Replace the flame sensor, clean the burners to ensure you have a good clean burn pattern and the flame is properly reaching the flame sensor.

Look for a flashing LED and determine what the failure code is.

Posted on Dec 06, 2008

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Why heater coils glow?


It sounds like you're describing one of two things. The hot surface ignitor in a gas-fired furnace, or the resistive heat strips in an electric furnace.

The hot surface ignitor in a gas-fired furnace lights the burners. This ignitor in modern furnaces serves the same purpose as the standing pilot flame did in older furnaces. It provides the required heat to ignite the gas at the burners. Without an ignition source, a gas-fired furnace cannot provide heat. When the ignitor is activated it will glow bright orange or yellow.

The resistive heat strips in an electric furnace actually provide the heat to a home or building. When the furnace turns on, the heat strips are activated and usually glow orange when they reach peak temperature. In almost all cases, the heat strips are not easily seen or accessed without removing covers or panels inside the furnace.

Feb 28, 2011 | Heating & Cooling

1 Answer

I have central air ( Dimond 80 York Heating Air conditoning Unit ) My air conditoning unit has stopped working. The board has checked out ok.but there seems to be a voltage problem some where from inside...


Try the following step.....

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).




Jun 08, 2010 | Heating & Cooling

1 Answer

I have a carrier 58sx040. Sometimes after the pilot comes on the main flame will start then stop about every 3 seconds. This problem intermittent. There is always a noise coming from the gas inlet when...


Dirty flame rod, polish it with a scrub pad.

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Mar 13, 2010 | Carrier Heating & Cooling

1 Answer

Goodman unit. when i turn it on the blower fan and the exhaust fan comes on butit does not lite no flames at all. i don't even hear the gas click in.


On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Feb 15, 2010 | Intertherm P3RA-048K Air Conditioner

1 Answer

I have an americanaire ultra sx 80 furnace that if it does start up the 1st time, the induction motor continue to run and it will not start


On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Jan 04, 2010 | Heating & Cooling

2 Answers

The exhaust blower starts for about 15 seconds then shuts off. several minutes later, the same thing happens - over and over


goodman furnance the exhaust fan starts, igniter glows hot, all burners lite up & will burn for about a minute and shuts down . I think it senses the room blower does not start so it shuts down.

Oct 20, 2009 | Ruud UBHC Air Conditioner

1 Answer

Rheem gas furnace pilot lights, but no burners or fan


If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.

Jan 06, 2009 | Heating & Cooling

1 Answer

The burners go out before the fan comes on


Replace your flame sensor, but before you do that, see if you can clean it with light wool, or emery cloth, or light sand paper. It's a metal rod that points in the current of your flame.

Dec 05, 2008 | Heating & Cooling

1 Answer

Burners go out before the fan starts


that makes no sense? the door on does exactly the same thing as you holding the switch closed and neither has anything to do with the problem you are describing. if door were off nothing would happen. if door was on ,nothing would happen unless the switch was closed. it may be coincidence, but sounds like the unit is not proofing the flame. look for a little needle like sensor that protrudes into the flame path in front of a burner. when the burners light it senses flame and tells gas valve burners lit and its ok to stay on. then heat builds and the fan is briught on. once in a blue moon the overtemp sensor trips open prematurely as soon as the burners start to heat up. it is a little wire in , wire out sensor above the burners that protreudes into the bulkhead above the burners. if it is cold and open its bad. if you jump it and burners light and stay lit and fan comes on its bad. fairly cheap and easy to replace. you may have an old fan limit switch the rotates like a spring to bring the fan on as it heats up, then turns off burner if its gets to hot or is set to low. it also turns fan of as burners cool down.

Dec 05, 2008 | Heating & Cooling

1 Answer

I have an electonic start furnace. Everything kicks on but the heat. It's like the burners won't light up. I don't have a lot of money to fix it so I was wondering if I could somehow trouble shoot the...


yes! The furnace goes through 4--steps for complete run time. Step -1 the small vent fan comes on, and prove it thru the small rubber tube that sucks the switch close and tells the c.b. its turnning, Step 2.. the glow plug glow and 08 seconds later, Step -3 then the gas valve open and dump in gas ,which ignites and heat up the box. and proves it got flame through a flame sensor (pin) sticking in the flame .& Step -4, the box heats up to a predetermined temp. and turn on the fan! thats all. Thank-you-very-much!

Aug 27, 2008 | Intertherm Heating & Cooling

Not finding what you are looking for?
Heating & Cooling Logo

Related Topics:

113 people viewed this question

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

paulcarew

Level 3 Expert

2028 Answers

Dan Webster
Dan Webster

Level 3 Expert

8205 Answers

Cris Sparks
Cris Sparks

Level 2 Expert

338 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...