low pressure, that's where you hook the suction gauge. As for adding more refrigerant, I wouldn't do that until I measure the subcooling.
If you charge it in heating unless you weigh it in you want about 10° to 15° subcooling. Then this summer you need to check the subcooling at about 95° outdoor ambient then charge it to about 10° to 15° subcooling in the cooling mode and that should be the correct charge.
Feb 15, 2010 | Heating & Cooling
Heatpump A/C not working
First,Turn on the heat cycle (Not Emergency)and see if the outside unit come on,If not,and you don't have low voltage outside,Go to the inside unit and test the transformer,If you have low voltage from the transformer but not outside,It is the low voltage wires,If you don't have low voltage from the transformer,It's the transformer.If you have low voltage outside when in heat mode,but the unit won't come on,It's the contactor.Let me know if you need more help.
Please take time to rate this fixya
May 13, 2009 | Goodman CLQ36AR49 Air Conditioner
5 year old Goodman CKJ48-1A Condenser Unit
The high side psi. should be at least around 100# ps more than the low side psi. The low side psi sounds ok, but the high side tells you the problem is the outside condenser is plugging up! Go to an ac supply house,and buy a gallon of coil cleanner and dilute it and fully clean the outside condenser coils ,after it's cleaned ,check the charge now!
Sep 07, 2008 | Goodman CLQ36AR49 Air Conditioner
Goodman CLQ36AR49 Air Conditioner Logo
531 people viewed this question
Top Goodman Heating & Cooling Experts
Paul Carew
Tim Whalen
christian nielsen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others