Question about Carrier 38CKC036 Air Conditioner
Gas heater won't work
Gas heater cut on, ignited, shut back off. Tried a few more times. Tech came and cleaned flame sensor. Worked fine for 2 days.Today blower turns on, not even a glow to ignite burners. Tech came and changes the glow ignition. Now doing it again. Red led light blinks short, long,long. It is a Carrier brand about 11years old.
  • zajam Jan 05, 2009
    Thanks for looking at my problem. After resetting it, it finally is doing ok. It is extremely sensitive. If it gets turned on and off too much it just shuts down. We also changed to a digital thermostat because if I moved the lever too fast on the old kind it would shut down. It's hot here now anyway. Louisiana winters are lovely. Been running the a/c for over a week.
  • Keith Miller
    Keith Miller May 11, 2010
    is there a code explanation on the panel
    President:
  • 2,976 Answers
Which flame sensor did he replace? The pilot flame or the plenum temp. sensor.
Posted on Aug 10, 2009
Payne 383KAV heater. Gas valve won't open to fire heater.
Being as how you changed the gas valve, make sure the arrow on the bottom of the gas valve is pointed towards the burner. Check for 24 volts at the common and main valve terminals on the gas valve when the thermostat is calling for heat...terminals MV and C. You will only have 24v there if the flame sensor senses flame... either pilot flame or main gas. You coud have 24v there without gas flowing or flame if is is a thermocouple standing pilot system and the gas valve is not in the 'on' position. But standing pilot systems usually do not have flame sensors.
With a flame sensor in the system, you have to have either spark ignition or glow coil ignition. If its spark ignition check for 24 volts at the pilot valve and common terminals on the gas valve WHILE the ignitor is sparking. That would be PV and C. The ignitor should spark and 24v should be on PV and C for 30 seconds to a full minute without ignition if it is a spark-to-pilot system.
If you have a glow coil, it will energize and burn bright orange for a minimum of 30 seconds BEFORE the main valve is energized. Then MV and C is only receiving 24v for approximately 5 to 6 seconds. This gives the flame sensor the time to prove the flame....if it does not prove flame, the system shuts down.
Dec 29, 2014 | Heating & Cooling
Burner lights and shuts off 3 times and then give warning lights A and B
It depends on the model but AB on most of the AOS the A & B LED's lighting up usually means ignition/flame failure.
Ignition/flame failure:
The gas control valve/thermostat has reached the maximum number of retries (3) for ignition and is currently locked out for one hour. Cycle the power to the water heater off and on to reset.
Basic troubleshooting/solutions:
1 Ensure flame sensor is making good contact with the burner flame and ensure flame is steady. Also ensure supply and manifold gas pressures are within the requirements in the installation manual.
2 Gas supply is turned off - pressure is too low. For low gas pressure, consult with your gas utility.
3 Ensure the flame sensor is clean - use fine steel wool to clean the flame sensor.
4 Check igniter assembly plug and the socket on the bottom of the gas control valve/thermostat for good connection. Replace igniter assembly if the plug is worn or damaged. Replace the gas control valve/thermostat if socket is worn or damaged.
5 Replace igniter assembly.
If this does not apply to your model then here is a link to the instruction manuals for all models:
Residential Gas
Apr 14, 2013 | A.O. Smith Water Heaters
I have a richmond 40 gallon powervent water heater. It seems to light, but shuts itself off after about 5 seconds. I am leaning toward the vapor sensor. I know there are reset codes, but have not been...
1) Could be the vapor sensor. That's a suspect.
2) General troubleshoot: clean burner and combustion parts, clean air intake, bleed air from gas line, check gas pressure. Color of gas flame should be clear blue, and flame should be strong, and no combustion by-product dripping back into combustion chamber. No chemicals of any kind stored in air supply. Plenty of fresh air. Water heater in hot attic needs more air. If water heater has igniter, then igniter has to be checked. Flame sensor must be positioned correctly and operational at time of combustion, or sensor will signal gas control to turn off gas. Gas control valve can be bad.
Open following link for possible illustrations and reading.
http://waterheatertimer.org/How-to-install-gas-water-heater.html#troubleshoot
3) Specific troubleshoot begins with identifying gas control valve and reading the service manual.
I think the Rheem/Richmond power vent has intellivent gas control
Open following link to identify gas valve and download possible service manual:
http://waterheatertimer.org/How-to-adjust-water-heater-temperature.html#intelli
4) Take a moment and rate answer:
And take advantage of fixya expert assistance live.
For a price, expert works with you while you work on water heater or any do-it-yourself project.
Fixya is always less expensive than a service call.
Sep 04, 2011 | Audiovox Richmond 6G40-36F 6-Year Tall Gas...
Heater turns on and heats garage to set temperature, than shuts off. when the temperature drops, the unit kicks on again. everything starts working again but only for a few seconds and than shuts off. it...
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor.If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 11, 2010 | Mr. Heater Natural Gas Garage Heater -...
The Goodman Heater was installed in 2004. Thermostat set at 75F, the fan that blows CO2 out was on for about 1 minute, then I could hear the sound of the gas blowing into the furnace, but the ignitor...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 30, 2010 | Goodman GMS80903BNA Heater
Furnace will start and sequence fine run for five minutes or so then the flame cuts out....miller type furnace put a new board in last year so now it cycles three times and goes into soft lockout.....
Clean the flame sensor.
Nov 19, 2010 | Heating & Cooling
Opened & cleaned pool. Haward 250 Heater woun't stay on.
Could be a dirty or faulty ignition sensor. This is the sensor that tells the heater that there is a flame burning normally. If that sensor gets dirty or fails, the heater thinks there's no flame even though there is and cuts the gas as a safety measure. Cut the power, remove the cover, and check all the wire connections to be sure the leads are clean and dry and snug. The ignition sensor is near the bottom. If that doesn't work, then the sensor might be faulty rather than dirty. Call a tech to replace it.
May 30, 2010 | Hayward 250kbtu Ng Pool Heater - Inground
My Goodman heater has a problem igniting at times
Hi, I would have to assume your igniter is weak or has a crack in it. Do you see glow from the igniter every time? There is a flame sensor that looks for flame after the gas comes on and it will lockout after three tries, if the flame came on and shut back down every time, it would be problem with that.
Jan 08, 2010 | Goodman Heating & Cooling
I have a problem with my heating system. It is about 10 years old and has had the ignitor, combustion blower motor, and programable thermostat replace in it's lifetime. The system worked great last year....
sounds like its not proofing flame. it has a sensor usually like a needle sticks out into the flame that tells the gas valve the flame lit and is burning so its ok to keep sending gas, if its fails to proof flame then burner shuts down, then it tries to relight 3 times then locks out on fail safe. the blower will sometimes run continually once that occurs to highlight a failed condition. every time you reset it will try again 3 times then shut down. lp gas is very dangerous, even i do not work on it as the gas acts like gasoline and lays around. not like natural gas that disperses well. if you see the flame sensor try gently cleaning it with a little emory cloth. also a loose ground can cause this. check tio be sure any green wires are snug , they actually flow volts to ground through the flame on some to proof, thats why no ground no flame. if that fails then the board is most likely problem. change wire for wire , or get generic replacemant and follow directions exactly. good luck.some ignitors act as a flamre proofer as soon as they are done igniting! rarely do they fail to perform both funtions.
Nov 20, 2008 | Heating & Cooling
My goodman gmt090-4 shuts off about 10 sec. after burners ignite
Check the pressure sensor. I tapped on mine a few times, removed the hose and checked it for blockage and replaced. It has been working fine since. I do have a new sensor on order.
Oct 04, 2008 | Goodman GMS90703BXA Heater
Carrier 38CKC036 Air Conditioner Logo
281 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others