Question about York Yankees Bedding MLB Comforter
Heat pump wiring
Dear Sir/Madam,
I have a York heat pump Model # E2EBQ24AQ6A.
Recently I have installed a Forced Air 2 stage heating Gas furnace in my house and I don't want to use heating from heat pump. Just I want to use A/C. Could you please let me know how I can do the wiring for the heat pump to the furnace circuit board. The thermostat wires are already hooked up to the furnace and its working. R,G,W.
Thank you for your time.
Regards,
Reza
  • 700 Answers
Yes i can , you need to hookup the r and the o together so that the reversing vvalvce is allways energized . so with that im mind send r,y,c,o to theout side unit. at the ahu you'll hook up the 5 wires for the furnace, r g w1 w2 com and at the thermostat r,w1,w2,y,g,com,o then you will be set (the o get hooked up to o and goes straight out side.
Posted on Dec 25, 2008
We have 2 furnaces in our house, both on the braeburn 3200 model thermostats.
If you have a dual fuel system - gas/heat pump the heat pump should lock out at around 41 degrees depending on what the outside lockout sensor is set at. It may be that both the heat pump and furnace could be running at the same time if the outside lockout isn't working or there could be a problem with the thermostat. Best bet would be to have a service tech check it out. However if you want to check it out here are the terminals Terminations: R,Y1,Y2,W2,E,G,O,B,L,C. W2, E and B are the heating terminals for 2nd stage heat and emergency heat. First stage heat, compressor Y1 with B (reversing valve on heat pump) energized together. 2nd stage W2 energized for gas or electric heat . No power to Y1 and B when W2 is energized if gas. E can be energized with Y1 and B if you have electric heat or if you switch over to emergency heat, E will be energized.
Feb 02, 2016 | Heating & Cooling
Can't get the gas furnace to heat.
All York/JCI thermostats made by Venstar
The setup is probably incomplete. Did you configure the thermostat for a 2 stage heat pump? The heat pump should have a thermostat wire connected to R, C, Y1, Y2, and O, that makes 5 wires. I suspect you are only using first stage compression and or first stage blower speed.
Nov 23, 2013 | Source1 CTS Series Model S1-THPU32P7S...
I am trouble shooting a Bryant Hi-bred system that uses an air cooled heat pump with high efficiency gas furnace for backup and low ambient operation. How does the system decide whether to use the air...
Your t-stat should be set up so that the furnace is the second stage heat and also emergency heat. First stage (heat Pump comes on) sometimes they use Time to start 2nd stage, sometimes they use outdoor temp and this all bepends how bryant has set it up, without a model # I cannot tell you but send it and i will look in somebooks i have to tell you.
Mar 01, 2011 | Bryant Heating & Cooling
I have a lennox 2 stage gas furnace and a lennox XP15 heat pump controlled through the Lennox 7000 touchscreen thermostat. I want to disable the heat pump due to excessive noise due to lower temperature...
At tstat press options. Press installer setup. Yes, you are qualified. System settings, non heat pump. Gas/ oil heat. Save changes. That should do it with no wiring changes.
Jun 18, 2017 | Heating & Cooling
I paid $20 last night to talk to someone. He told me how to hook up the Lux DMH110 but when i hooked it up this morning the heater came on when i put it on COOL and the fan just come on when i put it on...
If you have this type of system your thermostat will not work;
  • Multi-Stage Heat Pumps
  • 3 Wire Hydronic Systems
  • Line Voltage Systems (120/240 VAC)
  • This thermostat is only for this type of HVAC systems;
  • Most 24V Heating and A/C Systems
  • 1 Stage Heat/1 Stage Cool: Gas, Oil, Electric, or Single Stage Heat Pump Systems
  • 2 Wire Heat Only Hydronic Systems (Hot Water Baseboard & Radiator)
  • Millivolt Systems (Wall Heaters / Furnaces & Gas Fireplaces)
    1. Never connect a low voltage thermostat to line voltage.
    Two wires control a heat only system.
    1. Connect one wire to W and the other to RH.
    Two wires control a cool only system.
    1. Connect one wire to RC and the other to Y.
    Three wires for forced air heat only system, where the previous thermostat
    did not have a clock or timer.
    1. The previous RH or RC wire is the 24-volt transformer wire. Connect it to RH. Leave jumper connecting RH to RC. Connect the forced air heat system to W, and the fan wire to G.
    Three wires for a heat only, forced
    water system that did NOT have a
    clock or timer.
    1. This system employ 3 wire zone valves. Currently no Lux controls are compatible with this system.
    Three wires control a heat only, forced water system that DID have a clock or timer.
    1. Tape off and do NOT install any clock or timer wire. Often they are labeled C or TC. Install the remaining two wires, one to RH and the other to W.
    Four wires control a heat only system,
    and two of the wires operate clock or timer. The other two wires operate the heater.
    1. Tape off and do NOT install any clock or timer wire. Often they are labeled C or TC. Install the remaining two wires, one to RH and the other to W. The jumper connecting RH to RC may remain or be removed.
    Two wires control heating AND cooling.
    1. Currently no Lux controls are compatible with this system.
    Three wires control heating and cooling. One wire operates heat, one operates cooling and the third provides 24 VAC.
    1. Connect the 24-volt power wire to RH. Install a jumper connecting RH to RC. This jumper is usually pre-wired. connect the heat wire to W, and the cooling wire to Y.
    Three wires control a cooling only system. One wire operates the compressor, one operates the fan and the third provides
    24 VAC.
    1. Connect the 24-volt power wire to RC. Connect the cooling wire to Y and the fan wire to G.
    Four wires control a heating and cooling, electric, gas or oil, forced air system that
    is NOT a heat pump.
    1. Connect the 24 VAC transformer wire to RH or RC. Install a jumper connecting RH to RC This jumper is often prewired. Connect the heat wire to W, the cooling wire to Y. and the fan wire to G.
    Four wires control a Single Stage Heat Pump. They were labeled: G, Y, R or
    RH or RC, With either B or was used.
    1. Do not connect wires to both B and O. Connect the reversing valve wire to B or O, just as the previous thermostat. Install a jumper wire from RH to RC. Connect 24 VAC wire to RH too. Install a second jumper wire from W to Y. Connect compressor wire to Y and the fan wire to G.
    More than 4 wires are connected to the
    old thermostat
    Jun 27, 2010 | Heating & Cooling
    What is the difference between stage two and aux heat?
    The furnace shoud be wired to W1 amd EM Heat. If your heater is a two stage furnace then hook the thermostat W1 to stage 1 amd W2 to stage 2. Most new 2 stage heaters will control stage 2 with the control board.
    Jan 03, 2010 | Heating & Cooling
    I have a honeywell thermostat model # th5220d1003-0636 & need to know what connections to make for gas forced air heat.
    This is a Focus Pro 2 heat,2 cool thermostat. If you are connecting this to a single stage(1 heat) residential furnace then your connections are: At the thermostat the R and Rc therminals are internally connected so you can connect your R terminal wire from the furnace to the R terminal at the thermostat(this is your 24 volt supply for both heating and cooling. The W or W1 wire (heating) from your furnace you connect to the W1 terminal at the thermostat. The W2 wire from your furnace(if your furnace is a 2 stage furnace) you connect to the W2 terminal at the thermostat. The G wire from your furnace(indoor fan) you connect to the G terminal at the thermostat. The Y1 wire(cooling) from your furnace you connect to the Y1 terminal at the thermostat. The C wire(common or neutral) from the furnace you connect to the C terminal at the thermostat.
    Nov 14, 2009 | Honeywell Programmable Thermostat Heater
    I need help with my central heat and air unit, it has a heat pump. the model number is GQ3RA-036K. I am changing the theromstat out and the wires are connected to it. there are eight wire colors that are...
    Normal 0 MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman";} Thermostat wire color codes explained.
    Please note. Not all installers use the proper color codes when they install or replace equipment. It may be necessary go go to the furnace or outdoor unit to verify what wires are for what purpose. Also be sure there are no splices in the wire that could change the wire colors between components.
    • R (red) or Rh (Red heat) 24 volts from equipment.
    • Rc (Red cooling) 24 volts from transformer in cooling equipment.
    Note: If only furnace has a transformer and cooling equipment does not jumper Rc and Rh.
    • W (White) sends 24 volts to furnace control to start the heating cycle.
    • W2 (no standardized wire color, usually whatever wire color is available) controls second stage heat.
    Note: W2 is most often used for heat pumps to control what is called emegency heat or Auxillary heat, and most often will use the white wire.
    • Y (yellow) often (blue) is used, controls cooling unit (outdoor condensing unit) also is used for heat pump heat.
    • Y2 (no standardized wire color, usually whatever wire color is available) controls second stage cooling.
    • G (Green) controls the fan "on" operation of the furnace/air handler. Also often is used to start the blower for many electric furnaces.
    • C (common) most often brown but can also be black or other color available to installer.
    • O (orange) Energizes heat pump reversing valve for cooling (Trane and most other brands).
    • B (Blue) Energizes heat pump reversing valve for heating (Rheem, Ruud and Weatherking).
    May 07, 2009 | Heating & Cooling
    Wc wiring on thermostat
    sounds like you have a heat pump the w2 on old thermostat is for a second stage heat. If you can give me a little more information on type of system you have (forced air furnace with heat/cool, Heat pump or boiler)? How many wires are on old thermostat? Is it a no programmable or programmable? How old is the furnace?
    Jan 17, 2009 | Honeywell Programmable Thermostat Heater
    RTH7400 thermostat installed-screen display unlit-used page 10 wire installation. Used heat pump wiring-which does not show W2 and Y2 on heat pump schematic, so used conventional displayed W2 and Y2...
    w2 and y2 are used for 2stage applications
    w2 = 2 stage heat
    y2= 2 stage cool
    If your system is a single stage system, look for the y1 and y2 terminals. If the thermostat does not have y1 and y2 then you may have the wrong thermostat. As always, please read the directions carefully. Thanks!
    Jul 03, 2008 | Heating & Cooling
    York Yankees Bedding MLB Comforter Logo
    1,023 people viewed this question
    Top York Sport & Outdoor - Others Experts
    Paul Carew
    Shehu Pro
    Shehu Pro
    ray gallant
    Are you a York Sport and Outdoor - Other Expert? Answer questions, earn points and help others
