Question about Honeywell CT87B ROUND HEATING&COOLING MECHANICAL THERMOSTAT - WHITE Heater
Ruud furnace starts up burners shut down after 30 60 seconds
The furnace ignites and the burners work for various times, the first time was a bout 20 seconds, I cleaned the thermo coupler and the burners stayed on for almost a minute before shutting down.
  • 148 Answers
Check the flame sensor it could be carboned up
Posted on May 02, 2009
Having problem with lennox furnace Model ML193DF090P48C-02.Furnace has been working but now and getting worse furnace will kick on 20 seconds or so but nothing.Igniter does not come on.When it finally
Usually when your flame sensor gets dirty, the igniter and burner come on for approx.15 seconds, then shuts down. After 3 tries it will lock the furnace out. You have to shut the power off to the furnace then turn it back on to reset it. You need to turn all the power off to the furnace and remove the flame sensor, clean it with some very fine steel wool and put it back in. Be careful not to handle the Sensor (metal) part with your fingers. Turn the power on and set your thermostat so that it will call for Heat. That should fix, it if not you may need a new flame sensor.
Mar 16, 2014 | Heating & Cooling
Ruud furnace troubleshooting
check that elements are intact and getting voltage
Nov 14, 2013 | Heating & Cooling
Ruud 80 plus furnace
Make sure you give it time. Gas furnaces ignite first and then the fan comes on. It will run for a while to heat the exchanger first. If the fan comes on with the heat it will blow cold initially. The fan also continues to run after the burners shut off to expel the existing heat in the ductwork
Oct 19, 2013 | Heating & Cooling
Have a ruud achiever 90 plus furnace. the flame goes out after the igniter quits. any ideas
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Ruud UBHC Air Conditioner
My furnace comes on and heates the house for about
Make sure filters are clean . if they are stopped up the unit will over heat. Lets start there. Russ
Mar 22, 2010 | Ruud UBHC Air Conditioner
Gas furnace, main burner ignites the other 2 don't. then shutdn.
Between the burners is a small rail in the pressed steel where the flame runs across to light the other burners and it sounds like there is dirt or debris in the step over rails causing the problem. You will need to use some compressed air on those rails to clear them out. Once the rails are clear the other two burners should ignite right away.
Dec 21, 2009 | Heating & Cooling
Lennox furnace 17 yeanrs old. flame comes on and the shuts down sometimes right away some times in a few minutes. We have the furnace go down to 58 at night. It takes all day to get back to 67.
Sounds like a dirty flame sensor.
Also 9 degrees is a large swing to recover. Most specialist will advise no more than a 5 degree set back, otherwise recovery time eliminates any savings you may achieve.
Dec 05, 2009 | Dayton (3E407) Heater
Ruud furnace Model URKA A030jK08 Code opt 589
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Nov 23, 2009 | Heating & Cooling
Gas burners ignite then shut down
I need your model number to be sure, but I sounds like a flame sensor. If you have a hot surface ignitor(orange glow device) then in the same area there should be a small single wire sensor that sits in the flame Remove and wire brush the end and try that.
If you have a circuit board count the fast and slow flashes after it fails 3 tiimes and this will make a code
Nov 19, 2008 | Ruud Matching Split Air Conditioner
Heating & Cooling Logo
175 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
Paul Carew
vance jones
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others