Thanks to Wellinka have sorted timer issues re heating off periods so thanks for that.
Have a problem seperating the hot water/heating with the CM921 and a Baxi duo tec 28 He. Can only get hot water when heating programmed on so nothing during night if needed. Any useful suggestions appreciated please.
CremeStout
  • 123 Answers
SOURCE: Honeywell ST6400C programmer doesn't switch off
Since you have three on/off timing modes could there be an overlap in the times?
The wires in the unit might be crossed. (don't always assume the contractor who wired maintained the correct colors , I have a friend who blew out a heating pipe because when a replacement motor valve was installed it was never wired right and the plumber assumed the colors were correct so no overtemp shutoff created steam in PVC pipes, OPPS)
There fore maybe one is still coming on. Do you have more than one heating zone? IF so see below
I guess the main question is why manually turn it off? why not use the program.
I will assume your heat is know as forced hot water heating. My house is multizoned however when the zone calling for heat turns off (zone valve closes) I installed a bypass valve in the lowest zone in the house, and reduced the circulator low shut off temp to 130 F which means even though the heat isn't on my circulator will continue to run dumping this excess heat in the lowest part of house to rise through house. (the spring loaded water valve allows the heated water to flow into this zone )We do have two thermistats. And even though the lowest one is not calling for heat the radiators are hot when the excess is dumped into this zone. So investigate and see if your system might be similar. (multizone).
Investigate your wiring, reprogram, replace any battery backup.
Posted on Dec 19, 2007
  • 579 Answers
SOURCE: loss of temperature control
Is the heater staying on all the time? Most likely cause of themostat trouble is the sensor. Try to find it and measure its resistance at different temps to verify the trouble.
Posted on Dec 31, 2007
  • 16 Answers
SOURCE: cannot get central heating working,for honeywell ST6400 programme
with y plan 3 connections on programmer HW on HW off CH on HW on to cylinder stat then HW call to Orange on Mvalve to power boiler and pump HW off to grey wire on Mvalve to close hot water CH to room stat common then heating call to white on Mvalve
Posted on Aug 17, 2009
  • 55 Answers
SOURCE: Honeywell thermostat CM921, how to set the heating for a 6.30am??
if you have a programable tstat you need to go through the settings for each day and time. usually the buttton will say prgm or program sometimes it will be set try to get into the settings menue and then you can adjust times
Posted on Sep 13, 2009
  • 36 Answers
SOURCE: boiler is a baxi control for heating is honeywell.
this will be your diaphram inside your divertor valve.
the one that looks like a spaceship.
it will e split.
Posted on Jan 31, 2010
How do I set the central heating programme
its a lot hope ur ready for it but here you go. although you listed a LS112 I could not find any thing on it but maybe you meant LP112 so if it is what you need good luck..
Manual abstract: user guide DRAYTON LP112
Detailed instructions for use are in the User's Guide.
[. . . ] Common
Neutral
Spare
Earth
Live
On
MAKE
MODEL
Off
Lifestyle
SINGLE CHANNEL
Timeswitch
for heating OR hot water
TIMESWITCH TERMINAL COMPARISONS
Lifestyle
SINGLE CHANNEL
Timeswitch
DAY-TO-DAY VARIATIONS Cont. . . Over-riding the program
THE LP711 7-DAY ELECTRONIC TIMESWITCH Cont. . . If the engineer hasn't set your timings for you, your programmer will work with a standard program that has been set at the factory. If this doesn't suit you, it's very easy to change it ­ when you've read this introductory section, simply go to the section that contains your programmer model.
THE LP112 24hr ELECTRONIC PROGRAMMER Cont. . . [. . . ] Now plug the Lifestyle unit into the wall-plate and tighten the securing screws. FITTING A NEW WALL-PLATE The ideal location is 1. 4m above floor level, with reasonable lighting, good access, no condensation, no extremes of temperature, and a supporting surface that fully covers the back of the unit. Position with 70mm clearance to the right, 25mm above, and sufficient room to access the securing screws underneath. Fix, with terminals at the top, either direct to a flat wall using wall plugs and No. 6 x 1" (25mm) woodscrews, or on a flush mounting single conduit box type UA1 (BS4662) using M3. 5 x 14 bolts. DO NOT USE A SURFACE MOUNTING BOX.
USING A DRAYTON SIMP-L-FIT, ALTHOUGH NOT NECESSARY, WILL MAKE THIS INSTALLATION EASIER.
If the engineer has set your program and timings ­ you won't need to do anything else. Just keep this guide in a safe place for future reference.
I Press SET?, and you'll see OFF1, the end of your first central heating period. Adjust this in the same way, press SET?, then repeat the procedure for ON2, OFF2, ON3 and OFF3.
Connection Charts
Arrowed numbers relate to the junction box. DAY-TO-DAY VARIATIONS Sometimes you might need to change the way you use your system temporarily ­ perhaps due to an exceptionally cold day. Here's how to do it ­ without affecting the timings in your program.
SWITCHING ON 1 ­ start of first timed period OFF 1 ­ end of first timed period ON 2 ­ start of second timed period* OFF 2 ­ end of second timed period* ON 3 ­ start of third timed period OFF 3 ­ final switch-off of the day
STANDARD PROGRAM MON-FRI 6. 30am 8. 30am 12. 00pm 12. 00pm 4. 30pm 10. 30pm SAT-SUN 7. 00am 9. 00am 12. 00pm 12. 00pm 4. 00pm 11. 00pm
I LP112 ­ a 24hr program, with linked central heating and hot water on for up to 3 heating periods each day, and every day the same. I LP241 ­ a 24hr program, with central heating and hot water working independently for up to 3 heating periods each day, and every day the same. I LP522 ­ a 5/2-day program allowing for different timings at the weekends, with central heating and hot water working independently for up to 3 heating periods each day. I LP722 ­ a 7-day program allowing for different timings on each day of the week, with central heating and hot water working independently for up to 3 heating periods each day.
Set the hot water I When you press SET?after setting OFF3 for the central heating, the display will ask `SET HW PROG?'.
*Thermostat Key
C H S N E L Common Call for Heat Satisfied Neutral Earth Live
Wiring Colour Codes
GR Y BK BL BR RD W OR YG Grey Yellow Black Blue Brown Red White Orange Yellow/Green
STANDARD PROGRAM 6. 30am 8. 30am 12. 00pm 12. 00pm 4. 30pm 10. 30pm I Press YES, then set your times in the same way. Remember, in this mode you can have different times to your central heating if you wish. after setting OFF3 for the hot water, the programmer will return to normal operation.
Switching on and off On the front of the timeswitch is an Advance button. It allows you to switch your system on or off, irrespective of the program. Press Advance to switch it on, and it will stay on until the end of the next OFF period. Turn it off, and it will stay off until the beginning of the next ON period.
THE LP522 5/2-DAY ELECTRONIC PROGRAMMER LP522 ­ a 5/2-day program allowing for different timings at the weekends, with central heating and hot water working independently for up to 3 heating periods each day. If the timings haven't been set for you, then your programmer will still be on the factory-set standard program. This means that central heating and hot water will operate together, with the same timings for weekdays and different ones for the weekend. But it's easy to make changes, and have heating and water working independently ­ just follow the instructions. [. . . ] SETTING THE CLOCK
MON TUE WED THU FRI PROG?
The clock in your programmer has been set at the factory, and automatically accounts for British Summer Time. button until you see SET CLOCK?.
Spring-Return 2-Valve System
ROOM THERMOSTAT
RTS 1&2 RTS 4, 5&6 ETS 1 ELN N LN E 4 C L 1 1 H 3 3 2
Set weekday hot water I When you press SET?after setting OFF3 for the central heating, the display will ask `SET HW MON to FRI PROG?'.
I Press YES, and you'll see ON1, the start of your first central heating period. If the ­ and + buttons are held down, the time changes in 10-minute steps.
PROGRAMMER
NL1234
CYLINDER THERMOSTAT
SCH 2C1
SET TO 'P'
HTS 3
3124
5
#- LINK L-1 FOR 230V OUTPUT
21
64
8
6
Set the hour I Press SET?, and you'll see OFF1, the end of your first central heating period. [. . . ]
Oct 01, 2018 | The Audio Players & Recorders
Setting the programme
try this model instead...
[. . . ] Common
Neutral
Spare
Earth
Live
On
MAKE
MODEL
Off
Lifestyle
SINGLE CHANNEL
Timeswitch
Lifestyle
SINGLE CHANNEL
Timeswitch
Connection Charts
*Thermostat Key
Wiring Colour Codes
ROOM THERMOSTAT
PROGRAMMER
NL1234
CYLINDER THERMOSTAT
SCH 2C1
SET TO 'P'
HTS 3
3124
5
21
64
8
6
Oct 01, 2018 | Heating & Cooling
WHEN SET FOR HOT WATER RADIATORS ARE HEATING ALSO
there should be a seperate adjustment for hot water and for central heating, if they are on timer that is. If you are switching on at the boiler / combi check for the seperate switches
Jun 08, 2016 | Cars & Trucks
Hi, I am having problems with the timer that controls my boiler. It is a 'Lifestyle LP522'. The hot water is set to come on in the morning for 4 hours and again at 4pm for 3 hours. The heating is...
then there must be a problem with the programmer as the boiler thermostat will call for heat only if the programme is on try setting the water side to 24 hrs it won't cost any more to run , but will prove if programmer is working .
Mar 07, 2017 | Heating & Cooling
How do i set the heating/hot water timer on the LP112-24 acl controler ?
The instructions are available here: http://www.draytoncontrols.co.uk/Complete_LP_Installation_User_Instructions.aspx I hope I have been of help but please do not hesitate to ask if you have any further questions. Set the central heating Press the YES button, and the display will ask 'SET CH PROG?'. Press YES and you'll see ON1, the start of your first central heating period. Adjust it in 1-minute steps using the - and + buttons. If the - and + buttons are held down, the time changes in 10-minute steps. Press SET?, and you'll see OFF1, the end of your first central heating period. Adjust this in the same way, press SET?, then repeat the procedure for ON2, OFF2, ON3 and OFF3. Set the hot water When you press SET? after setting OFF3 for the central heating, the display will ask 'SET HW PROG?'. Press YES, then set your times in the same way. Remember, in this mode you can have different times to your central heating if you wish. When you press SET? after setting OFF3 for the hot water, the programmer will return to normal operation.
Feb 19, 2011 | Heating & Cooling
Just bought a house and it has a grundfos timer/pump attached at the hot water tank. I have no hot water and the timer doesn't turn (as I've seen other timers do). Is it supposed to turn so that the...
Grundfos is a sealed unit and not a repairable item.
The timer dial should turn.
And pins located around dial control ON-OFF functions as timer dial rotates.
Does the receptacle have power?
If receptacle has power, and Grundfos is not working, then it is broken.
Grundfos manuals for UP series pumps do not show breakdown or parts list of any kind.
http://www.us.grundfos.com/web/download.nsf/Pages
Bigger question:
Why don't you have hot water?
Is water heater functioning?
Water heater is a separate appliance from Grundfos pump.
Grundfos pump circulates hot water from tank into the lines so there is no waiting for hot water ... but hot water heater should still make hot water.
http://waterheatertimer.org/Water-heater-recirculation-system.html
Add a comment about water heater if that is also a problem.
You could have 2 problems, and water heater is main issue.
For do-it-yourself electric water heater repairs:
http://waterheatertimer.org/6DIY.html
Nov 20, 2010 | Grundfos The UP1510B5ATLC 125th HP 1...
User guide needed for old Honeywell programmable heating control
It depends on your system some will only work with hot water on and heating do you have two zone valves?
Jul 18, 2017 | Honeywell TH4210D1005 Heater
Off - Service Due = no hot water what am I supposed to do?
Called the Gas man... fiddled with some buttons, over-rode the system. All fine now.
Sep 29, 2009 | Honeywell Electronic Programmable...
Cannot get central heating working,for honeywell ST6400 programme
Jun 13, 2009 | Honeywell Programmable Thermostat Heater
Heating & Cooling Logo
Top Honeywell Heating & Cooling Experts
Paul Carew
Paul
Paul
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others