Question about Carrier XHB123D X/Y Series Heat/Cool Air Conditioner
Blower runs, Ignitor glows, no 24V at gas valve, no click....
I have Carrier Weathermaster 8000 with ces0110057-02 control board.
When thermostat calls for heat, I hear click on the board, diffuser turns on, ignitor glows shortly after... and then NOTHING. I measure V across 2 terminals on gas valve as well as each terminal and ground. All measurements show 0V. Main blower works fine since I can turn my fan on and it runs. I checked 3A auto fuse on the board and it has not blown. I checked the wire terminals and nothing seems loose.
Do I have a bad board? If so, is it worthwhile to spend $$$ on the replacement board? My furnace is 13 years old.
  • 306 Answers
Check the two wires coming directly off the transformer. They will be connected to the board the line voltage will be black and white and the 24voltage will be something like blue and red undo from board and check to see if you have 24 volts there. If not your transformer is bad 10 dollar part. Take it to Heating and Air parts house to replace. Let me know ken
Posted on Dec 13, 2008
  • Ken Bledsoe Dec 17, 2008
    Did you get your unit fixed? ken
The unit cycles through all levels and then displays Ignition failure, code B2. I replaced the flame sensor, the ignitor, and there is natural gas at the gas valve.
Sequence of operation for most Gas fired furnaces...
Demand for heat from t-stat
Control board demands combustion chamber purge
(IDM /induced draft motor if it has one)
Control board tests all safeties (this is usually via
the IDM wiring.)
Control board sends 24v to PV at the gas valve igniting
the pilot OR control board sends voltage to the
ignitor as in yours.
Control board sends 24v to MV at the gas valve.
Control board allows time for heat exchanger to warm
then calls for blower operation.
Your sequence of operation? Won't be the flame sensor unless ignion has been achieved. If the ignitor is working/glowing red? Is the IDM working? Make & model#?
May 26, 2015 | Heating & Cooling
My Bryant Gas furnace model number is 373LAV036095 the pilot light won't light. Gives us indication that the pressure value is stuck??? Sends into lockout mode. Where is the pressure value located in the...
This is a down flow unit. There is no pressure valve on this unit. Here is all the parts on this unit.
1. Manual - reset, when used.
2. Blower and blower motor
3. Relief box also known as a exhaust flue.
4. Gas valve control knob or electric switch, ON/OFF
5. Gas Valve
6. Gas burner
7. Ratting plate
8. Blower door safety switch
9. Blocked vent safeguard tube and switch
10. Gas Manifold
11. Manual limit switch (2)
12.Hot surface ignitor
13. Flame sensor
14. Inducer blower motor
15. Control board with relays and transformer.
That is all the parts. The first thing the heater gets a call from the thermostat to the control board marked W. The board sends 24v to the inducer fan relay which makes and causes the inducer fan to come on now there is a small tube that runs from the inducer fan box to a switch when the switch makes it sends power to the board which proves you have cleared the exhaust flue then the flat surface ignitor starts to glow and then gas valve opens and fires. now if this tube is stopped up the heater will not fire and will lock the unit out. Also if the flue is stopped up with trash it will do the same thing. If you are not familiar with gas heating units you should call a service company out and check out the system there is a lot of things that need to be checked out every heating season as to keep you and your family safe.
Mar 02, 2015 | Heating & Cooling
Does not ignite, no gas getting to unit to ignite. Gas supply is on.
More than likely your gas valve or control board is malfunctioning. You can use a multimeter to check for voltage at the gas valve when the furnace calls for it. In sequence, the IDM will come on, then another click that starts the ignitor which glows, then the next click will be the board sending power to the gas valve. You should have 2 wires on the gas valve, put the meter leads there and when the board calls for the gas valve, you should have 24v at the gas valve. If not, the board is faulty. If you do have the voltage there, the gas valve is faulty and needs replaced. Sometimes you can take a pair of pliers or similar tool and gently knock on top of the gas valve and it will get the valve "unstuck" which can get you some heat if needed. Hope this helps!
Nov 28, 2011 | Goodman GMS90703BXA Heater
The water heater red light keeps flashing rapidly on my Powervent 2 model 41VRP40N. It is not producing hot water and when I read the manual it says it needs more heat. What does this mean. How do I fix...
There are many things to check. The single most important test is for 24V at the gas valve after the ignitor is supposed tp be on. 19 V or less and there is either a bad ground or the ingition control board has failed. (Wire ground problems are a high probablilty)
Here is what the book says:
PROBLEM #1 - HOT SURFACE IGNITOR DOES NOT GLOW RED
(Remember to wait for purge time, 17/34 seconds, on models so equipped).
Possible causes
A. No main power
B. Faulty transformer
C. Faulty thermostat
D. Faulty limit switch
E. Faulty blower interlock switch
F. Faulty hot surface ignitor
G. Faulty ignition control
Solution
Step #1
Perform normal system checks of main power, transformer, thermostat, limit
switch, blower interlock switch, and replace faulty component.
Step #2
With power on and thermostat set at its highest position, check voltage
between "TH" and "TR" on HS780 ignition control. If 24 volts is not present
check output at transformer. If no, replace transformer. If transformer
checks out OK look at other controls in the 24 volt circuit I.E.: thermostat,
limit switch, blower interlock switch. Check for 120 volts between "neut"
(L2) and "120" (L1). Check for 120 volts at the ignitor across "IGN" and
"IGN" terminals on the HS780 ignition module. If 120 volts is present,
replace ignitor. If no, replace the 780 series module
PROBLEM #2 - IGNITOR GLOWS RED BUT MAIN BURNER
WOULDN'T LIGHT
Possible causes
A. Improper ignitor alignment
B. Faulty ignition control
C. Faulty gas valve
D. High inlet gas pressure
E. Polarity reversed
F. No earth ground
Solution
Step #1
Check for availability of gas at gas valve. Make sure the manual valve
upstream of the gas valve and the gas valve are in the full on position. Also
make sure gas is being supplied to the system at the proper pressure, too
high will lock-up the valve.
Step #2
Check proper polarity of "NEUT" and "120" on the ignition control by reversing
the wires, if reversed gas valve will not open. If this does not solve the
problem, replace wires as they were.
Step #3
Check for proper ignitor position.
Step #4
Check for a good earth ground by using a meter connected between L1
and furnace chassis. Should read 120 volts, if no, check and/or repair ignition
ground wire or ignition control mounting screws.
CAUTION POLARITY MUST BE OBSERVED
Step #5
Check for 24 volts at the gas valve terminals; "1" and "2" on a 7200 series,
"M" and "C" on a 7100 series, "TH" and "TR" on a 7000 series. If yes,
check wire integrity or change the gas valve. If no, change the 780 series
ignition module.
That is pretty much all of the troubleshooting required.
Thanks for choosing FixYa,
Kelly
Feb 14, 2011 | Rheem 40 Gallon FVR NATGAS Low WATER...
Carrier 48sx gas pack. Won't turn on. No smell. No igniting sound. Blower fan works. How do I troubleshoot this?
Remove the panel from the heater section, you will need to watch what happends as there is a call for heat. There may be a light on the control board that lights up or blinks to indicate a call for heat. The inducer blower (exhaust blower) will start. INn a few seconds after the blower starts, the igniter will glow orange. After a few more seconds the gas valve should open and the burner will ignite. If the inducer does not run, you may have a bad motor or control board. If the igniter does not glow, you could have a bad pressure switch, bad pressure switch hose or a broken igniter. If the gas valve does not open, you may have a bad control board or bad gas valve. If you get no light on control board, bad fuse, bad thermostat or bad control board.
Jan 03, 2011 | Heating & Cooling
Carrier Weathermaker 8000 led stays on constant, blower works and i have power to the controller. no power at the ignitor/gas valve.
Check your thermostat level +29 and mode in Heat. If still problem, Check power
RV. Please write if your problem not solved with above solution. Thanks.
Dec 11, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...
CARRIER WEATHERMAKER 8000.NOT SURE HOW OLD. HAVE POWER,FAN COMES ON,IGNITOR GLOWS,GAS VALVE OPENS,BLOWER RUNS,IGNITOR GOES OUT. CYCLES THREE TIMES LOCKS OUT. ANY IDEAS?
sounds like the roll out switch may be sensing a clog. here is a website that can explain things better, hope it helps Tim:
http://arnoldservice.com/Troubleshooting_Heating_Problems.htm
Oct 30, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...
Carrier Gas Furnace and Hunter Thermostat not working
Definitely a furnace issue. The gas valve is not opening if you see no flame. I have seen the igniter glow but not send enough voltage to the circuit board to make the gas valve open. If this is the case you should replace the igniter. It is very fragile so please use care when replacing. Check all connections at the circuit board as well as the gas valve. Check your gas supply. Check to see if you get 24 volts AC to the gas valve. If no, replace the circuit board. If yes, replace the gas valve once you confirm that you have gas to it. If you get a pilot flame only, you will need to clean the burners and flame tray that spreads the flame from one burner to the next.
Dec 06, 2009 | Heating & Cooling
Goodman GMP075-3 ignition problem
bad board,i have had several board failures on goodman
Dec 18, 2008 | Goodman GDS80904BNA Open Flame Heater
Gas not coming on Carrier Weather Maker 8000
either the gas valve is not opening or your not getting gas to the furnace.  also the gas valve won't open unless the draft motor comes on.  if the ignitor is trying to light, but there's no gas, it might be a bad gas valve. i would call your closest NATE certified contractor
Nov 12, 2008 | Carrier XHB123D X/Y Series Heat/Cool Air...
Carrier XHB123D X/Y Series Heat/Cool Air Conditioner Logo
402 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Bill Long