Burner not full force
I have and intertherm propane forced air with a single burner. when the thermostat calls for heat the exhaust blower turns on and because the pilot is always on the burner turns on also.. but the burner isnt strong enough to heat the box so the blower motor never gets the signal to turn on
    Problem Solver:
  • 12 Answers
Could be your gas pressure is too low. Also, there is a particular type of spider that likes to get into the gas line at the gas valve and spin a little web in there. I have often seen this as the cause of low gas pressure. If neither of these is the cause, I would suspect a faulty gas valve.
Posted on Dec 16, 2008
Furnace goes out when blower should start
There is a sensor called a pressure switch that is attached to the area of the blower motor for the exhaust fan. It is bad or plugged.
Nov 16, 2015 | Heating & Cooling
Pilot and burner light then gas shut off model 7900
How many degrees before it reaches desired temp, does it shut off? A thermostat is designed to shut the furnace off a couple/ few degrees before it reaches set temp. It has what is called a heat anticipater, which shuts the burner down, and lets the blower use the remaining heat from the heat exchanger to bring it up to desired temp making it more efficient. If it is more than a few degrees, replace the thermostat. You can jump out the red and white wires to confirm the faulty thermostat. If by doing this, the furnace never shuts down, until you separate the red and white wires. That confirms a faulty thermostat. Hope this helps someone.
Oct 06, 2014 | Coleman Propane Forced Air Heater...
When i turn the heat up sometimes it takes a long time for the gas furnace to start ..why?
Watch your furnace when you turn the thermostat up...make sure to record everything that it is doing. If you have an induced draft, forced air system, then the heat sequence of order should go like this... Initial call for heat from tstat, Inducer vent motor turns on-pulls in the pressure switch, circuit board sends power to igniter whether it is spark or hot surface, then gas valve opens. Flame sensor senses flame, burner stays on, and blower motor kicks in to heat the space. If you notice any variance from this, then something needs to be checked by an HVAC Service Tech.
Dec 14, 2013 | Honeywell Programmable Thermostat Heater
I have a customer with a evcon direct vent forced hot air furnace. The thermostate calls for heat , the combustion fan comes on then the ignitor lites and the burner comes on for about 2 minutes, jsut...
same thing happened to mine. go on the roof and pull the cap off. mine was rusted thru the inner pipe (exhaust side) letting the exhaust air to get drawn back into the combustion air side. causing it to short cycle or snuff the flame out.
Oct 29, 2011 | Tools & Hardware - Others
We have a coleman electronic ignite propane furnace for a mobile home it is not even 3 winters old. Regulator just replaced, tenant ran out of gas. We turned off the power and reset the computer-the...
This furnace should have a diagnostic light that will give you a starting point where to look. It is located on the control board and will blink a code. If you remove the panel with the door switch on it, you will erase the code. Look for a small viewing port that looks on to the circuit board. Once you get the code, look on the wiring diagram for a explaination of the codes.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 24, 2010 | Coleman Propane Forced Air Heater...
Hi~ i have a coleman-evcon heater in a mobile. The heater comes on when the thermosat is turned up to, say 65 from 55, then before the air blown out is even really warm, it shuts off. it runs on propane,...
Jan 13, 2010 | Coleman Propane Forced Air Heater...
My Home propane tank was empty, I just had it filled, but when I go to turn on the heat, a flame icon comes up. I noticed on the heater it has an on/off switch for the automatic pilot light. I am not sure...
Make sure all switches are on and open. It may take a few attempts to get gas to the burners so you may have to reset the furnace by either the Emergency switch or circuit breaker. If it takes longer than 3 tries, you may have a gas regulator problem and will need to call your gas company for repair. The regulator belongs to the gas company so they shouldn't charge you to repair or replace.
Jan 04, 2010 | Coleman Propane Forced Air Heater...
My heater will not light. It is eletric ignition, there is power coming into the unit.
In order for the furnace to light, a few things must happen. The thermostat must have a call for heat thus making a connection (closing a switch) sending a signal to a computer circuit board. The board will in turn blink a light indicating a call for heat is registered. It will then send power to a fan motor that will remove old air from the burner area and introduce fresh air to the burner. Once the blower comes up to speed, the pressure closes a a pressure switch. Once the switch closes, it sends power to an igniter, either a glow type or spark type. It also sends power to one side of the gas valve to open up the pilot gas valve and send gas to the pilot assembly. Once the computer senses there is heat at the pilot valve, it will open up the second gas valve and send gas to the main burner. The trick is to know where it is going wrong. First you must watch this sequence to follow the workings. To do this you may have to remove some panels on the furnace and hold a door switch closed temporarily to trick the furnace to run. Follow the sequence above to find where it ain't happening and look at what must be done to fix it. It could be as simple as a bad thermostat (no call for heat) or a plugged exhaust vent not allowing the pressure switch to close. Let us know how you make out with the diagnosis!
Oct 13, 2009 | Coleman Propane Forced Air Heater...
Furnace blower motor turns on and off all the time...
blower will not shut off. will only shut off by turning off circuit breaker. changed thermostat. no help. what should i check?
Dec 20, 2008 | Coleman Propane Forced Air Heater...
Heating & Cooling Logo
64 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Marvin
Marvin
john h