I have goodman gmp heater dose work for few mintes
My heater works for 10 mintes then short off , and blows gold air . i have to shout off the unite for few hours and well work there after the same way 10 mints . change flam senser. ignitor same problem.
  • 1,420 Answers
Sequence of operation on your gas furnace may help diagnose your problem.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces like yours will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Posted on Dec 10, 2008
Gmp 100-3 fan runs even when tstat is set to off an fan setting to auto. unit ran fine all summer in cool mode and was off for the last couple weeks. just notice the fan was on yeaterday. ran unit in...
Hello, one way to check is remove the green wire from the G termimal on the circuit board in the Furnace, if tn
His turns it off it may be a short in the tstat wiring or bad thermostat, if it does not turn it off the relay on tne control board is stuck and tne entire board must be replaced.
Sep 28, 2011 | Goodman GMS90703BXA Heater
Goodman Air handler blowing fuse if switch outside unit not runni
Sounds like your compressor in your heat pump is siezed . You can try a "Hard Start" Capacitor...which basically gives your compressor a kickstart and works 95% of the time when compressors get older....It's hooked up in parallel with the existing Capacitor...if you're not familiar with Electrical etc I would call an expert and mention what I said . If this doesn't work you will likely need a new Compressor/Unit . You could also have a short to ground in the heat pump side....likely the compressor is the problem however the original Capacitor could also be the problem
Oct 27, 2009 | Heating & Cooling
How to fix twinning problem for a goodman GMP 100-4
Call AAA back it should be warrented if they worked on it frst don't touch it or you lose your warrent, it does sound like the thermal bulb is not in the flame so call them back fist then let me know post here and I will try to help you if they do not sove the problem, you should have a work order they gave you when they did the repair. Hold on to it.
Oct 09, 2009 | Goodman GMS90703BXA Heater
Goodman Furnace GMP 050-03
You need to check for 24 volts across the gas valve as the ignitor glows. If you get it, it is a bad gas valve. If there is no voltage or strange voltage, replace the control board.
Dec 09, 2008 | Goodman GMS90703BXA Heater
Goodman Furnace/AC unit not working 3a fuse blows even after replacement. once thermostat is turned on and clicks to start ac unit the fuse blows
3 amp is standard.the fuse is blowing to protect the transformer.It is telling you that there is a short in the low voltage wiring.Goodman also had an issue with the coil shorting on the contactor.To prevent damage.....i'd call a pro.It should be a fairly simple repair.