Furnace attempted to start but failed after so manay tries. This may help you.

Sequence of operation, Gas Furnace.

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).

This is why we technicians earn the big bucks!

Posted on Dec 05, 2008

  • Level 1:

    An expert who has achieved level 1.

  • Contributor
  • 1 Answer

My led light keeps blinking once i have a goodman furnace what could it be please help me its cold

Posted on Dec 08, 2009

5 Suggested Answers

milten1
  • 1304 Answers

SOURCE: goodman furnace indicator light flashes four times

this is a overlimit cut out,
whats happening is the internal cabinet is getting too hot, so the system should shut down until that temp drops below safety levels,
this particular problem, usually deals with air flow, your not getting the proper amount of air through the blower.
i would check, your filter here, usually this is the first thing to check before trying any sort of re4pair

Posted on Oct 17, 2009

djnick989
  • 1067 Answers

SOURCE: 1993 goodman status light 4 times blinking

Witch blower is running, the inducer or the systems blower?
System blower could mean the the high limit is opening and shutting down the systems gas train, I would check this out first.

The other problem could be with the pressure switch for the gas train, it is supplied from the inducer motor, check to see if it is operating fully.

HSI boards do go from time to time, this sounds more like a system control problem.

Posted on Jan 25, 2008

machtcl1
  • 61 Answers

SOURCE: goodman furnace 4 blinks

The limit switch is usually a little fiberglass board (2" x 3") with two wires going to it. Usually held in by two 1/4" or 5/16" hex screws. These go bad if you have insufficient air flow through the furnace.(dirty filters,undersized supply or return ducts)
Sometimes they will reset if you tap on them or clean them.
The limit control will have a rating printed on it stating its trip and reset temps.(L170 - 30f or something like that) Make sure to replace it with the same rated switch.

Posted on Jan 02, 2009

  • 1915 Answers

SOURCE: I have a Goodman GMPN080-4 furnace. The light on

Hi 3 blinks should mean it is the pressure switch there should be a code in the manual or inside of the door

Posted on Jan 30, 2010

shastalaker7
  • 1515 Answers

SOURCE: goodman furnace fault light blinks 3 times it

Hi, what you have to do is where you see this light flashing, there is a circuit board. Remove the panel. If everything goes black, you have a door switch on the perimeter that you can tape down to restore power to the furnace. On the panel, you will find a error code sheet glued on it telling you what the flashes mean. 3 flashes may say you have an open pressure switch, or 4 may say the inducer motors off or something else. It will almost troubleshoot itself. Find out what the 3 flashes mean and if you cant figure out what to do, contact me and I will walk you through it. It sounds like you have a dirty flame sensor, or an intermittent problem in the ignitor module. Check it out as it will tell you.
Sincerely,
Shastalaker7

Posted on Feb 25, 2010

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

My heating blanket is flashing on and off wat does that mean


It means it is probably burnt out at that setting. Try another setting and see if the light stays constant.

Flashing light on any appliance usually tells you it is not working or you haven't completed all steps (like in the case of a coffe maker for example).

Mar 04, 2015 | Heaters

1 Answer

I have a goodman furnace GMP100-4 REV B..about a year ago it was not working. The fan would start but it would not ignite. We found out we need a new ignitor and it was a good quick easy fix. Now a ye


Any light flashin on the control board? If not then look for a small fuse blown on the board. See lights a flashing count them flashes

A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

Nov 29, 2011 | Goodman Heaters

1 Answer

I have a Goodman GMP 125-5 furnace. It had a 3 light code i replaced the presure switch now it is giving me a 1 light code please help


A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
themobilian_3094.jpg

Oct 28, 2011 | Goodman Heaters

1 Answer

I have goodman GMP series furance the furnance and gas comes on and fires up then goes out flame sensor is good what else could be wrong


Improper ground from control to burner.
Incorrect electrical wiring, check polarity.
Tubing partially clogged between inducer and proving switch.

A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

Oct 18, 2011 | Goodman GMS90703BXA Heater

1 Answer

Suddenly not working im not sure if there even is a pilot to be lit


Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

Feb 03, 2011 | Goodman Heaters

2 Answers

What mean L1 and L2 for the connexion of the heater


L1 Means Line Voltage L2 means Line Voltage

If you have 220 as your supply voltage than one side would go to L1 and the other to L2.
Hope this helps if you still have problems post another post along with more information as to what voltage you have.

Jan 02, 2011 | Dimplex EF621C Electric Wall Mounted Panel...

2 Answers

What does oh mean on hot tub a cal spa


'OH' means 'over-heat'.

Basically the high-limit temperature sensor has detected a temperature far in excess of what it should be.

Check the filter(s), water flow, pump etc....

Regards,
Ian.
http://hottub.synthasite.com

Jan 26, 2010 | Coleman (5040B750) Patio Heater

1 Answer

Flashes error number 62?? What does this mean


On my Rinnai Avenger 25 , this code means that your unit has a faulty fan motor and you need to do a service call. Hope this helps.

May 20, 2009 | Rinnai RHFE-1004FA 38,400 BTU Energy Saver...

5 Answers

Rinnai Convector 516TR Heater


Hi, Here is the link to the manual. I think something like 'thermo coupling' probably means you need a technician! 
http://www.rinnaisales.co.nz/tradesmart/rinnai2/pdfs/installations/153.pdf

Jun 24, 2008 | Heaters

Not finding what you are looking for?
Goodman GMS90703BXA Heater Logo

3,574 people viewed this question

Ask a Question

Usually answered in minutes!

Top Goodman Heaters Experts

paulcarew

Level 3 Expert

1904 Answers

Dan Webster
Dan Webster

Level 3 Expert

8147 Answers

Ken Thomas

Level 2 Expert

118 Answers

Are you a Goodman Heater Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...