Question about Intertherm Heating & Cooling
Ruud air to air heatpump intertherm propane furnace honeywell th5220d non programable thermostate.fan on furnace will not turn off in aux.mode even though the furnace heat kicks on and off. thank you for any info.Ray
  • 85 Answers
Make sure fan relay is wired correctly (G) wire. Ensure the fan on therm is not on, it should be on Auto or off.
If your furnace is short cycling because it has to keep heating your home, the delay in the control board may be staying on to compensate for the exchangers getting hot. If it heats normally, then put your attention to your thermostat.
Set the heating system on aux heat only. Fan should not be on, if it does stay on after a heating cycle, see if the furnace is heating normally, and reaching temp as desired before the heat comes off. Then check the therm wiring, pull the face of the therm, disconnect green wire (fan) and try the heating again.
Posted on Dec 06, 2008
How do I reset the temp my heat pump switches from electric to gas. It runs much more economically on electri than on propane. The thermostat is a Honeywell th8000. Code 350 setting I believe. Thanks
Heatpumps are more complex than an AC unit. Yes, there is a difference between a heatpump and an air conditioner. Where the real difference lies is out side in the condenser unit. There's a defrost board out in the unit, and depending on the brand and model, one of the wires will need to be changed so that the gas furnace will not come on. The problem with this, heatpumps use the heat that is available from the outdoors and transfers it to indoor. When the temps outside drop below 50 degrees, there's not enough latent heat to transfer, thus calling the propane furnace to operate. Without the addition of the furnace, you will not be able to heat the area properly. The only way to remedy this, is to remove the propane furnace and replace it with an electric airhandler with a heat strip for "emergency heat". The emergency heat term is used when the temps drop below the temps I mentioned above and calls for the heat strips to come on.
Feb 03, 2017 | Honeywell Heating & Cooling
How can I connect an Intertherm furnace with a heat pump to a new Honeywell thermostat?
Ensure that that thermostat is for a heat pump and has connections for the emergency heat strips.
Feb 02, 2016 | Heating & Cooling
Have an Intertherm thermostate in mobile home controlling gas hearing and elec ac. Blue wire to thermostat connects to the "A" terminal on the thermostat...Blue wire goes to a terminal on the...
If there are only two wires going to the thermostat? Then you will not be able to use a Digital Programable stat. Intertherm and Coleman furnaces do the switching different than regular furnaces. They use the switching from heat to AC at the furnace with the rocker switch. They use the thermostat to either break the connection or make the connection. They use a heating only thermostat.... Hope this helps
Jan 02, 2011 | Intertherm P3RA-048K Air Conditioner
Ruud UBHC AC System - Provides no Aux Heat
Tried this on my unit today, and observed the same results, but got Aux Heat (with A setting), if the H (blue wire) connected to B terminal, as per instructions for my 6036 Ritetemp. However, in this case, when the set temp is reached, I hear the click, but HVAC still blows aux heat indefinitely.
I also have RUUD UBEA 17J10..., and replaced my old honeywell with 6036, and can't get heat pump working. Both of my units are 14 years old, so I'm thinking to replace them soon.
Jan 06, 2010 | Ruud UBHC Air Conditioner
THE AIR HANDLER IN SET IN 75 DE GREE, THE CONDENSING UNIT GET OFF BUT THE A/H IS RUNNING AND DON'T STOP UNTIL THE C/U START AGAIN Y GET AGAIN THE 75, MY SYSTEM IS A 5 TON 12 SEER BOTH ARE INTERTHERM
1 Do you have a digtal thermostate?
Do you have GAS ELECT OR HEATPUMP
All of the fan setting have a dip switch so the fan can be set to match
the type of heat you have
2. is the fan switch in the on poision
Oct 28, 2009 | Intertherm Heating & Cooling
I have an old 1973 Mac 1199 Intertherm propane furnace The burner will come on and it takes a long time for the blower to come on Sometimes the blower wont come on at all and after awile the burner will...
Replace the fan limit switch. It is sometimes mounted in the ductwork and sometimes just below the ductwork in the furnace cabinet. Note where the little arrows are pointing to on the temperature scale so you can set the new control to the same as the old. Usually this control is made by Honeywell and may have three wires going to it.
Oct 20, 2009 | Intertherm Heating & Cooling
One honeywell to another
you need to program the thermostat for the reversing valve "O" it will tell you how to do this in the manual. you will need to chang from "O" to "B" or "B" to "O" depending on how its set.
Jun 24, 2009 | Honeywell Programmable Thermostat Heater
Intertherm propane furnace makes popping sound when running
It sounds like you have a possible hole in the heat exchanger. Turn the heat off and turn the fan on. If you feel any air coming back out of the heat exchanger, you have a hole. A yellow flame is not a good sign. I would even consider having a service professional come out and take a look.
Apr 05, 2009 | Intertherm P3RA-048K Air Conditioner
Manual Thermostat replcaement with Programmable Digital unit.
Hopefully there are markings on the old t-stat as to what terminal is what.
on the honeywell 8000 use the heat pump labeling and then the standard wiring would be
R- red
AUX-white
Y- yellow
B- O/B
C- black
G- green
There should not be a bare wire, it probably just has the insulation stripped back way too far.
You should probably open the furnace and compare the terminal label in the furnace to the wire color. normally yellow and blue pass through the furnace and are wire nutted to wires going to the outdoor unit. In the furnace the white wire will connect to the w or w1 terminal. also, you will need to set the Honeywell stat to have the following parameters.
170-7
190-1
200-0
other parameters that I did not specify, you may read the manual and make your own decision but I recommend factory settings for the other parameters
Jun 14, 2008 | Ruud UBHC Air Conditioner
I tried to replace my digital manual Honeywell thermostat that is only 6 months old (new construction) with a programable thermostat. I followed the instructions marking the wires and connecting them up...
Your "R" terminal is basically your "hot" and your "C" terminal is basically your "neutral" to simplify explanation. The Furnace supplies the "R" power to the thermostat and then depending on what wire the thermostat sends the power back on determines what the system does. The thermostat terminals are as follows "G" is fan, "W" or "aux" is elect heat, "Y" tells the outdoor unit to run, "O" or "B" tells the outdoor unit whether it is heating or cooling, and "E" is emergency heat. "G" should connect from the t-stat directly to the furnace and go no further. "W" or "aux" AND "E" should both connect to your "W" or "W1" terminal in the furnace, there should also be a "W" connection to the heat pump ( this allows the H/P to turn on the elect heat when the unit defrosts) "Y" and "O" or "B" may or may not connect to a terminal in the furnace, usually they just pass through the furnace from the t-stat to the H/P and get wire nutted in the furnace. Now, here is the key. As I mentioned previously "O" or "B", a system will only use one or the other. The entire industry (except for Rheem and Ruud) uses the "O" terminial which has 24v on it when you are cooling and no power when you are heating. Rheem and Ruud use the "B" terminal which is just backwards, 24v in heating and no power in cooling. This is all for a heat pump, If you do not have a heat pump, then disregard the references to "O", "B", "E", and "aux". You will have R-power on red wire, W-heat signal to furnace, G-fan signal to furnace, and "Y" cool signal to outdoor unit.
Jun 08, 2008 | Honeywell Heating & Cooling
Heating & Cooling Logo
178 people viewed this question
Top Intertherm Heating & Cooling Experts
Dennis Boxerman
Dan Webster
Dan Webster
Bill Long
Are you an Intertherm Heating and Cooling Expert? Answer questions, earn points and help others