Furnace trouble Working on a Carrier sx from 1990, has three wire bi-metal pilot with spark and 100% lockout on the spark module. Homeowner says it only fails in cold o.d. temps (less than 35 degrees). Home owner finds unit off and silent, resets 120v and unit re-lights and runs. Don't know what parts have been replaced so far but it looks like a new spark mod. and the pilot was clean but I cleaned it again. Limit switch looks old but I think limit failure would cause the blower to run. Any ideas?
    Habit-Forming:
    New Friend:
  • 117 Answers
How long unit runs after reset .If limit tripped blower motor will still run and if that's the case you might have a bad heat exchanger
Posted on May 25, 2017
2 Suggested Answers
SOURCE: Working on a Carrier sx
Check the heater relay on the control board found in the blower part of this furnace. It's found in a steel enclosed box
I'm having the same problem currently. I now have the blower running constantly set the thermostat to on not auto. until the part arrives
This has happened before but this time the relay has gone cloudy from sparking on and off. Tapping the relay may help just be careful when you have bypassed the door switch.
Good luck
Posted on Dec 21, 2008
How do u light the oven
GAS OVENS
The spark igniter tip is dirty (can clean it with either a little wire brush or a piece of fine sandpaper).
2) The Pilot flame is too low, and the tip of the igniter is not in the flame good enough. (the flame acts as a circuit when it touches the tip & completes the circuit).
3) The spark module is no good and needs to be replaced.(But 1 & 2 are your best bet).
spark module does not sense the flame when it's on. The spark igniter is also the flame sensor which provides feedback to the spark module.
Make sure the igniter is properly aligned with the burner lighting holes and it is clean. All lighting holes must be clean too. You can enlarge them using a drill bit one size bigger.
If it would not fix the problem, replace the bake burner and the igniter.
There is a small chance for the spark module itself to be bad as well.
The oven safety valve
(also called the gas valve) is the part that ensures that gas is not released until the igniter has reached the correct temperature needed to ignite the gas. While this part can fail, it is uncommon. If the hot surface igniter does not glow you should first verify that you have voltage to the circuit. This is a live voltage check and should be performed by a qualified person. If voltage is lost at the valve terminals then you should verify the continuity of the bi-metal in the valve using a multi-meter.
Apr 22, 2015 | Ovens
Tip
Heater check out list for heater failures
Almost all furnaces built after 1978 have intermittant type pilots.
Ca banned them requiring electronic spark or hot surface ignitors, followed by induced draft motors, pressure switches or centrifigal switches that "prove" a induced draft exists, allowing the pilot sequence to commence.
electronic spark type units have a high voltage low amperage spark that is AC. Fire rectifies electricity that passes through it meaning AC becomes DC ! Fire is a terrible conducter however as a result , the DC signal is only milliamps/volts signal strength. the DC prescence is proof a flame exists for pilot, and safe to commence to mainburners.
As long as pressure switches stay closed, safeties and limits stay closed
and the DC signal to the ignition module is not broken, the furnace will run.
The normal sequence of operation is upon a call for heat from the thermostat a 24 volt signal is sent to W white (heat circuit) at the low voltage terminal board on furnace.
from there depending on unit and age the heat circuit may include a circuit board, but it still has the typical limits and safetys reqired for operation
its just not using electromechanical relays to control fan and induced draft motor etc.
for the induced draft to begin ,all limits, safetys in heat circuit must be closed.
induced draft begins and a proving switch, either pressure or centrifigal close allowung the pilot to begin, a spark or hot surface ignitor is energized and a pilot flame established,modern types use flame rectification to prove a flame, older Carrier, Payne,types have a 3 wire switch in the piloyt assembly that is a bi metal that expands and contracts clicking open and shut, allowing pilot or main burners, depending if cold or hot.
pressure switches are attached with tubing to the induced draft wheel housing and sense pressure differential and close upon induced draft running, the orifices that the tube attaches to on induced draft housing often plugs or is restricted causing pressure switch to fail to close, or waver on open and close , open , close, .
if you can run the fan in the on postion , you have both high and low voltage to the furnace.
if you dont have fan control check power, breaker , fuses.
on Dec 04, 2009 | Heating & Cooling
I have a carrier supersavior 58ssb060-cc furnace.
i believe this furnace has a bi metal pilot safety. it may be stuck in the run position. tap the pilot switch lightly with the fat end of a screw driver and see if it resets.it is under the burners.3 wires and a tube go into it
Oct 15, 2014 | Heating & Cooling
Our Kenmore Elite Gas stove has 1 pilot that won't light when the knob is turned. How do we fix this.
The oven burner igniter
commonly known as the hot surface igniter is used in modern gas oven burners to open the gas valve and to ignite the gas. As the igniter draws electric current it will heat to a high temperature and glow, as well as cause the bi-metal in the oven safety valve to warp and open the valve releasing the gas to be ignited. This sequence normally takes about a minute. Igniters come in both flat and round styles and are very fragile. If the burner does not light then you should check the igniter first. If the igniter does not glow at all, then check for power to the circuit. This is a live voltage check and should be performed by a qualified person. If power is present then the igniter may be open circuit and can be checked for continuity with a multi-meter. If the igniter is glowing, but the burner is not lighting, the igniter may be weak and still be at fault because it requires a certain amount of current draw to open the valve. This check requires the use of an amp meter and should be performed by a qualified person. If the igniter is defective then it must be replaced.
GAS OVENS 1)The spark igniter tip is dirty (can clean it with either a little wire brush or a piece of fine sandpaper).
Apr 12, 2014 | Kenmore Elite Stainless Steel 40" Dual...
I posted a question about the Ultra sx 90 (Armstrong) furnace not lighting and the combustion blower keeps running. I did clean the flame sensor and no change. I also changed the spark control moduleas...
When this problem has occurred on my York furnace, the temperature limit switch had to be replaced. You may have checked this in your troubleshooting but if not, it's worth a try
Jan 19, 2013 | Fasco Heating & Cooling
Have Goldstar Model R1804h ac/heater window unit when turned to heat blows only cold air what is easiest thing to check and purchase first.
If your thermostat is working on the Heat cycle (listen for "click" when turned up and down on Heat), then your heating coil assembly is probably bad. The heating coil is in series with a Fusible Link and a Bi-metal thermostat, if any of these three fails, there will be no heat from the coils.The Link and Bi-metal Thermostat are made up as part of the heater coil assembly.
Jan 18, 2013 | Goldstar Heating & Cooling
I have a Carrier model # 58MXA080-F-15112. I think my furnace is 30 plus years old. it isn't heating properly. The blower turns on and sometimes the flames come on, but sometimes they don't. As...
A 13 code means the furnace cycled on limit more than three times consecutively and is in a lockout for 3 hours. A 14 is ignition lockout. An ignitor does not intermittently quit working. I'm the service mgr at our shop, and I know that particular furnace model has a service bulletin out on bad secondary heat exchangers. If your lucky the filter is dirty, or the furnace condensate trap or drain is clogged. Most likely the secondary heat exchanger is plugged up and isn't allowing the pressure switch to make. Or the furnace is overheating due to it not being able to properly vent hot gas. Which would explain the high limit lockouts. Call an authorized carrier dealer so you can take advantage of the free heat exchangers and the $300 labor credit. You can also call an authorized Bryant dealer to perform the work for you. Only an authorized dealer can rectify this problem because the Bryant corp requires testing and paperwork in order to get your free parts and labor credit.
Good luck.
Dec 23, 2012 | Heating & Cooling
Furnace gas valve is not opening
YOUR FURNACE IS IN LOCKOUT MODE DUE TO A SAFETY FEATURE OF UNIT. USUALLY THE HIGH LIMIT HAS BEEN TRIPPED, OR YOU PRESSURE SWITCH FROM DRAFT INDUCER MOTOR FAULTY OR PLUGGED. IT WILL CONTINUE LOCKOUT MODE UNTIL THIS IS FIXED.
Dec 23, 2012 | Carrier Weathermaker 8000 Gas Furnace 125k...
Gas heater won't ignite
I agree. Either the pilot flame is dirty and is not making good contact to heat up the bi metal strip on the pilot assembly, or the pilot assembly is defective. 90% of the time if you clean the pilot orfice and the pilot burner it will take care of the problem
Nov 16, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...
Heating & Cooling Logo
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen