Question about Goodman GMS90703BXA Heater
No Heat-Inducer motor doesn't start ?..humming noise only..warm..
Getting 1 blink on circuit board..means problem could be gas valve or flame sensor?
Didn't see any cracks in igniter/took flame sensor out and cleaned it..still nothing
Is there a relay that could be out? But, if I turn the fan to ON at the therm. it comes on OK and normal air is blowing thru the vents.
Can you turn the fan ON and then click on the HEAT to get heat?
Please help..down in the 30's.
  • 1 more comment
  • SILKYR Dec 07, 2008
    Oh, forgot to add that it's a Goodman GMP100-5 furnace
  • SILKYR Dec 11, 2008
    Thanks for the advise. The 1 blink on the board was confusing. Replaced the inducer motor and it fired right up..although the board is still doing the 1 blink...I suppose that problem will rear it's ugly head soon and will have to be dealt with...maybe a new board or flame sensor or gas valve. But at least for now with it in the 30's ..we have HEAT!
    Note: the replacement motor is different from the original in that improvements have been made...you can spin the cage without taking off the assembly and it has male lead blades where as on the old one you couldn't spin the cage and the wires went inside the motor.
    So when replacing it, you have to cut the wires and put on female connectors and there were no instructions so wasn't sure which wire went to which lead so just did white to left and black to right...guess it was correct since it worked.
  • JudieG Jan 21, 2009
    I have a Goodman 90 Plus with a bad inducer blower. I've looked on line for a replacement with no luck. Can you tell me where I might find one?
  • 1,420 Answers
Bad inducer motor most likely. Check the leads and plug. If it just homms, it is stuck. Check to see if the drain hoses are free of moisture. Can you get to the shaft to spin it to see if it is free?
Posted on Dec 08, 2008
Amana Air Command 90 furnace LED light blinks 3 times pause 3 times
TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.
2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.
3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.
4 BLINKS Open limit switch Verify continuity through rollout switch circuit.
5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.
6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.
8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.
9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.
10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.
12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
Nov 11, 2013 | Patton Electric Patton PUH680-U Electric...
Hi :) I have the Trane Furnace that just turn on
on older tranes if 120v power is reversed it would do that try switching leads on pigtail to board. make sure to unplug first!
Oct 31, 2013 | American Standard Trane Ge Gas Furnace...
Goodman gms80903bna light blinks once fan runs all the time,
I believe this code is ignition failure.
Turn power off and after 20 seconds turn power on with thermostat calling for heat. Vent blower should come on first. After a bit igniter should lite up. You should hear click noise of gas valve open up. If igniter does lite and you hear click noise, flame should come on for a few seconds minimum. If igniter doesn't lite and you hear click noise from gas valve, igniter is bad. If flame lites and then goes out, flame sensor probably needs cleaned. Both igniter and flame sensor are in metal plate under burners. Igniter has 2 wire going to it and flame sensor has one wire. If you think it is flame sensor you can remove with taking it out with 1 1/4" hex screw. Flame sensor will have white film on it if it needs cleaned, clean with steel wool or a dollar bill. If it isn't weither of these it is gas valve or circuit board.
Jan 27, 2011 | Goodman Heating & Cooling
Carrier 58sxc120 won't ignite and I get a fault code blinking light of short long short don't know what it means.
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 24, 2010 | General Heating & Cooling
No blinks normal running igniter glows gas comes on wont run
Check for 24 volts across the gas valve when Ignitor is glowing. If no, bad board. If yes, bad gas valve or blockage.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 05, 2010 | Goodman GMS90703BXA Heater
Red light blinking continuosly meanig gas valve relay short how can I fix myself - furnance only blows cold air
You will need to check for 24 volts AC to the gas valve after the igniter starts sparking or glowing. If you have it but it does not open, bad gas valve and you will need to replace it. If you are not getting 24 volts after it starts glowing or sparking, you have a bad board.
Jan 16, 2010 | Heating & Cooling
Goodman gmnt060 3b doesn't light
check for 24vac between wires on gas valve about 5-10 seconds after ignitor starts to glow. If ignitor does not glow, check for 120 vac to ignitor after inducer goes on.
First...sequence of operation..power to W, inducer motor gets 120v and starts, 10-15 seconds later, ignitor gets 120v and glows, 5-10 seconds, gas valve gets 24v and opens, after 3-4 seconds the flame sensor approves flame and unit stays on. If this is not happening, it has to be in this sequence. Which ever is not happening and you do have voltage to that component, that component is bad. If you are getting a error code on board after it tries to light, pay attention to the code. if a 1 lock out code, that just means it tried 3 times and did not recognize a flame.
Jan 06, 2010 | Goodman GDS80904BNA Open Flame Heater
FURNACE COMES ON AND SHUTS DOWN WITHIN 15 SECONDS
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control). When all else fails, check the ground connection for corrosion.
Nov 23, 2009 | Heating & Cooling
Goodman GMP 125-4 one blinking light code. Gas valve has been replaced (at cost of $443). Didn't fix problem. Same co wanted $415 to replace circuit board. I did it myself for $99 part. Still same problem!...
One blink means it didn't light after a number of attempts. You replaced the circuit board and gas valve. Read on for some suggestions. On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Nov 18, 2009 | Goodman GDS80904BNA Open Flame Heater
Goodman GMS90703BXA Heater Logo
1,200 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others