Have an amana central air duelfuel heat system.when aux heat[gas] heats the house and shuts off the fans still blow for 3 to 5 minutes with the last couple of minutes being cold air which cools the air it just heated. also heatpump will start heating when it comes on then after 3 or 4 minutes it starts blowing cold air like when the air conditioner is running.i have had problems from day of install 4 mounths ago with problems that keep coming up. please i need help fast i do not think company that istalled has a clue.by the way it came with a 10 year parts and labor warranty but if can't fix the unit what good is that.
  • Danny Clark
    Danny Clark May 11, 2010
    This would take a true, on site diagnostic to be sure.
    But it sounds like you may have a bad defrost control board.
    Here's how it works.
    Heat pump is in operation, the indoor coil gets hot, the outdoor coil gets very cold. It routinely needs to defrost.
    When it goes into defrost mode, the refrigerant reverses flow causing the indoor coil to get cold and the outdoor coil to get hot, thereby defrosting the outdoor coil. Basically, to defrost, it is going into AC mode.
    During that time, the defrost board is supposed to bring on the secondary heat source, in your case, the furnace. This keeps hot air coming out instead of cold during that defrost cycle.
    You need to get an accurate temperature reading device and determine what temperature the air coming out of the vents is when you say it is cold.
    If it is room temperature, during the few moment right before shut down, that is normal. Your hand is roughly 94 degrees so anything cooler than that will feel cool.
    If your indoor air is 70 degrees, when the fan is circulating air only, it will be blowing 70 degree air. That will feel cool to the hand.
    If you discover the air coming out of the vent is 10 to 20 degrees colder than the air going into the return, then yes, the system is in cooling mode, or defrost, and you probably have a bad board.
    It is normal for the blower to continue to blow for a short time after the furnace shuts off, as it has to cool off the heat exchanger to prevent premature failure. (cracks)
    If you are used to a gas or electric furnace, you are probably used to 100 to 160 degree air coming out if the vents. That will of course feel very warm.
    When a heat pump is in heat mode, the temperature can range from 80 to 120 degrees depending on how cold it is in the home.
    (40 degree indoor air, 80 degrees from the vents is normal. 80 degree indoor air, 120 is normal)
    If the heat pump is producing 95 degree air at the vent, and your hand is 94/95 degrees, (Core body temp 98.6) then it will not feel worm to the hand, but 90 degree air will certainly warm the home.
    Thus the need for a good fast reading thermometer.
  • 85 Answers
Change your heating delay to shut off sooner, you can find this in the installation manual. Also the Thermostat may have delay after heat as well. It is true there could be many variables, but it also sounds like the Heatpump is not charged properly, you will have to have a different tech come out and check that. No need to have the installer mess your system up any further. This solution will only correct the auxilary heat, your heat pump on the other hand will require expert skills.
Posted on Dec 05, 2008
Central heating and air fan not working
it may have frozen and loosened someting it might just need to be seviced
Feb 27, 2014 | ATP HVAC - Heating, Ventilating, and Air...
I have a ac central unit that has freon put in it, but it still blows out hot air inside the house.
Need a bit more info. Do you hear the compressor come on? Is your Tstat in the cooling mode? Shut it down for a minute and turn it back on. you should hear the indoor fan come on . outside fan come on and the compressor come on the sametime as the out door fan comes on.. Freon is just a gas that is used to exchange heat .
Jun 26, 2011 | Heating & Cooling
Every time my heat pump turns on, the blue auxilliary light comes on, and it only blows icy air. I do not want to use that much power, so I turn it back down a few degrees. Now, it is 50 degrees in the...
A heat pump starts losing efficiency below 30F or so. The aux. heat helps the heat pump keep up with heat demand. The Aux heat can be electric heat strips or another type of heat. Check to make sure you have power to whatever type of aux heat you have (breaker not tripped, no overloads tripped). If it is electric heat check the heat strips to make sure they haven't burnt in to. Hope this helps.
Jan 10, 2010 | Amana PTH123B25AJ Heat Pump Air...
I have a central air and heat heat uses gas so when the heat is on should the main fan be turning
Typical systems are designed with a thermostatic "fan limit switch" which protrudes into the heater (house air portion of the passages). The "fan limit switch" is mounted to, and protrudes into the duct within the burner section of the heater, near the heated metal.
This switch triggers the circulating fan to turn on only after the sensor (thus air) within the duct has reached well above ambient temperature. This design prevents the fan from coming on sooner and the system blowing cold air, which people don't like.
Depending on system design, installation and current operating conditions, the time delay from main burners on to fan on can be up to a couple of minutes.
This same limit switch, if the temperature goes high enough, will also turn the gas valve off; a fire safety function.
Jan 06, 2010 | Goodman CKL49AR49 Air Conditioner
Central heat does not blow hot air, just warm air weakly
Sounds like some of the elements are not working. You being in Florida they may not have put very many elements in. It was 61 degrees last week. I know because I'm a Dolphin Fan. You will need a current sensing meter to check the elements.
Jan 04, 2010 | Heating & Cooling
Gas heater doesn't stay on longer than 5 minutes.
It sounds to me that your air flow is restricted somewhere. The first thing to check is your air filter. If that gets real dirty your restricted air flow will cause the hi-limit(hi temperature limit switch) in your heat exchanger compartment to over heat and open up your gas valve electrical circuit,thus, shutting off the gas to your burners. After the hi-limit switch cools down the furnace will go back to heating again then it will overheat again(you get the picture?) If it keeps cycling on and off like that the house will never get warm if it is cold outside. If your air filter is reasonably clean(you should be able to see light thru it easily) then the secondary heat exchanger could also be dirty, this is located above the indoor fan housing, you would need to pull the indoor blower assembly out of the furnace and look up above. The secondary heat exchanger looks similar to a radiator will fins. You can use a medium stiff plastic brush to brush the dirt,hair, whatever off of it. Another problem spot would be the cooling evaporator coil (if you have central airconditioning) located most likely above the furnace in the plenum(if your furnace is in a basement). This usually is difficult to access if an access cover wasn't installed when the airconditioning was installed. I would recommend an experience service tech to clean it for you. Also make sure all you supply air registers and return air registers are open . These are the things I would check first. Good luck!!
Nov 19, 2009 | Goodman GMS807034ANA Heater
Have a Amana a/c heater central furnace. Model number PGA30R0452A. The a/c part works fine. The heater part does not turn on sometimes. We have to keep turning it on and off to get to work. No matter what...
When you change from cooling to heating the fan will not come on immediately. A solenoid valve is energized (check that it is working) and operates a reverse valve, changing the gas flow in the system. It takes a few minutes for the system to build up sufficient heat and then the fan will come on. The humming sound is very likely coming from the solenoid valve. Make sure the air filters are clean. Obstruction caused by dirty air filter can prevent the air sensor from sensing the return air temperature.
Nov 18, 2009 | Heating & Cooling
1997 Amana 2 or 2.5 ton heat pump, 13 seer - air handler only blows 4-5 min
do you have a totaline t-stat. they and some other brands have a fan recirculation setting in the installers menu.
this is assuming that this happens in addition to the heating or cooling normally
Jul 02, 2008 | Amana PTH123B25AJ Heat Pump Air...
Air handler only blows air for 3-5 minutes before shut off & not cycling frequently
Sounds like it could be a very weak run capacitor on the blower motor. Run capacitors are sized specifically to the needs of the motor. When a run cap gets weak, the motor trys to compensate for it by drawing more power. More power draw = more heat in the motor, then the motor will overheat and shut off to protect itself. When the motor cools off it will automatically restart and run until it overheats again. Keep in mind that I am a technician that normally diagnoses equipment in a hands on manner. There are many practices and concepts that transcend all air conditioning systems but it is a constantly evolving industry. I live in south eastern WA and I don't see Amana units except as window units. It is possible to have something else causing this problem (faulty thermostat, failing thermal relay(if used), problem with electronic controls(if used)) there are a lot of potential variables