Cond. Unit FAN on an Rheem/Ruud Heat pump Model 10PJA4201
After replacing a bad Defrost cycle Board with a new updated model which has an Coil tyemp sensor & an Air temp sensor the cond.Fan is NOW drawing Air in thru the Top instead of thru the coils and out the Top, there was only rwo Fan contact taps with push pull connections, I only removed and installed one wire at a time, the wire are in the same places as was on the Old board, Is the Fan running the wrong direction, if so will it hurt anything? it is heating and cooling the way it is running
watugot
  • 290 Answers
SOURCE: Ruud heat pump outside unit trips circuit breaker
Check your wiring between the contactor and compressor for a short to ground, or check the compressor windings for short to ground.
With the Tstat off, the contactor should be open so the only way for the compressor to be trying to do anything is if the 110 volts from the unbroken side are traveling through the compressor to ground. Since 110v is not enough to run it, the overload is kicking it out, cooling off, and repeating the cycle. When you kick on the Tstat, the contactor is supplying voltage directly to ground without going through the resistence of the compressor windings and kicking the breaker.
Post back and let me know what you find.
Posted on Nov 20, 2007
dcp2
  • 63 Answers
SOURCE: split air cond fault
Need more information. What brand is it and also would be nice to know the model
Posted on Jan 25, 2008
chillmaster
  • 104 Answers
SOURCE: Ruud achiever heat pump
If back-up heat comes on when a/c is turned on and then the back up heat turns off shortly after the a/c turns off, then the low voltage wiring is NOT correct. Your "R" terminal is basically your "hot" and your "C" terminal is basically your "neutral" to simplify explanation. The Furnace supplies the "R" power to the thermostat and then depending on what wire the thermostat sends the power back on determines what the system does. The thermostat terminals are as follows "G" is fan, "W" or "aux" is elect heat, "Y" tells the outdoor unit to run, "O" or "B" tells the outdoor unit whether it is heating or cooling, and "E" is emergency heat. "G" should connect from the t-stat directly to the furnace and go no further. "W" or "aux" AND "E" should both connect to your "W" or "W1" terminal in the furnace, there should also be a "W" connection to the heat pump ( this allows the H/P to turn on the elect heat when the unit defrosts) "Y" and "O" or "B" may or may not connect to a terminal in the furnace, usually they just pass through the furnace from the t-stat to the H/P and get wire nutted in the furnace. Now, here is the key. As I mentioned previously "O" or "B", a system will only use one or the other. The entire industry (except for Rheem and Ruud) uses the "O" terminial which has 24v on it when you are cooling and no power when you are heating. Rheem and Ruud use the "B" terminal which is just backwards, 24v in heating and no power in cooling. this could also be your problem if the t-stat thinks it is telling the H/P to cool but the H/P is actuall interpreting the signal to heat. Check your amp draw on the furnace, if you have anything drawing 15 amps+ then it is most likely the actual elect heat running, if not then check the "B" terminal. Most universal t-stats come set from the factory to use the "O" terminal which is more common. Usually this can be changed in the installer setup menu on the stat or sometimes the stat will have separate "O" and "B" terminals
Posted on Jun 15, 2008
  • 182 Answers
SOURCE: Ruud Heat Pump
this may indicate you have low voltage but no high voltage.check fuses and breakers.
Posted on Aug 09, 2008
  • 306 Answers
SOURCE: v- lec MODEL ASW-H18A4/HSA air conditioner compressor cuts out.
If you get the numbers off the board give this web site a try. I live in the city they have shop in and they are very good.
http://www.wsconet.com/
Posted on Jan 28, 2009
Rheem heat pump not coming on in heat mode. Control board has two LED lights # 1 solid, #2 blinking. What does this mean?
Usually wen the led lights are blinking it means there is a problem. If you look on the door or the cover there should be a code that tells you what the blinking represents.
Example - one blink per second - compressor, two blinks - fan motor, etc. The other thing you can do is look up the model number on line for the installation manual and it should have all the info you need.
Jan 08, 2015 | Ruud Defrost Control Board 47-102684-08...
Heat Pump Blowing Cold
Unless you just installed or had the thermostat installed recently, I would not point at the thermostat as the problem. With what you have described I would suggest have your units serviced as it sounds like a loss of charge, or failed defrost control board. The "Aux" comes on when the unit is using secondary heating (electric heat strips). That occurs when the demand temperature (what you set it to) in Heat mode is more than the current room temperature, usually ~2-4 degrees higher. Also happens in defrost mode. Defrost is a heat pump cycle that melts any build up of ice on the condenser unit (outside unit). That process is simply the unit running in cool mode which will heat up the outside unit to melt any ice. Defrost cycles vary with manufacture but usually you can tell if is in defrost by looking at the outside unit, during defrost the unit will be warm or hot sometimes there is steam and the compressor will be running but not the fan. Defrost only happens on heat pumps in "Heat" mode. Rheem has a 10 yr compressor and parts warranty, so call the installer or Rheem authorized service company.
Nov 11, 2013 | Honeywell RTH7600D Touchscreen 7-Day...
My sister has a Ruud Achiever High efficency heat pump Model UPLA-049JAZ Serial #6408-M389910353 they just moved into this house in ND and have no information on this system..Over the winter it was...
There are 3 possiblites
1. you have a bad defrost board or defrost sensor.
2. Your low on Freon.
3. Your coils and/or your Filter is dirty.
May 01, 2011 | Heating & Cooling
Our air con runs, on heat, and after a time cuts out, blows cold and makes a sort of hissing noise (but not a real hiss) and then shuts down. It then restarts after a couple of minutes. Is this normal?
Yes.Think of a heat pump as a A/C in reverce in cool indoor coil is cold&outdoor coil is hot.Naw indoor coil is hot &outdoor coil is cold&fan is pulling in cold air from outside.its going to iceup& go into defrost cycle.If your unit has a timed defrost every 30,60,or90min.(witch ever yours is set for)Defrost control board checks a sensor on cond.coil,if it is frozen unit goes into defost.You will here a swishing noise,iis the reversing of refrigerant.you will also notice the outdoor fan is not operating&at termanation of defrost fan will blow out steem.the other metod is on demand defrost.when coil freezes unit defrosts.
Mar 02, 2010 | Heating & Cooling
Bryant heat pump model 697bno36-b froze up (solid block of ice) in low teens. I need to find the defrost timer to adjust or replace.
If you have the newer style control , it is part of the general circuit board and cannot be replaced seperately. There usually is an adjustment the can change time interval of defrost such as 45,60,90,120 minutes. On older models, there is a seperate control that either worked by time or by air restriction that has a tube that senses the air flow through the coil (this tube could be blocked or disconnected. Other possibility, is the reversing valve (Ihope not). This reversing valve has aelectric coil on it that activates the valve (if coil is bad it can be replaced;no big deal). If the valve itself is bad, then you got a big problem. To check this out, turn off unit. Wait 5 minutes, then turn system to air cond,(cold) and run the system on cold for a few minutes. If you get cold air (inside the house) then the reverse valve is ok; by the way, this will remove the ice and tell you that the defrost cycle circuit is the problem. Goodluck,Macgivor
Jan 16, 2010 | Bryant Heating & Cooling
Defrost Cycle Problems with Heat Pump
It's a defrost board issue. The timer on the board or something similar is hanging up. Unfortunately the solution is to replace the board. By lowering the temp. on the T-stat you are resetting the timer on the board. As you see that only works until the next cycle.
Feb 22, 2009 | Weather King 12AJA4801AH Air Conditioner
Defrost Cycle Problems with Weatherking Heat Pump Model 10PJA4201
look for your diagram on the back of the door panel
Nov 22, 2008 | Heating & Cooling
You need to replace the defrost board and sensor
Nov 21, 2008 | Weather King 10AJA6001AH Air Conditioner
RUUD Central Air/Heat Pump
Start with the simplest first it,s not fun but it's necessary EVERY TIME. Clean your evaporator and condenser coil, change your air filter. Getting to the evap. coil is often a real headache and a result doesn't get done often. When its clogged as you probably know the refrigerant can't absorb heat at the coil so it tries to absorb heat on the way to the compressor freezing the hot gas line the safety circuits that protect the heat pump compressor from getting liquid refrigerant back to the compressor almost immediately will take the compressor of line (looking somewhat like a defrost cycle). I hope this helps it's a tough repair GL!
Apr 10, 2007 | Ruud UBHC Air Conditioner
Heating & Cooling Logo
59 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster