Gas burner will not light. it has a s86c control intermittentpilot 100% shutoff . I HAVE 24 VOLTS AT THE CONTROL COMMING IN BUT NO VOLTAGE TO THE GAS VALVE . NO SPARK AT IGNITOR. PLEASE TELL ME THE SEQUENCE OF OPERATION.
  • 85 Answers
Therm calls for heat, enducer fan turns on, pressure switches closes, ignitor sparks, gas valve opens. If ignitor does not spark, it will go to try a few times then lockout. Do you have a led code on your control board, if so what is it blinking? Could be ignitor bad only..
Posted on Dec 04, 2008
Frigidaire furnace wont light pilot. we have replaced igniter and pressure switch
Gas valve solenoid have continuity? No continuity replace the valve
Getting 24 volts to the gas valve? No voltage from control board check fuse on control board.
Replace control board.
Any rollout switchs that are open and you won't get 24 volts to the gas valve.
Oct 27, 2011 | Goodman GMS90703BXA Heater
I have an early 80's mobile home with an "intertherm gas atmospheric furnace" pilot light is lit but can't get the furnace to "fire". Seems as though the limit control is stuck open. ...
If your pilot light is lit then I would first check your thermostat. Make sure it is on heat setting and fan is on auto, turn stat up to where it should be calling for heat. If you don't get burner to light remove front cover from thermostat and see if it has a mercury switch, if it does move temperature selector up and down and see if you can see a spark in mercury switch vial. If y ou cannot see a spark remove screws that attach t-stat to base.Remove carefully and disconnect wires that go to r and w terminals on stat base. Temporarily connect these two wires together. This should make burner light if you have power to thermostat. If burner does light disconnect wires and replace thermostat. Also if you have a volt meter check across these two wires and see if you have power there. Should be around 24 volts a.c. If your thermostat has a fan on setting try that. If fan runs you know you have power to furnace The gas valve needs 24 volts to operate and inside the electric control box in furnace there is a transformer to step down 110-120 supply voltage to 24 volts. If transformer is working you should be able to hear a low buzz or humming sound. You can also check across gas valve terminals when t-stat is set for heat, you should read about 24 volts. If you have 24 volts to gas valve and it is not opening then you need to replace gas valve. The main purpose of the limit switches is to turn blower on when temperature in heat exchanger reaches fan on temp,shut off blower after burner shuts off and heat in heat exchanger reaches fan off temperature, and limit if temperature exceedes set point without blower coming on. I hope this helps you. Thanks
Nov 25, 2010 | Heating & Cooling
I have central air ( Dimond 80 York Heating Air conditoning Unit ) My air conditoning unit has stopped working. The board has checked out ok.but there seems to be a voltage problem some where from inside...
Try the following step.....
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jun 08, 2010 | Heating & Cooling
No blinks normal running igniter glows gas comes on wont run
Check for 24 volts across the gas valve when Ignitor is glowing. If no, bad board. If yes, bad gas valve or blockage.
Mar 05, 2010 | Goodman GMS90703BXA Heater
80% ducane furnace makes several attempts to ignite then shuts down. glow stick lights but no ignition to main burners. any ideas?
Check for 24 volts across the gas valve terminals!
Mar 04, 2010 | Heating & Cooling
Red light blinking continuosly meanig gas valve relay short how can I fix myself - furnance only blows cold air
You will need to check for 24 volts AC to the gas valve after the igniter starts sparking or glowing. If you have it but it does not open, bad gas valve and you will need to replace it. If you are not getting 24 volts after it starts glowing or sparking, you have a bad board.
Jan 16, 2010 | Heating & Cooling
Having problems with Carrier 58RAV furnace. Goes through the motions, but gas never turns on. I think it is a problem with the LPGS. Please advise. Thanks
Dec 24, 2009 | Carrier Heating & Cooling
WILL NOT LIGHT ALL 5 BURNNERS WILL ONLY LIGHT 2 THEN SHUTS OFF GOES TO LOCKDOWN
Nov 23, 2009 | Coffee Makers & Espresso Machines
FURNACE COMES ON AND SHUTS DOWN WITHIN 15 SECONDS
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control). When all else fails, check the ground connection for corrosion.
Nov 23, 2009 | Heating & Cooling
My furnace turns on but does not heat. There are two distinctly different fans that turn on, but then they shut off. After a few minutes it does it again. I think this is because it is not igniting? Can I...
Read this first:
Nov 06, 2009 | Heating & Cooling
Heating & Cooling Logo
107 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen