Installation problem After installation, I couldn't get the humidifier to work. I connect the yellow wire to the humidistat and furnace's electronic board HUM connection. I can get a 24V signal (verified by multimeter) every time the furnace blower starts up. I hooked up the terminal connection, and plugged in the power supply. But both the fan and solenoid valve don't kick in, when the blower starts. Please help!! The connection I made is: HUM to humidistat, humidistat to humidifier, and humidifier to COM (as instructed by Carrier 58STA manual). Water is connected and verified, but since solenoid valve never kicked in, the panel is still bone dry. Something strange too. If I leave the humidifier plugged in , the furnace sometimes won't start. So I have to unplug it last night to keep the house warm. Any help is appreciated
  • 1 more comment
  • Anonymous Dec 01, 2007
    I have the same problem. It seems that the blower needs to be energized and the stat calling for heat with th burner running. Can this be the case? I don't have enough call for heat, so the humidifier never comes on.
  • Anonymous Jan 03, 2008
    All the above steps were done. We replaced the IAQ Vision Pro thermostat. All wiring was checked. All programming was checked.
    The humidifier will NOT turn on. Carrier furnace is new as of June 2007.
    Humidifier is Honeywell HE360A,B. Is there a compatibility problem?
    Humidity is set at 40% and frost at 8. Tom
    tabonneville@aol.com
  • tabbonn Jan 04, 2008
    I have a HE360A and a IAQ Vion Pro Honeywell thermostst. The machine will not turn on. I found a note on compatibility in the IAQ manual saying that the HE365 is compatible, but the 360 is NOT listed. Caan you tell me if it will not work with the IAQ Vision Pro?
    Novelist:
  • 114 Answers
I WOULD CHECK TO SEE IF YOU HAVE ENOUGH V/A OUT-PUT ON TRANSFORMER. I DONT KNOW IF YOURS CAME WITH ITS OWN TRANSFORMER. IF IT DIDNT YOU SHOULD HAVE A MINIMUM OF A 40 V/A RATING STAMPED OR PRINTED ON THE EXISTING TRANSFORMER. IF THE TRANSFORMER IS EXTREAMLY HOT ... YOU MAY NEED A 75 V/A TRANSFORMER WITH THE SAME VOLTAGES. INCREASING THE V/A CANNOT DAMMAGE ANYTHING IT JUST GIVES YOU MORE POWER WHEN EXCESIVE CONTROLS AND WIRING ARE ADDED TO A HVAC LOW-VOLAGE (24v) CIRCUIT. IF YOU LIKE YOU CAN CALL ME AT 727-363-7071. I AM A RETIRED HVAC&R CONTRACTOR WITH 45 YEARS EXPERIENCE. I HATE THE NEW SENSORS THEY HAVE TO ACTIVATE THESE NEW HUMIDIFIERS. I USE TO WIRE THE HUMIDIFIER TRANSFORMER (SUPPLIED WITH HUMIDIFIER) TO THE LINE (110V) SIDE TO THE LOW SPEED ON YOUR BLOWER MOTOR. THAT WAY THE ONLY THING THAT INTERUPTS THE CICUIT IS THE HUMIDISTAT. YOU NEVER WANT THE HUMIDIFIER TO RUN IF YOUR SYSTEM IS NOT "CALLING FOR HEAT". NEVER TRY TO ENERGIZE THE WATER SOLENOID THROUGH YOUR HEAT WIRE(USUALLY SMALL THE WHITE WIRE) FROM THE THERMOSTAT. THIS WILL RESULT IN BURNING YOUR HEAT ANTICIPATOR OUT ON THE T-STAT.
Posted on Apr 28, 2007
I have a aprilaire 700 I just installed on return plenum. Have a problem with the wiring, the instruction say to connect the R&C wires from humidistat to the same on furnace power strip. Is the C
Depending on the age of your furnace you may have an aux terminal for a humidifier. If not, you should use the white wire (heat) coming from the homes thermostat to power up the humidistat and ultimately bring on the humidifier. This way it will only run when in heating mode.
Nov 16, 2012 | Aprilaire 700 Humidifier
I just installed a Honeywell HE 360 Humidifier I purchased at Home depot. I replaced a Aprilaire model 110 . I have a 120v power duplex that is hot with the furnace blower motor, on so I assumed the sail...
Hello, in order to turn your humidifier on with the furnace the 120 volts coming from your humidifer you must hook it up to a step down transformer, then the transformer will provide 24 volts to you humidistat and solenoid valve. So you need a wire from the HUM on your control board to transformer primary side and a wire from neutral on the board to primary side of transformer. Then you need low voltage wire from secondary side of transformer to humidistat from humidistat to humidifier.
Feb 20, 2011 | Honeywell HE360A1027 Whole House...
How to connect the wires from the H8908A Humidistat and HE225 Humidifier to a carier model 58 STA090-14 furnace please? Thank you.
Not sure how much this will help you, but here is a link in pdf format to the Installation Manual, if you don't have one http://www.honeywellcentral.com/ssi/pdf/honeywell-commercial/HE220-Installation.pdf
If all else fails here is a number for Honeywell. Ask for Technical Support. (877) 841-2840
Feb 09, 2011 | Honeywell HE220A1019 Whole House...
I installed a honeywell 360a flow thru humidifier, and a new transformer. I have power thru the wires to the fan cover. Also the humditstat clicks when turned on. The fan does not work and the solenoid...
Posting a diagram of how you wired the installation will help the both of us figure out what the problem is. You don't have to accept or rate this solution in order to post comments or information. But accepting a solution will not stop you from communicating with the expert. You can still communicate with the expert as long as you need assistance regarding the issue stated herein.
Jan 11, 2011 | Honeywell HE360A1027 Whole House...
Wired a new 360 through Hum blew 3amp fuse. How to wire so it doesn't blow fuse. Have open EAC and EAC2.
Review figures 5, 6 and 7 on the installation instructions and compare with how you wired your installation.
The red wires are not used if you use a mechanical humidistat, (are used with electronic humidstat - supplies 24 volts and go to "hot", "commod" on humidstat). Yellow wired to "Hum" whether electronic or mechanical humidistat used.
If using sail switch or current sensing relay, cuts into one of the yellow wires. - One yellow goes directly to humidisat, then comes out of other side of humidistat & runs to to relay (or sail switch), and comes out of relay (or sail switch) and runs back to humidifier.
Dec 17, 2010 | Honeywell HE360A1027 Whole House...
Humidifier will not turn on (no fan, no water flow)
http://www.appliancefactoryparts.com/humidifiers/helpcenter/breakdowns/honeywell/honeywell-he360a1027.html
A breakdown diagram of parts etc above.
http://www.appliancefactoryparts.com/content/pdfs/110672-4.pdf
Shows you the HE360A.
To me it sounds like it is wired incorrectly, the solenoid should NOT get too hot at all. The PDF above shows wiring data.
Apr 03, 2010 | Honeywell HE360A1027 Whole House...
Wiring issue with the Honeywell HE360A Humidifier
Maybe I can help. this is 24v so it doestn't matter which wire goes where so here goes. 2 wires from humidistat go to furnace, split one of the wires(not both) so they reach the yellow wires on the humidifier. with marettsconnect one of the split wires to one of the yellow wires. do the same to the other split wire and yellow wire. what you should get is one wire from humidistat to furnace then one wire from humidifier to humidistat and one from humidifier to furnace. hope this helps
Jan 31, 2009 | Honeywell HE360A1027 Whole House...
Humidistat installation question
I suppose you are looking at the do-it-yourself model. Depending on the wire that is run up to you Regular Thermostat from your furnace. You may have to run a seperate line for the Humidistat. A digital thermostat that does Humidity and Temperature is recommended. Or you could just place a Humidistat near the furnace room. A wiring diagram will come with the Humidifier discribing the different ways to wire it.
Jan 09, 2009 | Honeywell Power Humidifier: Furnace...
Aprilaire 700 operating at wrong time
You want the humidifier to run in heat mode which is the r-w1 terminal on the stat.
Nov 17, 2008 | Aprilaire 700 Humidifier
Honeywell HE360A1027 Whole House Humidifier Humidifier Logo
718 people viewed this question
Top Honeywell Humidifiers Experts
Dennis
Simon Benzekri
Level 1 Expert
Christian Samuelsen
Christian Samuelsen
Are you a Honeywell Humidifier Expert? Answer questions, earn points and help others