Disconnecting green wire from thermostate did allow furnace to run properly but every time I want to switch back to heatpump I must reconnect green wire again.Here is how wires are connected to themostate.Red to rcJumper wire from RC to RYellow to YBlack to COrange to OBGreen to GWhite to AugWires go toWhite to W on furnace control panelYellow to heatpumpGreen to heatpump and G on panelOrange to heatpump Black to heatpump and C on panelRed to heatpump and R on panelBlue,Brown,purple,gray and white wires not used at thermostate and also not used at heatpump.It shows in wiring guide that there should be a jumper between Aux and Eand that E sends output when set to Em.heat.Should one of these unused wires go from E to heatpump.I have tried to get installer to come back and fix it but no luck.thank you very much again.
  • 2 more comments
  • RAY TRUMAN Dec 10, 2008
    there is no RH on t-stat
    had to disconnect green wire from g on t-state so that fan would not run constantly
  • dwkcool May 11, 2010
    is this a new t-stat
    Does the t-stat have an Rh also beside Rc and yes it needs a jumper wire from AUX to E
  • 334 Answers
Try this.
A T-stat.
Orange = O
Red = R (with existing jumper)
Black = C
Yellow = Y
White =W1 (Or AUG)
Green =G
At airhandler/furnace.
Green = blower wire (usually green, double check with schematic)
(Green should not go to the HP.)
Orange to HP
Red to red and to HP
black to blue (or C) and to HP
White to W
Yellow to HP. (It may also go to a "float switch" if installed. but that will just be a safety switch on the drain pan in case the line clogs and it overflows.)
The green is typically used for the blower motor. (furnace only)
The orange is used for the reversing valve. (changes from AC to heat, is located in the HP only)
Blue is typically used for common (or "C") but they may have changed it to black due to a broken wire, or other problems.
The only wires going to the HP should be
Red
Blue/black
orange
yellow
Orange should not be going to the furnace at all.
HP wiring should be
Orange to orange or O
Red to R or red
Blue/black to blue or C
Yellow to Y
Posted on Dec 10, 2008
How do I reset the temp my heat pump switches from electric to gas. It runs much more economically on electri than on propane. The thermostat is a Honeywell th8000. Code 350 setting I believe. Thanks
Heatpumps are more complex than an AC unit. Yes, there is a difference between a heatpump and an air conditioner. Where the real difference lies is out side in the condenser unit. There's a defrost board out in the unit, and depending on the brand and model, one of the wires will need to be changed so that the gas furnace will not come on. The problem with this, heatpumps use the heat that is available from the outdoors and transfers it to indoor. When the temps outside drop below 50 degrees, there's not enough latent heat to transfer, thus calling the propane furnace to operate. Without the addition of the furnace, you will not be able to heat the area properly. The only way to remedy this, is to remove the propane furnace and replace it with an electric airhandler with a heat strip for "emergency heat". The emergency heat term is used when the temps drop below the temps I mentioned above and calls for the heat strips to come on.
Feb 03, 2017 | Honeywell Heating & Cooling
I installed a run capacitor for my blower motor on my RUUD ac model UGPH10EBRJR. now it runs all the time. I even disconnected my thermostat and it kept running. is it my thermostat? or something else
An open limit switch may make the fan run all the time. Try disconnecting the Green wire @ the furnace...if that does the trick, then either the thermostat fan relay is stuck, or there is a short between the Red & Green wires somewhere in the thermostat wire.
Jan 18, 2015 | Ruud Heating & Cooling
My gas furnace and heat pump runs at the same time???
its likely the outside control unit board its supposed to only kick on gas only when the temp is at freezing..
or
the inside thermostat is not selected for heat pump, open it an look at the jumper / switch.
or just replace the thermostat , then return it saying you couldnt figure it out. :P
there are a lot more variables here after that you cant know how to check.
Nov 05, 2014 | Honeywell VisionPRO 8000 Programmable...
I Have a honeywell RTH2410 Thermostat I wired it without the blue wire which used to go to X on my old thermostat. Now it comes on with aux heat all the time and I have a Heat Pump. How can I fix this?
What was the old thermostat labels and the wire colors that went to them?
The typical heatpump wiring Terminals are:
R = Red = Hot side of Transformer
C-B-X = Common side of transformer Depending on brand of heatpump
Y = Yellow = Cooling Contactor
G = Green = Furnace Blower
O = Orange Reversing Valve Energize to Cool
B = Blue Reversing Energise to Heat Depending on brand of heatpump.
W2 = White = Auxiliary Heat
You need to be sure where each wire comes from when you connect them to the new thermostat.
The best way to do that is to go to the furnace and see where they are connected. R-Y-G are probably correct, you need to see where the Blue wire comes from and determine what the X terminal was on the old thermostat.
Dec 29, 2009 | Honeywell Electronic Programmable...
Furnace runs but once it gets to teamature it does not shut off but goes in and out of stages
Disconnect the thermostat wires from the circuit board. Tape door switch closed. Put a jumper on R and W on the circuit board. Let the heater run for about 5 min. Disconnect the jumper, furnace should shut down. If it continues to run you have a bad board. When you reconnect the thermostat, look for a shorted wire or a bad thermostat. I suspect a bad board if the furnace is hunting thru the stages.
Nov 03, 2009 | Goodman GMS90703BXA Heater
Thermostat Wiring Problems!!!
. your blue is probably common and if you hooked it to Y you shorted the transformer or blew the low voltage fuse. Green is fan, yellow is AC, Red is 24volt. Is it a heatpump or just ac? I think its probably a heat pump and your brown is your Reversing valve it needs to be hooked to O on the new stat. If its a heatpump your tstat must be a 2heat 1 cool stat w/ aux heat. Without knowing what terminals the wire were hooked to on the old stat you may have to look at whats hooked up at airhandler( furnace) and on A/C (heatpump) tobe able to determine what goes where on the new one.
Sep 20, 2009 | Heating & Cooling
Can you bypass piggyback system if you want to just use heatpump. John
I'm assuuming you are talking about your furnace or 2nd. stage heat, when you say piggyback system. Yes you can go to your thermostat or furnace and disconnect just the 2nd. stage heat wire(see furnace wiring diagram), this will not allow the heat to come on in the furnace but it will still allow the indoor blower to run and the heat pump.
Apr 20, 2009 | Goodman CLQ36AR49 Air Conditioner
Ruud air to air heatpump intertherm propane furnace honeywell th5220d non programable thermostate.fan on furnace will not turn off in aux.mode even though the furnace heat kicks on and off. thank you for...
Make sure fan relay is wired correctly (G) wire. Ensure the fan on therm is not on, it should be on Auto or off.
If your furnace is short cycling because it has to keep heating your home, the delay in the control board may be staying on to compensate for the exchangers getting hot. If it heats normally, then put your attention to your thermostat.
Set the heating system on aux heat only. Fan should not be on, if it does stay on after a heating cycle, see if the furnace is heating normally, and reaching temp as desired before the heat comes off. Then check the therm wiring, pull the face of the therm, disconnect green wire (fan) and try the heating again.
Dec 06, 2008 | Intertherm Heating & Cooling
Carrier Weathermaker gas 8000 will not ignite
1. check indoor unit wiring.
2 check sensar of thermostate.
3if not change thermostate
Mar 25, 2008 | Carrier XHB123D X/Y Series Heat/Cool Air...
Goodman GMP100-5 Rev Furnace Manual
I don't know where you are located, but there is a Goodman distributor in Sacramento, CA. Also in Ontario CA. They are a distributor so they may be able to help you or tell where to find someone who will help. Goodman is also known as GMC or Janitrol.
Jan 07, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
263 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen