When the standard 3 way switch is in the down position the dimmer switch only turns on or off the lights. With the standard switch in the up position the dimmer switch works correctly. I've tried 2 different dimmers thinking that the first one might be defective but that doesn't seem to be the case.
With 2 standard 3 way switches being used they work correctly, making me think the wiring is ok.
Thanks for your help.
    Problem Solver:
  • 19 Answers
At the switch you have a common ( either a hot or a wire going to lt). And two Travelers( Wires going from one switch to the other) Make sure your not mixing one of the travelers up with the Common easy mistake happens all the time. Travelers are always in the the same at the other end of the 3w switch , you may need to take it apart and look. If you need further help send me more details I hope this helped
Posted on Jan 04, 2009
2005 cavalier dash lights not working. all fuses are goood. replaced cluster, dimmer switch, multifunction switch
Back lighting or warning lights ? check engine , ABS , air bags , seat belt , oil light etc... ?
Interior Lamps Dimming
The second group includes lamps which may be dimmed. This group may use a combination of vacuum fluorescent (VF) illumination and incandescent lamps.
• Power window switches
• HVAC control head assembly
• Radio
• The instrument panel cluster (IPC)
When the ignition switch is turned to the ON position, the vacuum fluorescent (VF) display (radio) turns on at maximum brightness. When the park lamps are ON all incandescent back lighting turn ON at the dimming level indicated by the IP dimmer switch. At the same time all vacuum fluorescent (VF) displays dim to match the indicated dimming level. When the headlamp switch is placed in the PARK position, the park lamp supply voltage circuit provides an input to the body control module (BCM). The BCM then supplies voltage to the instrument panel dimmer switch through the instrument panel dimming lamps control circuit. The setting of the instrument panel dimmer switch determines the amount of voltage that the instrument panel dimmer switch supplies to the BCM through the instrument panel dimming lamps low reference circuit. The BCM then sends a pulse width modulated (PWM) voltage to all the interior lamps. All the vacuum florescent (VF) and incandescent back lighting lamps are provided a specific voltage and are then grounded. When the headlight switch is turned to the PARK or HEADLAMP position, all incandescent back lighting turn on at the dimming level indicated by the IP dimmer switch. When the IP dimmer switch is moved from MIN to MAX, all vacuum fluorescent (VF) displays, as well as all incandescent back lighting respond from Minimum intensity to maximum brightness in response to the IP dimmer switch.
I would have it checked for DTC'S - diagnostic trouble codes stored in the BCM !
DTC B2624 Display Dimming Input Range/Performance
The body control module (BCM) supplies voltage to the instrument panel dimmer switch through the instrument panel dimmer switch signal circuit. The dimmer switch varies the voltage and returns the new voltage to the BCM through the dimmer switch signal return circuit. The BCM uses this voltage to determine the illumination level of the instrument panel lamps.
DTC B2625 Display Dimming Pulse Width Modulation (PWM) Output Circuit Range/Performance
The body control module (BCM) receives a variable voltage from the instrument panel (I/P) lamp dimmer switch. The BCM uses this signal in order to vary the illumination level of the I/P lamps. The I/P dimming lamps output from the BCM is a pulse width modulated voltage supply used to light the I/P lamps. If a malfunction occurs in the I/P dimming lamps output circuit, this DTC is set.
DTC B2662 Park Lamp Switch Circuit Malfunction
The park lamps are controlled by the turn/headlamp switch. Positive battery voltage is supplied to the switch through the EXT LP fuse. When the turn/headlamp switch is placed in the park or head position, battery voltage is supplied to the park lamps. The body control module (BCM) is also connected to the park lamp circuit to sense whether or not the park lamps turn ON when the low beam or high beam headlamps are turned ON. The BCM also uses the parklamp battery positive voltage to power the instrument panel (I/P) dimmer output circuit. If the BCM senses that the low beam or high beam headlamps are ON and the park lamp input is not active, DTC B2662 sets.
Do the park lamps work ?
Jun 11, 2017 | Cars & Trucks
Switch and dimmer work opposite each other
Refer this issue directly to Lutron. They could have an ineresting explanation!
Jan 27, 2014 | Lutron Toggler Single Pole 600 Watt Preset...
I want to install the 18023 ge dimmer in the middle of a 4-way switch
Bob, Not quite enough info to be sure how you have this wired, but here's a shot. 3 or 4 way dimming switches are designed to work with other 3 or 4 way on-off switches, not with another dimmer. I never tried this but it is no surprise that it might work only if you keep the dimming function of switch C in the full-bright position, because you are using two dimmers wired in series. For best operation, you should replace C with a regular 3 or 4 way switch.
Dec 30, 2012 | GE 18023 Dimmer Rocker OnOff with Slide...
Dash lights go on and off while driving, then headlights do the same
Test the electrical circuit's ! Look at a wiring diagram so you know what wire's to test . Watch these video's , buy a DVOM - digital volt ohm meter . Learn to test so you don't listen to guesses .
Basic Electricity for Service Techs Ohm law Current Flow Opens Shorts
Mastering Voltage Drop Testing with Pete Meier and Jerry Truglia
Electric Testing Techniques You Need to Know Free wiring diagrams here . http://www.bbbind.com/free_tsb.html Enter vehicle info. year , make , model and engine size. Under system click on lighting ,then under subsystem click headlamps . Click the search button then the blue link's . Right away in the first diagram i see the headlamp / panel dimmer switch is a input to the BCM - body control module . I mite think your first response would be to want to replace the BCM ! Reading a discription of how the lights are suppose to work may shed some light on the problem .
Headlamp ON/OFF control is determined by the body control module (BCM) by a signal on the headlamp switch on input circuit when the headlamp switch is in the HEAD position. When the headlamp switch is in the AUTO position, the BCM determines headlamps ON/OFF by the voltage from the ambient light sensor.
If the headlight switch is left in the ON position, the inadvertent power control feature will turn off the headlights approximately 10 minutes after the ignition switch is turned to the OFF position. If the driver places the headlight switch in the ON position after the ignition switch has been turned OFF, or if the ignition switch is in the ACCY position, the headlights will remain on until turned off or the battery runs dead.
The high beam indicator is illuminated when the instrument cluster receives a class 2 serial data message from the BCM that the high beams are illuminated.
Having the vehicle checked for DTC'S - diagnostic trouble codes , BCM - codes ! Need a professional type scan tool . Part stores can't read body codes , dealer or independent repair shop .
DTC B2575
When the body control module (BCM) senses a request for low beam headlamp illumination, the BCM sends a ground signal to the low beam headlamp relay through the headlamp low beam relay control circuit. The headlamp low beam relay will apply voltage to illuminate the headlamps.
DTC B2580
When the body control module (BCM) receives a ground signal from the multifunction high beam or flash to pass (FTP) switch commanding to illuminate the high beam headlamps, the BCM will energize the high beam relay by grounding the high beam relay control circuit.
DTC B2600
DTC B2610
The body control module (BCM) receives a variable voltage signal from the instrument panel (I/P) dimmer switch requesting to illuminate the illumination lamps to a desired intensity. When this occurs, the BCM directly sends a variable voltage based on the I/P dimmer switch position on the instrument panel lamps dimming supply voltage circuit, instrument panel lamps dimming control circuit, and the LED dimming signal circuit.
Voltage for the instrument panel lamps dimming supply voltage circuit, instrument panel lamps dimming control circuit, and the LED dimming signal circuits is from the TBC 2 A fuse in the instrument panel fuse block directly through the BCM to these circuits.
DTC B2620
The BCM directly sends a 5 volt reference voltage to the I/P dimmer switch which is then adjusted based on the I/P dimmer switch position and returned as a dimming return and dimming input to the BCM. The BCM uses this signal to directly control the desired level of instrument panel illumination lamp intensity.
Your best bet , take it to a qualified repair shop .
Oct 23, 2017 | 2004 Chevrolet Avalanche
Using 3 way dimmer, lights don't appear to go to full light
Hi Gene,
When two 3-way switches are used to control a light - and you wish to install a dimmer, you replace only ONE of the switches. If you replace both switches with dimmers, and one dimmer is set to 50%, the light will only be able to get to 50% bright; regardless even if the other switch is set to 100%. The light can only get as bright as the current lowest dimmer position of either switch.
Most modern dimmers are solid state, and should be able to get full power to the lamps. Older dimmers aren't very efficient and work a little differently - but should still do a good job as far as brightness of the lamp. You can run into trouble trying to dim CFL (compact fluorescent lamps) if they are not labeled specifically for use with a dimmer. Even those that are labeled for use with a dimmer have a noticeably short range of dimming when compared to standard tungsten lamps, and tend to have an audible buzzing sound.
If this doesn't answer your question, please provide the wattage, type and number of lamps in the fixture. Your dimmer is rated for up to 600 watts, but may be less if it is in a switchbox with other dimmers or you have broken off portions of the heat shield as directed by the instructions.
Mar 17, 2012 | Lutron AY603P Ariadni 600W 3way Dimmer...
I changed the light bulbs in the fixture it controls, now it does not work. What is wrong?
This switch is designed to dim incandescent lamps. It has nothing in its description about being used with CFL (compact fluorescent lamps) types. If you are attempting to dim standard CFL types, it will not work.
CFL's are available in both dim-able and standard types. As you may have guessed, only those marked as "dim-able" will work with a dimmer switch. Dim-able CFLs cost slightly more than standard CFLs but may be controlled by any switch. Dimmer switches may only control incandescent and other type lamps that specifically state they are compatible with dimmer switches.
If you are attempting to dim incandescent lamps, make sure that you are not trying to dim lamps with a total wattage greater than the dimmer can handle. Most dimmer switches are rated for 600 watts, if you have two dimmer switches under one wall plate, the wattage rating drops to about 500 watts. This de-rating is because of the heat the switches create. There are dimmer switches that can dim more than 600 watts, but the price skyrockets for a 1000 watt dimmer, and keeps climbing.
If your wattage is within the limits of the dimmer, check the bulbs. If they are ok, the dimmer may have failed and require replacement.
If you found my reply helpful, please rate it "4 thumbs up". Good luck & thanks!
Aug 16, 2011 | GE 18027 Dimmer Toggle OnOff with Slide...
Power is on the T603WV. Most switches turn on when flipped up, this one you must press down to turn on. The light does NOT dim. I think it must be reversed. Please help. Wires were not identified as Hot...
As for the direction, just remove the cover plate, remove the 2 hold down screws, and flip the switch over.
Reinstall screws and cover.
As for not dimming, if you are using fluorescent bulbs, they will not dim.
Dec 21, 2010 | Pass & Seymour #T603WV 600W White 3WY...
I have a trimatron rotary dimer and i have no clue how to replace it with my other switch. the problem is the other switch only uses 1 black and 1 red wire not 2 black and 1 red plzzz help
If the dimmer has two leads, it is a standard dimmer. One wire brings power into the dimmer, the other lead send "dimmed" power out.
If the dimmer has three leads, it is a 3-way, which is a combination of a dimmer and a 3-way switch. One wire brings power into the dimmer, and the other two leads bring "dimmed" power out - when you cycle the on-off function (by clicking the switch) you are sending the "dimmed" power out one lead or the other. You can use a 3-way dimmer in place of a standard 2-way by simply not using one of the 2 wires coming out of the switch. BUT you must be certain to insulate the end of the lead you aren't using, because when the switch is "OFF", this unused lead will be live. If you are actually trying to wire a 3-way, here's an excellent how-to-- http://www.ehow.com/how_2280970_wire-threeway-dimmer-switch.html Please vote if you found this helpful. Thanks, Al
Jan 12, 2010 | Leviton Trimatron Rotary Dimmer 6602-i Lot...
Installed 3 way dimmer - when turning off at 2nd location can not control dimming from first location until second location has been turned off then able to control dimming at first location - pass &...
Some dimmers are specific to which end of the 3-way system they are installed on "Power" or "Switch Leg". The way you can test which side is the power and switch leg is to test the wire on the "Black" screw of the switch (common) to ground with the lights OFF. If you have power on the "common" screw with the lights OFF it's the power end, if you have no power on the "common" screw with the lights OFF it's the switch leg end. Verify that you have the dimmer on the side specified in the instructions (switch leg). Sounds to me like you have it on the "Power End" so you are dimming on of the travelers instead of the light. That is why it is dimmed in one position and not in the other. (See page N-23)
http://www.passandseymour.com/pdf/N.pdf
Oct 14, 2009 | Pass & Seymour #T603WV 600W White 3WY...
Dimmer switch is not dimming
florecent bulbs wont dim unless they are dimmable.
Dec 24, 2008 | Lutron ELECTRONICS CO. Q-603PH-WH "QUOTO"...
Cooper Wiring Devices  6009W-K ROTARY DIMMER REPLACEMENT KNOB WHITE Logo
202 people viewed this question
Top Cooper Wiring Devices Electrical Supplies Experts
ken skalski
Jim Y
Jim Y
Are you a Cooper Wiring Devices Electrical Supply Expert? Answer questions, earn points and help others