Question about Cross Furnace Draft Inducer Blower 115 Volts Fasco # A064
Furnace burner ignites then goes out
Older Heil furnace (75,000 btu's) burner egnites for about 15 seconds then goes out fan continues to run. Wahts the problem? Dave
  • jkfeith Dec 01, 2008
    I fixed it before I had an answer from you. The connector hose was loose. Thanks for getting back with mw anyway. BIG Dave
  • 61 Answers
Sound like a thermocouple, or flame sensor.
If it has flame sensor make sure you check micro amps to verify operation, because it might be the board that controls the sensor.
Posted on Dec 01, 2008
  • Joseph Lillie
    Joseph Lillie Dec 01, 2008
    You are very welcome, Make sure to try FixYa again.
Heil furnace blower motor stays on won't shut off at thermostat blows cold air continuously
Do you have t sat fan switch in on position??? If so blower will run continously set it to auto and it will cycle with heat call
Nov 12, 2012 | Heating & Cooling
My Amana GUI090B30B furnace will not ignite. The ignitor glows then the valve releases gas but the gas does not ignite. The ignitor goes out and the valve shuts after a second or two of trying to ignite...
Hello, it is possible that even tnough the ignitor is glowing it might be too weak to ignite the burners. I would cneck the resistance of the ignitor with a multmeter, should be between 40-90 ohms typically
Nov 28, 2011 | Heating & Cooling
Mr. Heater Big Maxx 75,000 BTU Heater will not ignite. Manufacturer says it's possibly a faulty chipboard. After replacing the chipboard with a new unit shipped from the manufacturer the unit still will...
Is the circuit board giving you a blinking error code?
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Feb 26, 2010 | Mr. Heater Natural Gas Garage Heater -...
Coleman furnace -- fan runs, ingniter won't light,
The chances are that the furnace was running when the power went out. This will cause the high limit switch to cutout and needs to be manually reset.
You will find that switch in the blower compartment near the blower. Usually somewher near the highest point of the cabinet.
Push the little red button firmly till it clicks.
When the power goes out while the furnace is running the heat builds up because the blower shuts down immediately and causes this limit switch to cut out.
If you have a electric tester you can also follow the low voltage circuit till you find the open switch. Ther is usually a wiring schematic on the door cover of most furnaces.
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Dec 09, 2009 | Coleman Propane Forced Air Heater...
HEIL 80% furnace T-STAT calls for heat, Inducer runs and nothing else happens, Ohm meter reads 4.9 on ignitor. MDL#NTGM100EHA2....Any help with this?
Nov 03, 2009 | Heating & Cooling
Fans and igniter light but not main burner green
Hi clean the flame senser , check out the pressure switch jump it out see if it lights . check you have power to the gas valve
Oct 10, 2009 | Sterling RF75 Natural Gas Heater (75,000...
A 1979 Colman RV furnace. Blower shuts off shortly after burner shuts off leaving a hot heat exchanger. After 15 seconds blower comes on again blows for 10 seconds shuts off comes on in 15 seconds blows...
The fan limiting switch is acting up. It should stay running until lower temp is reached. It will cycle until the temp stays below or at the low setting. Limit switches are adjustable.
Jun 09, 2009 | Coleman Propane Forced Air Heater...
16 year old Heil 75K btu furnace, some times does not ignite.
recommend getting a carbon monoxide indictor or having some one test it. with it being over 15 yrs old if checks good replace ignitor assy should fix it ok
Dec 14, 2008 | Cross Furnace Draft Inducer Blower 115...
Carrier Weathermaker gas 8000 will not ignite
Your hot surface igniter may be bad. It may be cracked which would prevent it from starting the burner flame.
May 21, 2008 | Heating & Cooling
Cross Furnace Draft Inducer Blower  115 Volts Fasco # A064 Logo
805 people viewed this question
Top Cross Measuring Tools & Sensors Experts
Vuk B
Tom Chichester
Are you a Cross Measuring Tool and Sensor Expert? Answer questions, earn points and help others