Carrier 394jaw036045 furnace won't light

I can hear the clicking, igniter but no spark.  A diagnostic manual is needed as to identify what part is needed.  The igniter is a 3 wire.

Posted by on

2 Answers

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    Superstar:

    An expert that got 20 achievements.

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

  • Master
  • 10,515 Answers
  • 4 more comments 
  • taran_2005
    taran_2005 Nov 30, 2008

    If u wana download manual, direct link wld be :-





    http://mfc.engr.arizona.edu/documents/LP...





    Thnx.

  • taran_2005
    taran_2005 Nov 30, 2008

    Hey,



    a spl gift for u :p





    DIAGNOSTIC MODEULE FOR GAS FURNACE AND WAYS TO RESOLVE IT WITHOUT ANY HELP





    http://homerepair.about.com/od/heatingco...





    Thnx.

  • jeffeverde Nov 29, 2010

    Manual is totally unrelated to a Carrier / Payne 394jaw036045

  • jeffeverde Nov 29, 2010

    suggested troubleshooting consists of- "Is it plugged in? Is it turned on? Call a technician"

  • jeffeverde Nov 29, 2010

    sorry -- that's LH680005

  • jeffeverde Nov 29, 2010

    clicking ignitor but no pilot could be the pilot assembly or the main gas valve (assuming, of course, that you've first verified that the gas is turned ON (blue knob on the control valve, and shut-off valve on the gas line somewhere outside the furnace cabinet)).

    Your pilot assembly is an LH680005, and can be found online for $65-120

    Your gas valve is a Carrier EF32CB197 (actually, a White-Rodgers 36e93-301-- new part# 36e93-304). The valve can be found online for $85 to $200

×

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    Genius:

    An expert who has answered 1,000 questions.

  • Master
  • 3,422 Answers

Hi,
Please click HERE for Manual.

Let me know if you need anything.

Good luck

Posted on Nov 30, 2008

  • jeffeverde Nov 29, 2010

    manual referenced has nothing in common with a Carrier / Payne 394jaw036045

×

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

I have a Lennox furnace Model G19 and the pilot will not light.e You get the normal clicking sound and the ignitor lights but it seems to be a very small flame and the pilot does not light. The ignit


probably need a new control board. so it sparks but gas not coming on? usually you will hear a click then hear gas coming out. if you have a voltage meter check voltave going to gas valve while ignighter is clicking if you have voltage bad gas valve. you should read about 24 volts at gas valve.

Mar 09, 2014 | Air Conditioners

1 Answer

I have goodman central air system. AC works, fan on works, heating does not. When I have heat on led flashes 3 times( pressure switch open), I blowed at the rubber hose and I can hear the clicks. I re


Check to make sure the orifice on the inducer motor is clear if it is clear **** on hose going to pressure switch to make sure it closes if ur hear it click while sliwly sucking look to see if igniter lites if igniter lites ur heat should work if it doesnt lite then the pressure switch may be bad

Nov 04, 2012 | Air Conditioners

1 Answer

Duo Therm Mod# 90120.001 runs but won't light


There are only three things that stop a burner from lighting (or engine from running): 1. No fuel 2. bad air/fuel mixture 3. no source of ignition.

Guess what? It's one of these three.

For starters, I actually have this furnace. First things first, make sure you have sufficient voltage to the unit. It runs on the 12 volt system, so make sure the battery is fully charged and/or you are plugged in to "shore" power and your inverter is working. If the voltage is low, the fan will run, the relays will click, but the gas valve may not open and the igniter may not have the juice to run.

At startup, you should hear relays clicking. Three times, on/off, 10 seconds apart, before the board gives up trying. If you don't hear this, probably bad board or bad hearing, but possibly bad sail switch (switch tripped by main blower air flow), relays, or gas valve actuators.

The blower will run even with the control board disconnected.

Next, check for obstructions in the inlet/exhaust, like wasp nests. Wasps LOVE hydrocarbons for some reason. Truthfully though, this shouldn't be a problem unless the nest completely obstructs the tube. This furnace has a choke which restricts the airflow to an area about the diameter of a large middle finger or a small thumb anyway. That's what the "burner air adjustment" adjusts.

If everything is clicking but it still doesn't light, you should be able to smell gas at the exhaust. If not, guess what? Probably no gas. Points to bad board, sail switch, low voltage at valve, or bad valve (unlikely).

Assuming you have gas smell, check the connection to the igniter. Heat/cool-down cycles will tend to loosen the nut. It's a .25 inch socket by the way. To get at it you need to remove the furnace from the RV.

After removal, to get the furnace out of its shroud, you only need to remove the hex screw at the center-front by the gas valve and the wiring pull-thru on the right side. Then the unit will slide out.

While you're at it, check the gas orifice for obstructions. I did this by removing the air inlet shroud, but there may be an easier way. I think you can remove the whole gas assembly instead, but removing the shroud lets you clean everything up a bit. I had mud wasps obstructing the inlet tube. The tube has a choke inside like a flattened golf ball. If you remove the tube it will fall out. It's a little tricky to get back in, but not impossible. Just line it up with a nail.

The gas jet is quite large as gas jets go. Remove the jet and clean it with brake cleaner and/or compressed air.

Check all connections, tighten as necessary. Clean and tighten ground connections, blow or vacuum away dust. Vacuum through the exhaust while you are at it.

Reassemble and spark her up on the bench.

You can McGyver a battery connection to the unit to test operation. Red to red, negative to yellow. The blue wires are for thermostat. Short them together to test operation.

This won't help much without gas, but you can at least see that the sail switch operates properly.

The sail switch controls gas flow.

You can't really test the igniter easily. It's high voltage and a pig to remove and replace. If you don't have a spare gasket, don't.

You can check voltage to gas valve. If none, it is either sail switch or board. Jump sail switch to test which.

Now the iffy bit. If the voltage is lower than 9.5 volts, the valve probably won't open. The question becomes "why." Bad ground? Bad connection somewhere? Bad input voltage? Bad board?

Check, clean and tighten connections. Clean edge connector on board - gently with cloth or pencil eraser. Try again.

This is the situation I have; there is a voltage drop at the valve (between connector and ground) of 3 volts. The furnace runs on shore power, but not on a fully-charged battery. I've ordered a new board.

If you don't understand me, or it still doesn't work, you need a licensed tech with access to parts. He should be able to bench-test unit, so just slide it out and take it to him.

Good luck!

PS: New board from http://www.dinosaurelectronics.com/ did the trick.

May 25, 2011 | Dometic Air Conditioners

1 Answer

Goodman gms80903bna light blinks once fan runs all the time,


I believe this code is ignition failure.
Turn power off and after 20 seconds turn power on with thermostat calling for heat. Vent blower should come on first. After a bit igniter should lite up. You should hear click noise of gas valve open up. If igniter does lite and you hear click noise, flame should come on for a few seconds minimum. If igniter doesn't lite and you hear click noise from gas valve, igniter is bad. If flame lites and then goes out, flame sensor probably needs cleaned. Both igniter and flame sensor are in metal plate under burners. Igniter has 2 wire going to it and flame sensor has one wire. If you think it is flame sensor you can remove with taking it out with 1 1/4" hex screw. Flame sensor will have white film on it if it needs cleaned, clean with steel wool or a dollar bill. If it isn't weither of these it is gas valve or circuit board.

Jan 27, 2011 | Goodman Air Conditioners

1 Answer

I have a Rheem furnace rglh-10nbrjr that motor runs but flame does not light. If I turn up thermostat, the fan comes on and I hear a click after 10 or 15 seconds. I see no spark or anything from electronic...


Hi, you shouldn't smell any gas until the pilot flame is etablished. The sequence of operation is the small inducer motor will start on a call for heat, Then on the motor you should have a poly type tube, clear, that runs over to a pressure switch. It is a round silver part that the hose connects to, The pressure from motor closes a set of contacts and you will hear a click. This is telling the electronic ignition to start to spark and light the pilot or hot surface ignitor, which ever you have. If you have no spark and the pressure switch is closed, you have a faulty ignitor board or module. To check the switch, it will have 2 wires going to it. Just take a piece of insulated wire and touch across the 2 terminals. It should fire up. If not, the module or board, ignitor has failed. You will need to take all of the numbers from it amd go to a appliance parts house to get a new one. Don't forget how it wires back in, or you will have more problems.
Sincerely,
Shastalaker7
A/C, Heating Contractor

Dec 28, 2010 | Air Conditioners

1 Answer

Just installed new Goodman 95% updraft furnace with 3" supply and vent lines going out through wall. Gas valve won't open. Circulation blower runs in manual on, A/C system runs fine. I have used an...


Make sure you have bled your gas lines. If any air is in the lines, it will cause the unit to do exactly what yours is doing. The relay "click" you hear is the gas valve opening, but if there is no gas, it will not ignite. This is common for a new install. I hope this helps or at least points you in the right direction! Good luck!

Sep 27, 2010 | Goodman Air Conditioners

1 Answer

Raypak pool/ spa heater Low NOx Model 407A: Will take long time to fire, stays in spark mode, and then when iit does fire, it shuts off and takes long time to fire again. If you can get it going it stays...


The pilot is not proving to the control.Check that there is a GROUND/EARTH stake to the pool heater in the dirt.The pilot assembly needs a ground wire too the control.

Sep 16, 2010 | Air Conditioners

1 Answer

I have a Rudd furnace model UGRA-04EMAES in heating cycle inducer makes pressure switch ignitor lites up no gas pressure i rplaced gas valve and board still no gas. Wat next?


Well first you want to verify that there is gas pressure coming from the connector. Turn off the valve and disconnect the connector. Then turn on the valve for 1 second and back off. You should get plenty of gas flow. Be careful doing this!. Then inspect the opening at the adapter to the control. There is a screen inside there. Make sure the screen is clear(not plugged with pipe dope,lint ect). When the igniter reaches the 2200 degrees you should hear the gas solenoid valve click open releasing gas. If you hear it click and no gas is released you will need to inspect the burner orfices. The orfice has an extremely small hole and there is a posibillity that they are plugged with debris. You will need to use a very small wire(like a tie strap) and insert it into each hole and see if there is anything in the orfice. If you do not hear the gas valve click then it might not be getting the signal it needs due to a weak igniter or flame rectification sensor. Does your furnace have a stand-by pilot that is lit by the hot surface igniter or does the igniter directly light the burner assembly?

Feb 20, 2010 | Air Conditioners

1 Answer

Ruud urgh07e36jkr heater wont turn on


Well I checked and the pilot would light and then go off right away and repeat.I jumped the 24v terminal to the pv pilot valve terminal on the ignition module and the main burner lit up. I then disconnected the spark igniter and the burner shut off and it tried ti relight producing hi energy sparks from the ignition module. So I ordered the module from american hvac parts online and replaced it. I recieved an updated module and had to hook up the 24v to the th-w terminal to make it work the old module was a s86ooh
And i just searched the new model number to figure out how to make it work. The new one has self diagnostics on it. It cost 208$ with shipping

Dec 11, 2008 | Ruud UAMB Air Conditioner

2 Answers

Turn Thermostat to call for heat (here click)from the t-stat calling. I do not here the multiple click (ignitor)and then the flow of gas. I have a Honeywell VR8204M electronic gas valve. I have votage...


Wiggle wires, it could be something as simple as a loos connection. If your getting power to valve and it's not opening your valve is bad. Also check your limits somethimes all limits are connected and one broken one will throw the system off.

Dec 01, 2008 | Honeywell Air Conditioners

Not finding what you are looking for?
Carrier XHB123D X/Y Series Heat/Cool Air Conditioner Logo

Related Topics:

589 people viewed this question

Ask a Question

Usually answered in minutes!

Top Carrier Air Conditioners Experts

Cindy Wells

Level 3 Expert

4761 Answers

yadayada
yadayada

Level 3 Expert

61249 Answers

Lawrence Oravetz

Level 3 Expert

7686 Answers

Are you a Carrier Air Conditioner Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...