Question about Marley Electric Hydronic Baseboard Heater, 58" 240V/1250 Watts
Have installed MD26 Line Voltage thermostat Heat comes on when turned on and won't shut off. If temp is turned down just enough to turn off, it never comes back on. Wiring seems correct.
SOURCE: marley md26 line voltage thermostat
The Black Wires from the md26 are your load(the heater) and the red lines are your line(power). The lines are also paired up on the thermostat with a red and black on the left and are red and black on the right. In the actual heater connect the black to the black wire and the white to the white and connect the grounds. In the thermostat connect the black from the heater to left side black( remember there are pairs left(black, red) right (black, red) and the white to the right side black connect the black from your power to the left side red and the white from your power to the right side red. Should be ready to go.
Posted on Nov 19, 2008
Have installed a new Honeywell thermostat. The fan does not turn off even when the room has reached the desired temperature. I originally replaced th ethermostat because the old one the fan ran forever and...
Most T-Stats have a On / Auto on a forced air system. On means the fan will run all the time even if it is not calling for heat. Auto only runs when calling for heat. Does the fan turn off in the auto mode at all? To test it...BE SURE THE FAN IS IN THE AUTO MODE ON THE T-STAT... Turn the thermostat all the way down and keep it there for appox 15 mins. If it is wired properly and the fan limit is set properly the fan should turn off. If it doesn't it is not the thermostat were the problem lies.
Most forced air units have a fan / high limit switch. There is a setting on the switch for the fan to turn on and a setting for the fan to turn off or it has a setting and a differental switch for it to turn off/on. Example - the fan comes on when the temp in the heat exchanger reaches 110 degrees F and will shut down at 95 degrees F after the thermostat is satified...this would hav a differental of 15 degrees F. It may be set to low and the fan continues to run long after all of the heat has been removed from the heat exchanger. This in turn will cause cool air to be coming out of the registers.
Mar 09, 2011 | Honeywell CT87B ROUND HEATING&COOLING...
Tip
Thermostat Line Voltage How to Install or Replace
You either have a new line voltage thermostat or have to replace your old line voltage thermostat. In either case the process is much the same.
  1. Make sure that all power is turned off at the breaker panel. Most heaters that use a line voltage thermostat usually use 240v current so the breaker will either be a double pole breaker or you will need to turn off two single pole breakers to kill all of the power.
  2. Check to see which wires are hooked to the breakers. In most cases it will be the red and black wires, but I have seen many times that the white and black wires were used. Often there is no red available when the white is used.
  3. Take out the two screws that hold the thermostat to the junction box. When you get the thermostat out make a note of which wires go to the heater (load) and which wires are coming from the breakers. (line)
  4. If you have a single pole thermostat installed one of the sets of wires may be wired straight through the box or have the line and load wires connected directly in the box. With a double pole t-stat you will have both sets of wires running through the t-stat.
  5. Remove the old thermostat and wire the new t-stat in the circuit with the load wires hooked to the load or heater and the line wires hooked to the wires coming from the breaker. Make sure to get a very good tight connection as resistance loads will heat up quickly if good contact is not made. This poor connection can and will start fires.
  6. Turn the power on and check the heater for heat output.
  7. Turn the power back off and carefully screw the thermostat to the junction box securely. Then you can reapply the power to the circuit.
Now you are up and running with a new line voltage thermostat installed.
http://www.fixya.com/support/r3894275-manual_honeywell_find_honeywell_manuals
http://www.fixya.com/support/r3623083-thermostat_wiring_terminal_designations
on Jan 16, 2010 | Heating & Cooling
The heater does not stay on long enough to heat my garage. it will come on for 3 to 5 minutes and shut off. it comes on again in 5 to 10 minutes for 3 to 5 minutes again. the heat is good when it runs....
You could tripping the high temp limit this will be located near the heat exchanger When it shuts how long does the blower motor stay running? Do you have a meter?
Dec 15, 2010 | Fahrenheat FUH5-4 Heater
Buzzing sound when aux heat comes on
Sounds like it could be a effiency function to warn you that the heat elements are on. Check your thermostat manual and see if you can turn this feature off. If this is not a feature then the thermostat may be wired wrong or something in the circuit may be trying to short out.
Jan 04, 2010 | Honeywell Electronic Programmable...
RHEEM OIL FURNACE MODEL ROBD 067 LBEA BLOWER
You will likely need to install an isolation relay in the W circuit from the thermostat. Some thermostats rob a small current through the W circuit to power the thermostat. This small current can be enough to start the fan circuit timer. You can test this by disconnecting W at the furnace and allowing the timer to shut down. If the fan shuts off with the W disconnected you can install a simple relay.
The relay coil will be connected to Common on one side and the W from the thermostat to the other. Then you will run a wire from R on the furnace to the relay and from the N.O. Contacts to the W terminal on the furnace. This will kill that signal that is starting the timer and the W can steal it's power through the coil back to common.
Dec 23, 2009 | Honeywell Electronic Programmable...
Rheem RHQA Heater:Blower works but no heat.
Is there a setting on the thermostat for Auto or Fan? If so, make sure it is in the Auto setting. You will have a contactor that turns on the elements and a relay for the fan. Follow the wiring diagram to see which relay energizes the fan then unplug it to see if the fan stops.
Nov 02, 2009 | Heating & Cooling
Gas heater shuts off & won't come back on
sounds like the thermostat replaceing it should help you could try cleaning the old one they can get dust it them
Feb 25, 2009 | Honeywell CT87B ROUND HEATING&COOLING...
Thermostat seems to be working, furnace does not always turn on
Joss sounds like the anticipator setting on thermostat i would replace it with a digital it will be more actturat . The furnace has to go over temp setting to turn off
Jan 15, 2009 | Honeywell Electronic Programmable...
Room temp is not where it should be before furnace shuts down
Did the installer check the amperage at your thermostat and then adjust the heat anticipator? Or you may need to have the blower time settings changed to suite your needs. Get them back in to check.
Nov 10, 2008 | Heating & Cooling
Marley md26 line voltage thermostat