Question about Weather King 10AJA2501AH Air Conditioner
Wiring a heat strip
My heat strip has a 60 & 30amp breaker what do I need in my breaker panel to hanel the heat strip
  • Anonymous Jan 20, 2009
    I have a heat strip system here in Florida. it only runs for 30 seconds at a time. Any help here?
  • 61 Answers
Both, You will need to hook up two separate breakers with two different circuits.
Posted on Nov 30, 2008
I HAVE A 2 1/2 TON PACKAGE HEAT PUMP . THE60 AMP BREAKER AT THE DISCONNECT BOX KEPT TRIPPING . I DISCONNECTED THE HEAT STRIPS AND NOW THE 60 AMP BREAKER ISNT TRIPPING . WHAT IS CAUSING MY BREAKER TO T
You need to check the current rating of your heat strips. If it is more than 60 amps then you need a bigger breaker. If 60 amps or less then your heat strips are going bad. Also make sure your fan turns smoothly without any wobble.
Jan 06, 2014 | Electrical Supplies
How to ground a circuit breaker panel to an outside ground rod
First of all you need to have two grounding rods outside the house. Usually they're 12' long and have to be driven in 11-11.5 feet... but different particulars apply to different states and local codes. Ground rods should be placed no less than 6' away from each other and as closely placed as possible to the equipment or structure they are intended to protect.
wrap the stripped 14 AWG wire tightly around the copper ground rod. Try to get it as flush against the rod as if possible so that when you heat the rod later, it bonds very strongly at all points. Then heat the copper rod, rather than the wire and allow the wire to be heated by the rod. Don't heat wires directly or instant oxidation will occur, making it much more difficult to solder. Leave the ground rod to cool off for about an hour.
You would then dig the area to place the rods. The wires running off of them need to be ran to the circuit breaker box and terminated to the grounding bar. If there isn't a grounding bar in the box (only neutral) you can buy a single grounding bar specific to your box to install.
Jun 23, 2012 | Square D Qo 100 Amp Breaker Box Qo120m100...
Need to install a 2pole 20 amp gfci breaker in an ite bq panel. what are my options as I don't think they make this breaker in type bq?
Hi Pauline, I'm an electrician and can help you with this problem.
The only breakers that are permitted to be installed in any circuit breaker panel are listed inside the door on the label. Introducing any other type or brand is a fire hazard and a code violation. The national electrical code is very clear on this.
If you need to provide a GFCI protected circuit from this panel, you'll probably need to install a smaller panel from this panel - called "sub-panel" of a brand and type that will accept a GFCI circuit breaker. This is done by purchasing a 2P20A GFCI breaker and a smaller circuit capacity / ampacity panel rated for the same voltage as the main panel. You'll also need a ground terminal strip for this panel, too. A 60A main lug panel with 8 or more circuits type panel might be a good place to start. Purchase a 2P circuit breaker with an ampacity no greater than the sub panel is rated at - in my example - a 2P60A would be right. You may use a smaller breaker (2P40A or 2P50A) if you wish - but none greater. Mount the sub panel in a location near the main panel. Remove and discard the bonding screw or lug (if provided and installed already) that may connect the neutral bar and threaded into the panel enclosure. Install the ground terminal strip you purchased separately into the threaded holes provided for it inside the panel enclosure. Install the Ground symbol sticker next to this bar. Run a 4 conductor cable, pipe & wire, etc. feeder sized for 60A based on the location, temperature, etc. between the main panel and the main lug panel. Terminate the cable the sub panel end as follows: black & red or "hot" wires into the the lugs that are connected to the bus bars, white or "neutral" to the neutral bar and the bare or green "ground" wire into the ground terminal strip you installed previously.
Next terminate the other end of the cable. Power off the main panel completely. Terminate the white neutral and the bare or green cable in the neutral bar in separate terminals. Install only one wire per terminal - do not "double up" wires under a single screw. If there is a separate strip for neutral and separate strip for ground - maintain neutral wires to neutral strip and ground wires to ground strip. Also, do not intermix ground and neutral wires in the others terminal strips! Install the 2P60A breaker in an unused space in the main panel. Connect the two hot wires to the breaker terminals. If using aluminum wires, be sure to clean and apply oxide inhibitor to stripped ends of the wires.
Now, you should have a smaller panel with 8 or more empty spaces for circuit breakers that will become live when the 2P60A breaker is in the main panel is turned on. With it still off, install the 2P20A GFCI breaker in the new sub panel. Run your circuit(s) to this panel. Connect them as usual - but any neutral and ground wires installed must be terminated in their respective terminal strips. As mentioned above, never install them in the others strip.
If installing in a 3 phase environment - you may wish to install a 3 phase sub panel so that 3 phase loads can be connected to it. This will require a 3P60A breaker and 5 wires instead of 4 wires to be run between the two panels. The additional wire would be a hot and blue in color for a 240/208/120 panel.
I hope this helps & good luck!
Apr 26, 2012 | Siemens /ite Bq Circuit Breaker Bq3b090 3p...
Trips the breaker on the trailer when the heat strip is turned on
You have an electrical short, it some time forms at the heat strip after years of use the small wires break and cause a short. You need to replace the heat strip, and or it might be a bad breaker. There is really need no other reason for the short.
Oct 07, 2010 | Dometic Rooftop RV Air Conditioner
I purchased a 5ton goodman heatpump 6 years ago. the breaker for the heat strips keeps tripping, which a service technician changed last year because it was doing the same thing. The heat strips only come...
Hi, sounds like you could have a couple of problems. If the breaker is tripping when the strips are calling, they are drawing more amps then they should. The data plate on the unit will tell you the Amperage rating of the heat strip package that is installed and should match that of the breaker. Since the breaker was replaced I would recheck how tight the wiring is at the breaker as they will lossen up do the the heat they are pulling. Make sure they are tight both at the breaker and at the strips, just turn the breaker off and check this. Also, the strips should energize when the thermostat needs them to help out the heating cycle. It is good you can manually turn them on, but you shouldn't have to. I can not guide you through the process of checking T-stat operation as I would need to be on site to see how they wired it at the unit and stat.If it has always worked this way then this is most likely the way the installer wired it. If not, you will need to have the stat checked out. I would consentrate on solving the breaker problem. Just look at the data plate for the strips amperage and see if it matches the breaker amps. Tighten these connections and I bet this will solve the big problem. If you had a clamp around amp probe and with some help from me I could guide you on how to do an amp check to see if its the strips, wiring, or breaker by doing a amperage check. Tighten up all the connections and keep me posted for more help. I will be here to help you solve this.
Good Luck,Shastalaker7
Jan 11, 2010 | Heating & Cooling
Rheem Heat pump 5 ton heat strip 10KW what
I would say this is around 75 amps of draw at max for both the compressor and heat units. . Therefore--at least 90 amp breaker, and probably 100 amps for good measure, and at least #4 or #2 wire to the unit.
Oct 09, 2009 | Heating & Cooling
My electric trips out when I switch the tumble dryer on
Sounds like the plug cord is wired wrong on the dryer, or the breaker is too small or going out. Or the heat strip could need to be replaced.You should have a 30 amp breaker for the dryer. Check the heat strip then your breaker.
Sep 02, 2009 | Hotpoint Dryers
Wiring a heat strip
DO YOU MEAN FEED IN OR FEEDING HEATING ELEMENT . I ASSUME YOU MEAN TO FEED FROM PANEL THE ANSWER IS YOU MUST RUN 2 CIRCUITS OF 3-cond #6 copper to unit connect the feeds to one breaker and the other circuit to the other breaker the neutrals connect to lug provided or purchase them and frame gnd to case , i would not recommend anything except copper as most mfg do not rec aluminum because on the heating and cooling of the unit and conductors
Nov 23, 2008 | Heating & Cooling
Circuit Installation
The process contain a certain degree of risk, but if you follow all safety steps, you should be just fine. Most standard electric panels have a main disconnect switch or breaker at the top of the panel or load center. It is a code requirement. If the load center doesn't have one, then look for the main disconnect at a different location possibly near the electric meter. Turn it off. You better have a flashlight handy or a caving or miner's helmet, because you are going to need a light source. Circuit breakers plug into the load center. The electricity flows into each breaker via a large metal strip inside the panel or load center. It is called a bus bar. This strip is HIGHLY dangerous. Touch this strip while it is energized and you will very likely die. If a screwdriver you are holding slips and touches it, expect nearly the same result. Keep in mind that even though the main breaker may be off, the bus bar may be energized for any number of reasons! Also, the wires leading into the top of the main disconnect are always energized and represent a life safety hazard. In other words, the inside of an electric panel or load center is ALWAYS a dangerous place to be. The black wire to a circuit attaches to one end of a standard or AFCI breaker. The location is almost always a hole that is drilled through a threaded cylinder. A screw twists into this cylinder and tightly clamps down the wire. When installing a new breaker, I always find it easier to attach the circuit wire to the breaker before I plug the breaker into the panel. When removing a breaker, I usually unplug the breaker from the bus bar and then remove the circuit wire from the end of the breaker. Make sure the breaker is in the off position. The end of the breaker where the circuit wire attaches almost always has a small notch in it. This notch fits under or slides into a metal tab strip that runs parallel with the bus bar. This is what stabilizes the breaker. Without this secondary attachment, the breakers would flap in the panel much like a sail that is not tied down to the mast or the side of a boat. Tip the end of the breaker so the notch slides into the metal tab. You then align the breaker with the bus bar and push it down onto the bar. The tension tabs on the breaker open slightly and grip the bus bar as the breaker seats itself. If you feel the breaker seated itself correctly, simply turn it on. All should be well. Remember to follow the instructions that come with the breaker. Always follow the sequence the manufacturer suggests. AFCI breakers require one additional step. You need to locate the white wire that is paired with the black wire in that circuit. The white wire actually attaches to the breaker as well. There is a coiled white wire that leads out of the breaker. This white wire attaches to the neutral bus bar in spot that is vacated when you disconnect the white wire of the circuit. If this answer scared you, call an electrician!
Aug 27, 2008 | General Electric 20 Amp, 1 Pole Thick Type...
Weather King 10AJA2501AH Air Conditioner Logo
Top Weather King Heating & Cooling Experts
Tim Whalen
John Tripp
John Tripp
acrman404a
Level 1 Expert