Question about Goodman GMS90703BXA Heater
Furnace start buts shuts off
My furnace induction motor start for a few seconds then blows the 3amp fuse on the board. If I unplug the pressure switch the induction fan will run, the fuse will not blow and of course the furnace will not ignite. After a while the furnace will eventualy start, run and provide heat. My unit is a Goodman GMNT 120-5
  • Anonymous Mar 17, 2014
    my goodman furnace gks9 starts blower runs and after few minutes burner stops
  • 69 Answers
It sounds like you have an obstruction in the exhaust vent. Thats why when you bybass the pressure switch it runs ok. Steve
Posted on Dec 21, 2008
Furnace will not ignite.
I think you are talking about draft induction pressure switch operation. Make sure the metal orifice located on the draft induction blower is clear. To check, remove the rubber tubing end at the pressure switch and blow into the tubing. It should be easy to blow through it. If it is plugged, remove the tubing from the blower orfice and use a paperclip, inserting it into the orfice to clear the opening. After repairing, and all is hooked up, retry the furnace start up procedure. If the code comes up again, replace the pressure switch.
Dec 17, 2014 | Goodman Manufacturing...
Amp fuse keeps blowing
The component being protected by the fuse is drawing excessive current - has to be a board or something because the motor always draws more than three amps. Check the units schematic for locating the possible offending board. Must be relatively new since you indicate it is multispeed. Still under warranty?
Feb 23, 2014 | Gibson KG7SA045C23A 45,000 BTU 80% Gas...
I have a Ducane MPGA100B4B gas furnace. The furnace only runs for about a minute then shut off. It does this far too frequent.\r\n First the induce draft blower turned on for a few seconds to check for...
Hello, sounds like the limit switch is opening on the furnace.Usually when a furnace goes off on its high limit is becuase the airflow is being restricted making the furnace overheat. a limit switch is there to protect the furnaace from overheating, most cuases are either dirt or the blower motor not running up to speed, anything that cuts down on the airflow will cause the high limt switch to open.
Feb 24, 2011 | Heating & Cooling
Doesnt blow any heat we checked all connections furnace clicks on but never gets warm we think maybe its the heating element but we are not sure how to get to it to check
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem.The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 19, 2010 | Heating & Cooling
Heater turns on and heats garage to set temperature, than shuts off. when the temperature drops, the unit kicks on again. everything starts working again but only for a few seconds and than shuts off. it...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor.If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 11, 2010 | Mr. Heater Natural Gas Garage Heater -...
The Goodman Heater was installed in 2004. Thermostat set at 75F, the fan that blows CO2 out was on for about 1 minute, then I could hear the sound of the gas blowing into the furnace, but the ignitor...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 30, 2010 | Goodman GMS80903BNA Heater
Induction fan motor cycles on and off , with no call for heat
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Heating & Cooling
York 92 % eff. furnace shuts down on # 3 error (pressure switch)
i have fixed almost every one of pc9 -----we have installed in our company,code three{flashes} at first new presure switches installed, same thing,york knows about this,induction motor bearings,could be bad.our local york dist, has boards,inducer, ***.motor, dual press.switch,free.as is known as the only way to fix.after all else is ruled out.one local competator called us if we wanted to join class action suit . good luck.furnaces work good at first, season or two then bam
Nov 28, 2009 | York Furnace Draft Inducer Blower Fasco #...
Goodman furnace
double check your wiring. R terminal on the furnace will provide 24 volts to the t-stat. W terminal in the t-stat will send 24 volts back to the furnace W terminal to turn on the heat. G terminal in the t-stat will send power to the G terminal in the furnace when the t-stat is switched to fan on. Y terminal in the t-stat will send power to the Y terminal in the furnace which in turn will send 24 volts to the A/C outside. The C terminal in the furnace should be connected to the c terminal in the A/C outside as well as to the T-stat. Check the fuse again
Jun 02, 2009 | Goodman GMS90703BXA Heater
Carrier Weathermaker SX (model 58SX100)
There is a small tube that comes off the inducer for cracks or water. If there are cracks then the pressure switch that it is attached to may not be closing all of the time. Also sometimes you can get water in that tubing which will also cause the pressure switch to not close. If thats the case shorten the tube so there is no low droop in it where water can collect. Another thing that I would do is disconnect the tube at the indicer, take a straightened out paper clip or stiff wire and poke it in the nipple on the inducer to make sure it is clear too. Let me know if any of these work. There may be other things we can do.
Jan 19, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...
Goodman GMS90703BXA Heater Logo
415 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others