Question about Heating & Cooling

1 Answer

York Air Handler trips main circuit breaker

A 10 year old York Air Handler is trpping the main circuit after running in heat mode for a short period of time.

Something is causing the unit to drawing more current then normal.

Posted by on

  • 2 more comments 
  • ptansill Nov 23, 2008

    Yes, it is.



    Testing: I'm running the Air Handler fan only

    to determine if the Blower is having an issues.

    I am going to monitor the current draw for the blower.



    The AH has been tripping the main circuit during Heat mode



    This unit has 2 electrical heating coils.



    I'm searching for proper max current draw to determine if the 50amp breaker is suffiecent.

    This is what has been in there for years without any problems.

  • ptansill Nov 23, 2008

    Jason,



    I checked the heating coil and the resistance in each are the same 19 Ohms.

    What do you know about the Time Delay Relay and Sequencers. I believe that the problem is associate with One of the Two.

  • ptansill Nov 24, 2008

    Jason,



    I should have mentioned this earlier.

    I put a new 50amp circuit breaker and only one phase leg get hot very hot about 2 to 3minutes in the heat mode.

    Can the phase post in the electrical panel have some corrosion or siot that would create a resistive path that would heatup?

    The reason I mention this is that the wire does not seem hot.

    What if the second sequenizer doesn't do its thing?

    Note: The fan runs continuiously.

  • Ken Bledsoe May 11, 2010

    Is this a electric furnace?

×

1 Answer

  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    MVP:

    An expert that gotĀ 5 achievements.

    Novelist:

    An expert who has written 50 answers of more than 400 characters.

    Governor:

    An expert whose answer gotĀ voted for 20 times.

  • Expert
  • 124 Answers

Almost has to be the electric heat strip coils. they usually come on in stages. when the damaged strip comes on it kicks breaker. turn off all power, check with a meter , gently remove strips and inspect for broken or shorted coils. usually best to buy a new heat strip module. they are usually held in place as a module with 4 screws and a snap together wire connector .good luck. i have had some success if the wires are broken and not to brittle by bending a minute loop in the end of each wire and reconnect with the tiniest screw and washer and nut you can find, i'm talking real tiny. about the size of a bb if you can find em , or you can remove the damaged strip wire entirely to get some heat from remaining.

Posted on Nov 23, 2008

  • Karen Duncan Nov 23, 2008

    the sequencer acts as a time delay generally the first strip and the fan come on and off together. then 90 seconds later the second strip kicks in. each 5 kw strip pulls about 20 amps of electric. so sequence should be call for heat , sequencer warms up and bimetal disc snaps closed and energizes stage one and fan at about 22 amps, then a minute or two later second strip kicks in and amps jumps to 42 to 44 amps. . the sequencer could be bad generally a number 33233 or 33234 from white rogers or similar is the part. fan and number one strip go to number one and 2 set of contacts. number two strip goes to 3rd set of contacts. test with amp probe to be sure fan stays on till last strip is satisfied. youdon't want any strip on without a fan.

  • Karen Duncan Nov 24, 2008

    YES THE BUSS BAR THE BREAKER CRIMPS ON TO CAN GET coroded and the looser the connection, the higher the amps. try snugging up the wires in the new breaker and move it to a new location in the panel. problem should correct itself. any two new buss bars should do the trick. an electrician can kill power and sometimes clean up the old buss bar . try some no corode on the new breaker female connections. these problems show up a lot this time of year. 2 to 3 amps of fan becomes 45 to 50 in heat. be sure connections are snug where wires enter and connect to airhandler wires. sometimes old wire nuts get loose. they should be snug and nocoroded to. nocorode is a electric grease in a tube. available at elec supply houses and home stores. best way to connect wires to electric strips is split bolts. also at home stores or elec supply house. they connect dissisimilar types of wires and get real snug. then you wrap them with a good roll of electric tape and they last forever, but good wire nuts will work and are commonly found. however of these dozens of failed connections i see 95 percent are wire nuts , especially if you join aluminum and copper. they expand and contract at different rates and that gets loose over time. always best to use split bolts on alum to copper.

×

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Why is my heat pump tripping circuit breaker continuously?


Probably a weak breaker. I would change it and see if it happens again. If the problem continues call a hvac guy out

Jan 10, 2016 | Rheem 2.5 Ton 13 Seer Heat Pump -...

3 Answers

Why after a loud bang did breaker trip on ac/heat unit. Wont run at all now


If its a heat pump and the compressor was running, there is a possibility that the compressor itself or something IN the compressor circuit shorted out and tripped the main breaker. It could also be something as simple as a shorted compressor run capacitor.

If its a forced air system with an electric air handler, resistance heat and central air conditioning....it could be just a shorted heating element that tripped a breaker OR it could have been a control circuit short that blew out the non-fused control transformer.

There are only about fifty scenarios that could have happened to cause the noise and to cause the systems failure....but these are the first few basics that could easily be investigated.

Apr 14, 2015 | Heating & Cooling

2 Answers

Any ideas as to why the panel breaker for my Goodman CPE24-1AB heat pump would immediately trip when the air conditioner is turned on?


Without looking up the specifications for this heat pump, I cannot be certain, but I expect the operation to provide cooling may require more power than when heating. You probably can find the specifications online for this unit. As you probably know, power is measured in watts and is calculated by voltage times current. This also is likely to be 240 volts operation. If you take the specified power on cooling and divide by voltage (240), that will indicate the current in amperage that will be required to start it. Your circuit breaker is set for current and needs to be a higher current than is required. If that is the problem, you can buy circuit breakers at Home Depot or Lowes. You have to remove the front panel of your breaker box and snap out the circuit breaker. To be safe it would be good to turn off the main breaker switch before you open the front panel and remove the circuit breaker for the heat pump. Should your calculation of current required be less than the rating of the circuit breaker, that implies a malfunction of the heat pump in the cooling mode and would require a service call to the local representative of the heat pump manufacturer.

May 16, 2014 | Goodman CLQ36AR49 Air Conditioner

2 Answers

Had 16 xi Trane heat pump installed 3 years ago. It ran well for the first couple of years. It began to stop heating and would blow cold air only. Have tried both aux heat and reg. heat to run and neither...


That's a complicated system that needs a qualified technician to service it. Lots of people can install them and they run fine, for a few years. Your indoor unit, operating on 2 heat elements, will feel like its blowing cold air even though its heating, just not so well. And not like you are accustomed to. Each element (5kw)=22.7amps, on average. So 3 elements operating should trip a breaker. Its probably been operating on 2 heat element plus the heat pump. And now you have trouble with the heat pump. If you can't TRUST the guys working on your equipment, try someone else. A second opinion. Normally a 3 or 4 ton unit will have 15kw heat installed, heatpump or not. 5 ton, 20kw. If yours is a 3-4ton, cooling, the 100amp(or normally two 60 amp) breaker should have been installed upon equipment change out. If yours is blowing cold all the time, something is wrong with your heatpump. The electric heat inside operates only when the heatpump can't keep up(real cold outside), the heatpump is in defrost(then it's actually in cooling mode), or if you have the tstat in aux/em. heat. Try a local trane dealer? Of a technician with 15-20 yrs under their belt. A trane dealer should have trane tech support also. BIG HELP!!!

Mar 01, 2017 | Haier Energy Star ESA3183 Air Conditioner

1 Answer

Hello: I have a Maytag MDE9700AYM that was purchased three years ago but has been installed for less than one year. After the unit runs for 10-20 minutes, the circuit breakers trips off. Otherwise the...


It's possibly the circuit breaker rather than the dryer itself. Usually when it trips, it is overloaded or shorted. Overload can be a result of a loose connection or a bad heating element,when you remove the old breaker, see if it has some noticeable burn/corrosion marks where the wire is screwed down, I think replacing the breaker will fix the problem. Hope this helped Tim


Nov 07, 2010 | Maytag MDE9700AYM Electric Dryer

1 Answer

Runs well in evening, during heat of midday shorts out.


Clean coils both inside and out. Then see what happens.

Jul 07, 2010 | Sharp AF-R100DX Air Conditioner

1 Answer

Compatability of a R22 air handler and a R410a heat pump


1. The units should match up without a problem.
2. You will need a 40 or 50 amp breaker for the A/H and 5 KW heat strip. You will probably need a 20 or 25 Amp for the condensing unit. I would check the FLA (full load amps) rating on both units, total them and install a breaker with no more than 20% more rating than the total. You can install a small box at the A/H with a breaker for the A/H and one for the condensing unit.

Nov 15, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...

1 Answer

Air conditioner trips circuit only in the evening?


first off, it's illegal to release freon into the atmosphere. the epa could charge you $32,500, so keep it under your hat. second, if it's getting too cold where the evaporator coils are icing up, it's too lille freon, not too much. as for the breaker tripping, your compressor might be wearing out. if it's pulling too much current, the motor is failing and the compressor needs replacing. and do not do it yourself unless you're certified by the epa to move freon and have the proper equipment to recollect the used freon.

Jul 29, 2009 | Heating & Cooling

3 Answers

Heat Pump/Furnace Trip Circuit Breaker


My system will run for a short period and then suddenly trips the circuit breaker in the main panel for the heat pump.

I have a Goodman - 3 ton system about 8 - 9 yrs old. I'm being told that I need to replace the heat pump/air conditioner compressor?

What do you think?

Oct 22, 2008 | Haier Energy Star ESA3183 Air Conditioner

Not finding what you are looking for?
Heating & Cooling Logo

Related Topics:

955 people viewed this question

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

paulcarew

Level 3 Expert

2364 Answers

Dan Webster
Dan Webster

Level 3 Expert

8205 Answers

Donni Steen

Level 3 Expert

659 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...