Question about Sta Rite Sta-Rite Max-E-Therm High Effiency - Propane Heater - 333,000 BTU
AGS code My pool heater ignites for 1 second and quits or doesn't ignite at all. I am reading an AGS code so I replaced the gas shutoff switch, and the high limit switch with no resolve. I checked the temperature governor, the bypass valve and they too are clean. I checked the flow switch, and it reads good for proper water flow. My filters are clean and my air flow switch is working properly, but I am still getting an AGS trouble. What am I overlooking? Could it be the logic module? Thanks for any suggestions you may have. Joe Bryan 352-200-8708
  • 4 Answers
AGS switch wiring may be bad. Jumper the switch at the molex connector on the board using a paper clip, with the plug still plugged on. Restore power.
Posted on Dec 04, 2009
I have a Master Temp 250 pool heater that shows an AGS error on the back of the board. The heater runs for about 20 seconds then shuts off, any ideas?
AGS = Auto Gas Shutoff...
What is happening is the heater is monitoring (or sorta, by reasons difficult to explain here) Water Flow and Water Temperature. In this case, the AGS is triggered by a low water flow, or high Incoming Water Temp.
High internal water temp = triggered AGS.
If you have and can confirm, PROPER water flow, water temp coming into heater is Lower than 104°, then it is possible you have a faulty AGS.
But in most cases, it's only doing its job. Locate the reason for the fault, or why the AGS Switch turned the heater off.
Jun 05, 2015 | Pentair Mastertemp 250 Natural Gas Pool...
I am getting an error code ags
AGS - Auto Gas Shutoff = Because of a problem sensed, the gas valve is closing, stopping gas supply and hence heater shutoff.
Improper water flow through heater! Check filter, pump, water supply lines, anything that will reduce water flow into heater.
A faulty Pressure Switch may cause this problem as well.
or...
In coming water to heater is over 104°
If all is good with the above, replace the AGS Switch.
May 31, 2015 | Jandy Laars LX Pool Heater / 400,000 BTU /...
Laars LX 250 AGS Service error. Burners ignite the go out.
if connected 120 volt switch red and black wires its not rectification
Nov 17, 2012 | Jandy Laars Lt 250,000 Btu Heater
IT TURNS ON THEN SHUTS OFF,DISPLAY FLASHES SERVICE AGS
Per your owner's manual:
AGS
(automatic gas shut-down)
1. Oscillating pump pressure.
1. Clean filter or identify and repair cause of pump oscillation.
2. Low gas supply pressure.
2. Identify and repair incorrect supply pipe size or pipe line blockage.
Refer to qualified service personnel.
3. No flame at burners.
3. No flame at burners. 3. Identify and correct loose wiring connections, or problems with igniter, flame sensor, gas valve, or ignition control.
For more info the manual is here:
http://www.jandy-downloads.com/pdfs/LXandLT_H02140B.pdf
John
May 29, 2011 | Jandy Laars LX Pool Heater / 400,000 BTU /...
Heater will fire, will heat for one hour then shutdown. will get digital read out AGS. can turn heater off, let set for a while turn heater on will heat up for an hour and it will shutdown again.
you didn't indicate exact model but here is what the AGS is for.
Not sure if yours has a combustion blower or not, if so check that it's flow is not obstructed. If it doesn't make sure there are no debries in the flue area. Here is the troubleshooting from their manual. You can download a manual from www.jandy.com
AGS
1. Oscillating pump pressure. 1. Clean filter or identify and repair cause of pump
oscillation.
2. Low gas supply pressure. 2. Identify and repair incorrect supply pipe size or
pipe line blockage.
problems with igniter, flame sensor , gas valve, or
ignition control.
Jul 16, 2010 | Jandy Laars LX Pool Heater / 400,000 BTU /...
Jandy lx250 heater is giving me service code ags
AGS automatic gas shut down
which means you have ignition failure, which can be from low gas pressure, or volume. if the heater fires then goes out the signal is not going back to the control module check all wiring.
Jun 16, 2009 | Jandy LAARS LX250 - NATURAL GAS, DIGITAL...
Code AGS, heater wont light
replace temp sensor for aqualink mounted in plumbing from pump
Mar 15, 2009 | Jandy Laars LX Pool Heater / 400,000 BTU /...
Sta Rite Sta-Rite Max-E-Therm High Effiency - Propane Heater - 333,000 BTU Logo
785 people viewed this question
Top Sta Rite Pool & Spa Experts
Jay Finke
Jay Finke
Oloyede Monsuru
john h
Are you a Sta Rite Pool and Spa Expert? Answer questions, earn points and help others