Question about Siemens 20Amp 1-pole arc-fault circuit breaker
3 combination arc fault breakers tripping under load
I have a 100 amp sub panel in garage,new addition above garage.2 arc faults serving lighting in the addition and 1 arc fault serving plugs in the addition.garage plugs are dedicated.When I plug chop saw or any large load in garage plugs it trips arc fault breakers that are on same phase. When I plug something in to the other phase like bath plug it trips the other arc fault breaker on that phase.These arc fault breakers will not trip unless there is a load.This is a older house and the only outlets affecting these arc faults is on the new sub panel.I can plug a halogen light in the arc fault circ that only has plugs, and it doesn't
trip.When I put a roto zip or vacume it does.I have tried these arc fault brakers in my own 100 amp sub panel and they do not trip with a vacume or roto zip.I have checked all nuetral connections at this house including transformer and meter.Please help.
  • 102 Answers
What is happening is the white wire that comes off the breaker is probably too close to another neutral or too close to a hot wire that is on one of the other circuits that will make it trip when you use a drill etc... Check to see if the coiled up white wire off of the breaker is not near a hot in the panel. I have had lots of arc fault breakers trip for that reason.
Posted on Nov 28, 2008
My 3 arc fault breakers run hot and draw about a third of an amp from the ground bar wire each, 24/7. Is this possibly normal?
How did check amps. I would check the amps on the circuit itself. Might be drawing close to max. thats why it's hotter. breaker should have no more than 80%. Of an amp draw on the circuit
Oct 05, 2016 | Eaton ARC FAULT CIRC BREAKER
Why are these breakers hot and constantly draw .35 amps from the ground bar?
When current is going through wiring and devices it normally operates warm. That is why most wire and devices such as breakers are rated at 70 degrees Celsius. In a panel, heat can be transferred through the buss bar they are connected to.
Breakers will trip for 2 reasons. Overload amperage and heat.
15amp Eaton Arc fault breaker type BRAF trips every day at same time. There are no high amp electrical things plugged in. What is causing this? should I have it replaced?
"Arc fault" breakers trip when an arc occurs, either in a receptacle or a light switch, for example. An arc can be caused by an old light switch, when turning it on. An arc can also occur when you unplug a chord while the device is still turned on or running.
Aug 25, 2013 | Eaton ARC FAULT CIRC BREAKER
Installing arc fault interrupter with ground fault
If you meant arch fault with ground fault then no, the two types interfere with each other and trip the breaker as one senses an arch and the other grounding.
If you meant ground fault breaker with a GFCI. receptacle, you only need one of the two, either GFCI. breaker or receptacle.
and for circuits, you can put up to 12 devices (i.e receptacle, light)assuming they consume 1 amp each. Anything over 12 amps or 80% of the rating on the breaker, it will trip/reset.
Or if your talking about wires on a breaker then no more than 2 wires recommended. Try adding a junction box outside the panel if your trying to add other branch circuits or tap off of a receptacle.
Apr 21, 2013 | Siemens Seimens Arc Fault Breaker
Arc fault breaker trips when you turn florescent and can lights on
Sounds like something is wrong with the light check the wiring. Unhook the light and try ther breaker if breaker does not trip then problem is in the circuit.
Jul 24, 2011 | Cutler Hammer "CUTLER HAMMER" ARC FAULT...
We have a new 12 room motel addition we are wiring. There are two bathrooms in which the arc-fault breakers are trippping. The loads are - two three lamp incandescant wall fixtures, and two GFCI...
Hi, I know it sounds simple but sometimes its the simplist things that get you. Check your earth, as it sounds as if this may be causing the problem.
Sep 28, 2010 | Eaton ARC FAULT CIRC BREAKER
Arc fault breaker trips sporadically
Are there any heaters anywhere in the circuit for this breaker? (ie: bathroom fan w/light and heater) If yes, I would suspect and inspect them first. Also,any type breaker will trip more easily if the electrical connection screws on the breaker are not tight enough...check to make sure that's not the case.
Jul 31, 2009 | Eaton 20A ARC FAULT BREAKER
Arc fault circ breakers feel warm
If the breakers are 20 amp and the panel is rated at 100 amps, only 5 breakers. if the panel is 200 amp, only 10, 20 amp breakers and so on
Dec 23, 2008 | Eaton ARC FAULT CIRC BREAKER
Arc fault trips under load
Arc fault breakers are definitely a pain. First make sure the receptacles are made for a 20 amp circuit. Second vacuums, Curlers,and most appliances will trip your breaker since they create an arc or a short if you will to operate. That is exactly what these breakers are made for. To stop the arc. Apparently they never really thought the whole arc fault thing through. As per code in most of arizona you only need this breaker in bedrooms where this type of appliance is not used. They also are more prone to popping so make sure you aren't running something on each of the receptacles at the same time
Dec 18, 2008 | Siemens 20Amp 1-pole arc-fault circuit...