My carrier 59 mvp Furnace has a problem with moisture in the vent outlet. The furnace will not fire up intil I losen the clamp and drain the moisture. I have to do this almost daily in when it is very cold.
  • gdnarcisi1 Dec 03, 2008
    Checked the vent pipe outside my home. No blockage. Any other ideas?
    Proton 77. You may have hit the nail on the head on this one. I will try exending the pipe or adding an elbow.
    Thanks for the help!
    Genius:
  • 1,239 Answers
HI
The first place to look is at the furnace brain, a box located somewhere in the unit connecting to the gas valve, look at this brain [controller] and there should be a light of series of lights.
On the box itself there should be a matrix of codes such as: green light flashing= bad glow plug, or red, bad controller box, do you have anything like this?
Most have some sort of led light that narrows down the problem.
If not at least do these things:
make sure the power is off, and that the blower motor spins by hand freely.
next if you have a volt ohm meter, you can test the plug to see if there is a circuit, if the glow plug is open, that is one problem,
If you have a volt meter you can measure the leads at the plug to see if voltage is there or not.
There are so many checks and switches that will operate dependent on the operation of something else.
Unplug the furnace and keep the power off the brain, if so equipped for several minutes, see if it resets.
If it does great, if not tell me if there is a brain box and what the lights are, and what the matrix of light codes say, and we can go from there.
You can also measure for voltage from the thermostat to the furnace and make sure it is getting a signal on all wires, a thermostat wire could have come loose.
very difficult to troubleshoot a furnace when one is in front of it, let along without seeing it.
If you find no box, let me know, and let me know from these checks above if anything changes, or gives you more info to pass on to me.
Step at a time we can find this, a volt ohm meter will be really helpful.
Posted on Dec 03, 2008
  • ABHISHEK.C
    ABHISHEK.C Dec 03, 2008
    Sandwiched between the coils are a compressor, two fans, a motor, and thermostat controls. Dirt is the biggest enemy of window air conditioners; it can lower the efficiency of the evaporator coil, block the operation of the fan that blows out the cool air,
  • 1,183 Answers
You need to see if you can extend the intake pipe out a few inches further as not to **** in the moist exhaust air or put an elbow on it facing horizontal away from the exhaust. You get freeze ups in 3 common instances: if your pipes aren't sloping back towards the furnace or you are sucking back in moist exhaust, or you have them buried under snow. Carrier will not have a record of problems because it is not a flaw with the unit itself, just how it is vented and recirculating (most likely). Thanks proton
    Genius:
  • 1,011 Answers
Normal 0 false false false MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman"; mso-ansi-language:#0400; mso-fareast-language:#0400; mso-bidi-language:#0400;} dear sir/madam,
  • Vent dryer and furnace flue pipes directly to the exterior
  • Properly seal all ductwork for airtightness
  • Install rain caps over roof vents to prevent water penetration
  • Normal 0 false false false MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman"; mso-ansi-language:#0400; mso-fareast-language:#0400; mso-bidi-language:#0400;} Install a fresh air exchange system to prevent elevated indoor humidity levels Install continuous soffit and ridge vents
thanks
good luck
  • Asfiya Ahamed
    Asfiya Ahamed Dec 03, 2008
    install a fresh air exchange system to prevent elevated indoor humidity levels
    install continuous soffit and ridge events
  • 837 Answers
Have you checked to make sure the inlet pipe is not blocked - be sure the screen is in place on the outside
  • Jay Glendenning
    Jay Glendenning Dec 03, 2008
    You say that you have to do this almost daily .. When does this occur? When you wake up in the am after the furnace starts to go into a daytime use as controlled by a programmable thermostat?
    What is the daily temp/night time temps set @ ?
Why is water coming out of my furnace exhaust pipe?
When natural gas or propane burns, water vapor is given off within the flu gasses so a bit of condensation in, off and around the flu discharge is quite normal. If it is a high efficiency furnace with the pvc flu pipe, they must be pitched properly BACK TO the furnace so the moisture will drain backwards and out a drain tap at the bottom of the riser. That style of furnace will have TWO drains...one up high for the air conditioner coil and one about 16" up from the bottom of the furnace off of the 'condensing coil' that the flue gasses pass through to extract a much greater amount of heat from the burned gas.
Many flu pipes are installed incorrectly which causes water to drip outside instead of back to the furnace and this usually results in huge icicles hanging off of them in the winter and eventually the partial blockage causes the flu's pressure switch to open.
If you have regular galvanized flu pipe, you have less than a 90% high efficiency furnace and the resultant flu gas temperature is much higher with a much greater quantity of water vapor in it. A little condensation is somewhat normal on the top of the flu cap as the hot moisture laden vapor comes in contact with the cold and dry outside air. If the moisture is all over the galvanized flu pipe in the basement, you are possibly venting into an oversized and unlined masonry chimney. IF that's the case, the chimney should really be lined with a flexible liner and properly connected to the furnace and water heater (if gas fired) with the proper connections and configuration.
Mar 25, 2015 | Heating & Cooling
FURNACE WONT FIRE UP ,LIGHT INDICATOR SAYS PRESSURE SWITCH OPEN W/ INDUCER FAN ON
PROBABLY MOISTURE IN PRESSURE SWITCH OR SNOW OR ICE BUILD UP NEAR VENT TERMINATION . PROBABLY JUST A BAD PRESSURE SWITCH
Dec 17, 2013 | AO Smith Miller / LSI / Home / Nordyne...
Carrier 38TZA036320 evaporator coil
Hello, sounds like a blocked drain line or cracked condensate pan. Try cleaning the drain line first with a wet/dry vac at the outlet of the 3/4 inch pvc line, if this does not help you will need to have the drain pan repaired or replaced.
Jul 04, 2012 | Heating & Cooling
Carrier 58STA furnace code 33, no ignition blower stays on. I have a Carrier 58STA furnace. It's getting a code 33 and never trying to ignite. The blower constantly stays on. It is pushing good air...
33 is a limit switch open take your furnace doors off and there should be a wiring diagram. on this furnace the blower will run if this is open. check rool out swict and linits. it sounds like you have a problem with over heating. how does the fire look ? is the vent blocked ? things like thathttp://www.scribd.com/doc/20861415/Carrier-58pav-Service-Maint i think page 9 has falt codes
Feb 11, 2011 | Heating & Cooling
My basement has water in it from time to time. I called a service guy out and he said the moisture in my basement is causing my furnace problems. is there anything i can do to correct this problem besides...
if its the furnace condensating it obviously needs a drain some high efficincy heaters need drains as they burn so efficient they sweat and condensate in flu and you need to get rid of this by draining if the furnace has no drain it must by your venting into area causing it condensate in the area furnace in, so you just need fresh air vent in doorway or wall to let more air in, but i reckon its more the draining of the furnace, if the plumber can't stop the moisture coming in, and didn't give you any solutions i hope you didn't pay him to come there for nothing! and if you are not using heater and moisture getting in still this is a drainage problem or water circuit, which is a plumbing problem not your furnace
Nov 23, 2010 | Goodman Heating & Cooling
The draft inducer comes on and the furnace lites as normanl Goes thru its cycle and kicks off. The problems is the draft may not kick on the next time and sticks and the motor gets hot, If I go remove the...
When a furnace is replaced with a newer style unit like yours with an inducer motor, they sometimes use the old vent pipe. These old style vent pipes are transite (light weight cement), the moisture created from your furnace exhaust is caught on the cool transite surface and runs back down into the blower blades or wheel bringing a white mineral deposit with it which causes your problem. The vent should nave been replaced with the heater using a metal vent material. You will need to replace your inducer motor assembly and vent pipe to prevent a recurrence.
Dec 04, 2009 | Omega Trane Furnace Draft Inducer Blower...
We have a dayton gas furnace model #3E463A. thought the control box was gone. got new one we furnace starts up the power goes on, fan starts no green pulsing light on control no ignition
When your furnace starts...the Ventor motor(exhaust fan) starts up....within a short time (seconds) the Pressure switch closes proving that the Fan is indeed running and the vent is not blocked...if this doesnt happen the furnace will not poweer the ignitor or fire at all....Check the vent pipe outside and look for obstructions or dirt on the screen inside the pipe...the condensate from the fuirnace may not be draining at all...due to plugged condensate drain lines...find this tube coming out of the furnace front...bottom of upper compartment usually , and pull it off the tap....if water starts coming out then your drain is plugged downstream of the furnace.
Oct 25, 2009 | Dayton Gas Furnace Heater
Heat not coming on carrier gas pack code 31
code 31 indicates pressure switch did not close or reopened during the heat cycle....1st thing to check is the inducer motor,,this is a small motor that turns a small blower wheel that draws the exhaust gases through the furnace and blows them into the vent pipe....1st locate the inducer assembly,,most easily identified by the small plastic fan blade that cools the inducer motor as it runs..1st turn off tstat and turn off furnace power switch..then turn on furnace switch,then set tstat to heat,set the temp above room temp by 5 degrees...remove the furnace front cover,locate the inducer motor,,if it isnt turning,but is warm or hot after a minute or so,likely the inducer motor is bad..if it isnt turning and isnt warm after 1 minute,then likely the main control board is bad,,not turning the inducer motor when it should,,,,,if the inducer motor is running,,then the pressure switch isnt closing,, could be a bad pressure switch but more likely there is a problem with the venting...some possible problems that would cause the pressure switch not to close in an 80% eff furnace [metal vent pipe] are: [1] a blockage in the vent pipe,base of chimney,dead bird at the furnace where vent connects to furnace or down inside the inducer assy,accessed by removing vent pipe from furnace....if all clear the chimney could be blocked up inside,,is the draft good when vent is removed from base of chimney?..if furnace is a 90%+ type [pvc plastic vent pipe],,then check the intake pipe at the furnace by removing it where it attaches to top of furnace..is the intake clogged with anything?..then check the intake and exhaust pipes outside for blockages,,including ice/frost/snow at the exhaust pipe outlet..
Jan 26, 2009 | Goodman GMS90703BXA Heater
I am living in a home with a carrier furnace. The furnace is in the back part of the house in a store room. It has two- 2 1/2 inch plastic pipes. One that suppplies air to the furnace and the other is...
As long as the fresh air intake pipe to the furnace is not plugged up the second vent is not needed some homes when they are new are air tight and need a fresh air circulation system
Oct 30, 2008 | Carrier Heating & Cooling
Heating & Cooling Logo
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen