I want to wire this to my house breaker panel, I am reading that you have to have a transfer switch and relocate the ground in the generators front panel. My plan was to wire it into an existing breaker in my panel box and putting a male plug near the garage door. Most people i know that use generators for emergency power just back feed the panel with a double male cord. I know that the main has to be off for safety. Just looking for a simple solution without having to buy a transfer switch and i am also reading that the generac transfer switch model 1276 is not capable of switching neutral and to make sure if you use one to make sure my generator has a floating neutral.
  • svlan44 Dec 12, 2008
    Carl is absolutely right, and I am right now in the process of getting a transfer switch. I do realize that this was not the thing to do, and i am educating people i know that useing the ole double male plug thing is a no no, My thanks to fixya and Carl
    Stan
  • svlan44 Dec 15, 2008
    Thanks Toolman Joe,
    I have been looking on the net and I think GE panel is sounding better all the time, next time i got to lowes will look at their product, You are sure right about the cost of some transfer switches, and i'm not looking to spend a whole lot. Just something so I won't be feeding the main line and still be safe.
    Thanks Stan
    Problem Solver:
  • 5 Answers
Most people don't buy a transfer switch because they cost almost as much as the generator. Lowe's sells a very inexpensive one that will work for most people. It is made by GE and costs $92. Lowe's Item #: 42210 Model: TM860S. Good for 60 amps and 8 circuits. It takes standard GE half size breakers but includes the 60 amp main breakers (which are also standard but make use of a novel device that ensures you can't send power back up the pole). It's a great little design and if a breaker ever fails, you can get a replacement at Lowe's or Home Depot.
Joe
Posted on Dec 14, 2008
  • 169 Answers
This is a bad idea in so many ways...
The reason many jurisdictions REQUIRE a transfer switch is to protect the poor linemen who will be working at the high voltage end of the power line that comes to your house. At your end of things you get 220 volts, going the other way you could be powering a transformer that will turn the 220 from your generator into 1050 or more volts. Quite a risk. If you do this and get caught you will very likely face both criminal and civil prosecution. If you're not all that concerned about the linemen, the other risk is that you'll inadvertently motorize your generator (turn it backwards) and blow engine parts all over the yard.
Next is the "male plug" idea. The reason we have female receptacles in the wall is that we don't want the (potentially) 220V live conductors hanging out where someone or something is apt to short out when the generator isn't connected.
I know from hearing it hundreds of times that you're so very much more careful than the average person, it isn't YOU we in the power generation business are worried about, it's the people who aren't you and will be operating the power equipment in an emergency situation.
Please, please consider carefully these safety aspects and at least use something like a manual transfer switch to do this job. A 200 amp manual switch costs less than $500, will add value to your house, and can usually be installed in less than a day.
Hope I've talked you out of this,
Carl
Posted on Dec 11, 2008
AS A MASTER ELECTRICIAN,I THINK ANYONE WHO DOES NOT USE A TRANSFER SWITCH IS AN IDIOT! IF YOU CANT QUOTE THE CODEBOOK AND HAVE EXPERIENCE WITH GENSET THEORY HIRE AN EXPERT! SCREW UP YOUR PLUMBING AND LEAVE ELECTRICAL WORK TO THE EXPERTS;A LIFE MAY HANG IN THE BALANCE.
Posted on Mar 23, 2009
As a master electrician in NYC, I say let the pro's wire your house for a gen. There are issues with grounding and neutrals that must be done correctly. And yes, transfer switch is a must. One more thing, buy a gen that provides true power so that you can operate your electronics. Not all gens are the same. When it comes to gens, price is directly proportional to power and quality. Hope this helps, Alex M.
Posted on Aug 25, 2011
    New Friend:
If you back-feed your electric panel rather than installing a transfer switch get a breaker interlock so there is no possible way you will forget to open the main it is also illegal to back feed a panel with out ether a interlock or a transfer switch and yes for all you code watchers the interlock is in the electrical code book and is a legal way to do it. please never use a double male plug for connection there is a special outlet for generator use you can get them in lowes or homedepot. good luck!
Posted on Mar 29, 2013
You put a double pole breaker on the end of the generator cord set. Turn off the main in the panel put the breaker on the line set in the panel start the generator plug in the line set to the generator turn on breaker at panel end of line set. Depending on generator you might have to turn off all double pole breakers in the panel. If your generator does not put out 240 V. you will have to jump out the double pole breaker to heat up both sides of the panel. In this case you probably will be lucky that you can run a refrigerator and a freezer.
Posted on Feb 16, 2009
Why are these breakers hot and constantly draw .35 amps from the ground bar?
When current is going through wiring and devices it normally operates warm. That is why most wire and devices such as breakers are rated at 70 degrees Celsius. In a panel, heat can be transferred through the buss bar they are connected to.
Breakers will trip for 2 reasons. Overload amperage and heat.
Oct 05, 2016 | Eaton ARC FAULT CIRC BREAKER
How does the wiring go from the own generator to its battery and then to electric panel
the ONAN generator only charges its own battery that it uses to start the machine,the generator itself is grounded with a 6 ft copper rod that is driven into the ground and secured to the ground strap of the generator,the wiring from the generator goes to a transfer switch that is installed ONLY BY A LICENSED ELECTRICIAN! DO NOT ATTEMPT THIS YOURSELF!,the switch is hooked up to your main electric line at the meter and to the breaker box,when the switch is used,it shuts off the main electricity from the company and opens the circuit to the generator only.here is the transfer switch,it can run everything up too 100 amps in your house or only 1 thing like your heat.
Apr 21, 2015 | Cars & Trucks
Can I remove a breaker from panel box cap the wires turn electric back on till I go get a new breaker.
You can but why not get a new breaker first. Once into the panel and you're done.
Nov 28, 2014 | Electric Electrical Supplies
Sorry the whole question wasn't on there. I moved a twenty amp beaker to the left side of the breaker box. It's the one that carries most of my kitchen. Now my kitchen light switch when on shuts on the...
Why did you move from one side to the other? What you say about the kitchen light is not possible. Did you also relocate wires from any other location inside the panel box. Also, is it possible for you to attach photos of your panel and perhaps a list of each breakers circuit.
Nov 21, 2014 | Electrical Supplies
Our 7788F keeps going into a ground fault condition. Need help troubleshooting. John
Ground Fault ???
Troubleshooting Ground Fault
Troubleshooting a ground fault circuit interrupt, or GFI, breaker is pretty straightforward. Troubleshooting the circuit itself can be quite time-consuming.
The GFI breaker is designed with a test button incorporated into the breaker itself.
Pushing the test button should trip the breaker.
On GFI-style breakers the neutral wire going into the house's outlets is connected to the breaker's neutral connector, the white neutral that comes out of the breaker is connected to the neutral bus in the panel, isolating the neutral bus from the neutral wire going into the house.
The test button actually shorts the neutral wire feeding the circuit to the neutral bus in the electrical panel creating a ground fault that should trip the breaker.
It is considered a ground fault because the neutral bus in the main electrical panel is actually connected to the ground bus through the panel's metal casing. What to do if the test button isn't tripping the breaker
Push the test button on the GFI breaker.
The breaker should trip.
If the breaker does not trip, then it may be that the breaker has already tripped and just looks like it's on.
The position of the switch may only move slightly from the on position towards the off position when tripped.
Push the switch on the GFI breaker all of the way toward the off position.
It may take some force to get the breaker to reset.
Turn the breaker back to the on position.
When the breaker has been reset properly you should feel some resistance when pushing the switch back on.
3 Push the test button again and the breaker should trip.
If the breaker still doesn't trip then you should test for power at the screw connections inside of the electrical panel.
Remove the screw that holds the dead front covering the breaker's connections.
Remove the dead front cover.
Test for power with your voltmeter set on AC volts on the highest scale.
For a single pole GFI breaker, touch the black lead from the tester to the silver screw on the GFI breaker and touch the red lead from the tester to the brass screw on the GFI breaker.
You should see 110 volts on the tester. If voltage is seen but the test button won't trip the breaker, then the breaker is bad and should be replaced.
5
Test for power on a two pole breaker by touching the red voltmeter lead to one of screws with a black or red wire connected to it.
Touch the black lead to the other screw with a black or red wire connected to it.
You should read 220 volts or close to it on your voltmeter.
If you read voltage and the test button won't trip, the breaker is bad and needs to be replaced.
What to do if the breaker won't reset and keeps tripping when turned on
6
Unplug everything that is plugged into any of the outlets on the circuit in question.
Try resetting the breaker again by pushing the switch all the way to the off position and then turning it back to the on position.
If it won't reset and trips when the breaker's switch hits the on position, it could be a bad breaker or a problem in the circuit itself.
7
Use your straight-tipped screwdriver to loosen the brass connection screw or screws on the GFI breaker.
Pull the black hot wire, or wires, out of the breaker's connectors.
Loosen the silver screw the white wire is connected to and remove it from the GFI breaker.
8
Push the switch all the way to the off position.
Turn the switch back to the on position.
If the breaker still won't reset, then the problem is the breaker itself and it should be replaced with a new one of the same size, brand and model.
If the breaker resets normally and the test button trips the breaker when pushed, the problem is in the circuit itself and an electrician should be called to find your ground fault.
9
Reconnect the black wire, or wires, to the brass screws on the GFI breaker.
Reconnect the white wire to the silver screw on the GFI breaker.
10
Replace the dead front cover into the breaker panel.
Install the screw or screws that hold the dead front in place.
http://www.hilo-electric.com/blank?pageid=63
Aug 14, 2013 | Computers & Internet
What is the difference between a ground wire and a neutral wire?
Here are links to help, then add a comment:
http://waterheatertimer.org/images/Inside-Main-Breaker-Box-12.jpg
rrrrrrrrrrrr
http://waterheatertimer.org/See-inside-main-breaker-box.html
http://waterheatertimer.org/Color-codewire.html
http://waterheatertimer.org/How-to-wire-T104-Intermatic-timer.html#T104
http://waterheatertimer.org/images/Test-wires-for-voltage-1-600.jpg
http://waterheatertimer.org/images/T104-wire-from-breaker-600.jpg
Always stand on dry boards and never directly on ground when testing live electricity. Do no lean into or touch anything made of metal. Tape wood sticks to tester leads.
240Volt circuit does not use neutral wire. Neutral is used to complete circuit for 120Volt... and that is only function for neutral.
Neutral and ground wires connect back to same wire coming in from the electric company transformer. So in a sense, neutral and ground are same.
However both neutral and ground wires connect to separate busbars inside the breaker box. And then both those busbars are bonded together or joined together ... so ground and neutral become the same thing inside breaker box.
For national electric code, the ground wire runs to each fixture, outlet, motor, appliance etc. The ground wire is essential for safety.
Absolutely the ground wire must connect to motor in case the motor housing becomes electrified after the motor overheats etc.
The ground wire carries no voltage and is safe to touch ... but don't test that theory in event there is funky off-code wiring on premises.
Please add a comment May 2013 for followup, and if you need specific wiring diagram... attach image of your situation
May 28, 2013 | Electrical Supplies
The blower fan on my furnace runs all day ,,, and on the trouble its said if light stay on that its incorrect twinning / polarity what do I do...and i bought a new board for if and still the same thing
You may have a bad ground or neutral wire in the circuit breaker panel for your house. Chack all wire connections and make sure that the black wire from your breaker panel connects to the black wire of the furnace. Check all ground wires in the furnace.
Jan 27, 2011 | Goodman GDS80904BNA Open Flame Heater
How do I run from a 100 amp main panel to a 60 amp subpanel, 125 from my house to the garage
See 60 Amp sub-panel image
Above image shows drawing of 60Amp sub-panel located next to main panel. Drawing shows #6 wire... 125' distance to garage calls for #4 wire. I ran #4 to my barn and have no problems.
Give thought to how many new breakers you want at garage.
See photo of subpanel that holds three 240V breakers
Using drawing as a guide. Replace existing 240Volt breaker with new 60 Amp breaker. Two hot wires connect to new 60 Amp breaker. Neutral connects to neutral busbar.
More space: You can free up space in main breaker box using a tandem breaker. Or by doubling up 2 lightly used 120V circuits onto one breaker. Do not double-up on 240 Breakers
Conduit: You want PVC conduit large enough to fit three #4 wires. Bigger conduit is easier to pull wires ... and maybe later ethernet wire, or alarm wire etc.
Ground wire: You can put a ground rod at garage and run #6 bare copper between sub-panel neutral-busbar and ground rod. Attach ground wire firmly with grounding clamp.
I want you to check with local electrical supply for exact code in your area concerning conduit requirements, grounding, and wire size. Tighten all lugs very tight against wire.
Oct 03, 2010 | Siemens 100 Amp Main Breaker Renovation...
How do i install a 20 amp double pole siemens breaker? i think the one initially installed in my house was put in improperly and it keeps blowing as a result. i have only had the house a few months and i...
It sounds like he was running something at 200 volts using both sides of the breaker, If not, he is definitely using the white wire someplace as the hot and just waiting for somebody to get zapped on it. The breaker could be bad, might be the problem, they do go bad. Just turn off the main, keep away from the big wires feeding the panel, take off your watch and rings, pop out the breaker, pull the wires off, put the wires on the new beaker, pop it back in, turn on the main, if it still breaks, you gotta chase down that white wire, cause something is wrong, I would check whatever it is that it powers to make sure it is right at the receptacle end. It should be marked. Hope this helps.
I just read the properly grounded part, if he is using the ground for the neutral, that is the problem, most newer boxes are polarized, meaning ground and neutral are separate, check out that wire, and see where it goes. If it is running something at 220 volts, mark the wire with black tape, and you should run a neutral to it to be safe.
Jul 04, 2010 | Electrical Supplies
Subpanel feeder
Run 1 1/2" to 2" gray pvc conduit.
Mar 30, 2009 | Cooper Wiring Devices INC #BP4404V IVY...
Generac 5606 XP Series XP8000E 12,000 Watt 410cc OHV Portable Gas Powered G Logo
2,622 people viewed this question
Top Generac Measuring Tools & Sensors Experts
deton8 von Splosion
Joseph Mueller
Joseph Mueller
David Ellis Rhea
Are you a Generac Measuring Tool and Sensor Expert? Answer questions, earn points and help others