I am replacing a white rodgers thermostat with a honeywell rth3100c. i have matched my wire as e (brown) to e w2 (white) o aux y (yellow) to y g (green) to g o (orange) to o l blank r (red) t r b blank c blank now i have a blue wire which was hooked up to the x1 on the old thermostat. where does this wire go?
  • tdomiano Dec 02, 2008
    I have hooked the blue to the c......now i put it on heat and it takes about 5 minuts to kick the unit on.....when it kicks on it displays aux heat on the thermostat instead of heat on.
  • tdomiano Dec 03, 2008
    thermostat working.....blower went out......all is fixed now thanks so much for the help.
  • 85 Answers
Blue (C) or sometimes (B) should be your common wire. Look at your schematics and locate common. Your Brown wire is (E) and is emergency heat, white wire (W) is Auxilary Heat, green wire (G) is fan relay, red wire (R) is power, yellow wire (Y) is Cooling and orange wire (O) is reversing valve.
Posted on Dec 02, 2008
  • Armando Bernal Dec 02, 2008
    Do you have back up emergency heat? if so click your thermostat to emergency heat. Also the unit has a natural 5 min delay, it can be reconfigured on your therm schematics. Your therm may need to reconfigured.
Need help understanding how to wire a new programmeable thermostat. I currently have a White Rodgers 1F73 model (non-programmeable) connected. I am confused with the instructions on how to connect the...
the black wire is your common wire, you need to program your thermostat, in the advance mode, to tell the t-stat if your heat pump reversing valve is energized on cooling or heating, is the orange wire connected to your t-stat.= w2/o/b
Dec 20, 2014 | Honeywell Heating & Cooling
How do you relpace an A.C. thermostat?
E Back up heat/ white wire
AUX Jumper to E
Y yellow wire / Cooling - compressor
G Indoor fan Green wire
O Reversing valve energised in cooling most units Orange wire
L unknown. consult your manual Leave open
R Main power Red wire
B Reversing valve energised in Heat Rheem units only.
C Common second leg of power Blue wire.
Aug 30, 2014 | Honeywell RTH3100C - Digital Heat Pump...
W and W2 wiring on old thermostat...where do they go on the new thermostat?
It depends on the equipment you are connecting the thermostat to. If you have a heat pump, the thermostat must be wired differently than if you have separate heating and cooling equipment. If you have a two-stage or modulating furnace (or boiler), the w and w2 wires will conect for heating, and the y and g wires will connect to the air conditioner. Naturally, some configuring must be done with the new thermostat so that it acts correctly. w-w2-wiring-old-thermostat-go-new-u40lsvyytnuesyuv3fbafhtd-1-0.jpg
please mark this answer helpful.
Feb 22, 2013 | Honeywell RTH6400D 5-1-1-Day Programmable...
Replaced Bryant T-stat model TSTATBBNB001 with Honeywell t-stat
Hello,You forgot to wire the O terminal w1 witch is the reversing valve.It is important to check if old stat is using O or B in witch case B terminal=w1 leaving O unused.
Apr 21, 2010 | Honeywell Heating & Cooling
Your original wiring configuration seems to indicate that you have an air conditioner (not heat pump) and either a gas or electric furnace. If this is the case you may need a different thermostat for your application.
Apr 21, 2010 | Honeywell Heat/Cool Thermostat
Wireing a honeywell thermostat
Bill ..You dont have a heat pump.This controller will not work for a conventional system. Get the right thermostat
Jul 24, 2009 | Heating & Cooling
Heat will not shut off
Take white off of Aux, and attach it to L
Feb 16, 2009 | Honeywell Programmable Thermostat Heater
I had an old thermostat that i had to change need wiring diagram
both thermostatats will have terminal designators R,W,Y,G, possibly O/B, C, W1,W2, Y1, Y2, etc.
Simplest method is to remove wires from old stat one at a time. mark where they came from and then install at same desinated terminal on the new t-stat. Hope this helps. be sure to shut off power supply to the unit (furnace) first. The wire coming to the R (RH,RC) terminal is the 24 volt a/c hot, all others are feeding back to perform given function.
Dec 20, 2008 | Honeywell Programmable Thermostat Heater
Thermostat Wiring: W2? E? Where to connect?
You have a heat pump. You need a thermostat for "Heat pump with Electric back-up heat". Make sure the 'stat has either an "aux" (auxilliary heat) or an "E"(Emergency heat) terminal. The wiring instructions will be provided with the thermostat.
Dec 15, 2008 | Honeywell Electronic Programmable...