Question about Aprilaire 600 Humidifier
Aprilaire 440 Solenoid clicking
The solenoid valve opens up ok when the furnace comes on but begins to have spasms, clicking on/off rapidly for about 5-10 seconds before shutting off. Very annoying. I have replaced it once but the new one is having the same problem. The Furnace was replaced this summer (Acroaire 90+) so I am wondering if this old humidifier is simply not compatible with the new furnace. I checked the wiring and it seems to be wired as per instructions. I am willing to get a ne humidifier but scared I’ll have the same problem if it is originating from the furnace. Any help is appreciated. Bob
JMuskovitz
  • 135 Answers
SOURCE: Aprilaire 760 Humidifier water continues to run
You need to determine whether the problem is in the solenoid or in the furnace electronics. You could put a voltmeter on the solenoid connection to see if the furnace is still holding the solenoid open after the blower stops. This will tell you whether it is the solenoid or not.
Posted on Feb 19, 2007
  • 3 Answers
SOURCE: Humidifier control .
if humidifier was wired into thermostat circuit for power instead of seperate transformer , this can happen. you need to see if you voltage going to the solenoid valve. if you do , and it isn't opening, the valve is bad . this is assuming that it is using a # 50 relay to come on only when the fan runs . . make sure the water valve is open
Posted on Dec 28, 2007
  • 30 Answers
SOURCE: turning on the humidifier shuts off the furnace
It is possible you may have wired it wrong. Make sure your humidifer is not robbing power from your thermostat. This would explain when your humidifer makes a demand to come on it robs power from your t-stat making it lose its call for heat. Wire your humidistat to the "w" terminal and the common terminal so it only runs on a call for heat. With the bypass type of humidifier you purchased it wont do you any good to run when the heat isn't running anyway. If you want an independent operation humidifier you need a steam type.
Posted on Jan 05, 2009
  • 51 Answers
SOURCE: We have an old Aprilaire humidifier (Manual
close the by pass air flow valve. shut off the water supply and finally flow the thermostat wire to the transformer or the controller and shut off or disconnect. Unit should be serviced before winter. Cell may need to be replaced
Posted on Aug 10, 2009
  • 744 Answers
SOURCE: Water drips from unit
>>Is this dripping normal?<<
No - it sounds like the fill valve, which is operated electrically, is leaking and probably needs to be replaced. If there is a separate water shut off valve for the humidifier, turn it off and see if the dripping stops. You are correct in that the humidifier should not operate in the summer. You will need to turn off the water to the humidifier to replace the valve. Also look for any other leaks in the tubing connected to the valve.
While you're there, check the unit for scaling and also check the pad or wheel - it probably needs to be replaced too.
Posted on Aug 17, 2009
Solenoid valve
The humidistat could be defective.
Dec 04, 2013 | Aprilaire 700 Humidifier
2005 Aprilaire 700 humidifier. Replaced a non-working circuit board. Now, the humidifier works fine when the furnace is running. It starts and stops as it should based on humidistat setting. Problem: ...
It sounds like it is just miswired. The low voltage wiring off the humidistat should be on W and C on the circ. board at the furnace. If you have it on R and C then it will power it constantly regardless if the heat is running or not. W is only energized on a call for heat which is typically when you want that type of humidifier to run
Feb 02, 2013 | Aprilaire Humidifiers
I need to replace the solenoid on a 560. Can someone point me to where I can find directions to do this?
Hello, turn the water off at the saddle valve and turn off your Furnace. Then disconnect the wires from the solenoid and disconnect the supply water tubing from the solenoid and the outlet tubing, now unscrew the solenoid and replace it with new one and reconnect everything and open saddle valve and turn Furnace back on.
Dec 10, 2011 | Aprilaire 550 Humidifier
My aprilaire 700 isn't coming on (no water flow). The front part of the unit has fallen off the furnace twice (held on by plastic nubs/slots...) and blew the furnace fuse/ and circuit breaker probably...
Check for voltaged at the solenoid valve. This will either be a 24 volt or 110 volt solenoid valve. Confirm power into the unit 110 volts. If you have power into the unit and no voltaged at the solenoid valve on a call for humidification at the humidistat than the circuit board or the step down transfgormer has failed.. If you do have voltage at the solenid valve than the valve has failed.
Jan 26, 2011 | Aprilaire 700 Humidifier
My aprilaire humidifier model 500 series does not seem to kick in. I try moving the manual control when the furnace kicks in but even turning the control to the max nothing happens
Check to see if you are getting 24 volts at the transformer, if you are then bring the power directly from the transformer to the solenoid valve and see if the solenoid valve clicks open by moving the knob on the humidistat. If nothing happens then most likely the solenoid valve is bad and needs to be replaced. If the solenoid valve does work after bringing power directly to it then either tne problem is the humidistat it self or the sail switch/current sensing relay.
Jan 09, 2011 | Aprilaire 550 Humidifier
760 aprilaire humidifier does not let water to the filter. I have cleaned and checked the lines in and out of solenoid.
Normal 0 false false false MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman"; mso-ansi-language:#0400; mso-fareast-language:#0400; mso-bidi-language:#0400;} Your Aprilaire Humidifier is designed to operate in conjunction with your furnace blower motor. Most installers wire a humidifier to operate when the furnace is calling for heat. To determine if your Aprilaire Humidifier is maintaining proper humidity, turn up the heat temperature 5 degrees above the current room temperature on your thermostat and set your humidifier control to call for humidity. The humidifier control is located on the cold air return duct. To set your humidifier control to call for humidity, turn the control dial to the off position and slowly rotate the dial until you hear a “click” on the control. You should also hear a click at the solenoid valve located on your Aprilaire unit. The humidifier control will have a click point at the current relative humidity level in your home. If the current relative humidity is 45% or the outdoor temperature is above 60F, the control will only operate the humidifier in the test mode.
  1. No click at the solenoid valve indicates an electrical problem. Contact your heating and air conditioning dealer to further check the electrical components of your Aprilaire Humidifier.
  1. The click sound at the solenoid valve indicates there is electricity to the solenoid valve. By turning the dial of your humidifier control to a setting above the “click point” you should see water coming out of the drain line within a few minutes which would indicate your humidifier is working.
  1. If the solenoid valve makes a click sound and there is no water draining from the unit, this would indicate the flow of water is being obstructed.
1. To determine if water flow is being obstructed, turn the dial of your humidifier control to the off position. The first location you would want to check for an obstruction would be at the saddle valve located on the water line supplying water to the humidifier. When checking the saddle valve, you want to make sure it is completely open. This can be done by turning the valve all the way to the left. If anything is clogged, it can be dislodged by turning the saddle valve all the way to the right and back to the left. Once this is done, turn the humidifier control dial above the click point and you should see water coming out the drain line.
If water is still not coming out of the drain, check the orifice and in-line strainer to make sure they are not clogged. The orifice is located in the tube on the discharge side of the solenoid valve and the in-line strainer is located on the inlet side of the solenoid valve. You may clear the orifice by inserting a needle through the small opening. Clean the strainer by running it under warm water to dislodge deposits or replace. After clearing and re-installing the orifice and strainer (be sure to double wrench all water connections), turn the humidifier control dial above the click point and you should see water coming out the drain line.
Mar 10, 2010 | Aprilaire Humidifiers
Solenoid valve will not shut when the furnace is off
Most likely you have crud buildup in the solenoid valve. But first make sure that you test accross the solenoid connections for voltage when the furnace is OFF. Put your meter to AC volts and see if you see 24 Volts when furnace is ON and 0 Volts when furnace is OFF. If you get those readings then you need to replace your solenoid valve.
Available from mfg for about $55-60
or on ebay for about $40 shipped.
search for Aprilaire 4040 Solenoid
If the above tests fail, you will need to ensure that the wiring is correct and not shorted, but is probably your valve. Install a fridge water filter in the water line to help prevent this in the future.
Dec 21, 2009 | Aprilaire 550 Humidifier
I have a aprilaire 112. How do you test the solenoid valve to determine if it working properly?
without using a meter? OK take the water line loose from the humidifier that connects to the solnoid. Turn the humidifier on or raise the humidity and water should flow. Keep in mind that if wired correctly the humidifier will only work when your furnace is running although some can be wired to bring on your furnace. You should hear or feel the click if no water comes out you may have no water flow as these valves are pretty durable and seldom fail
Dec 11, 2009 | Aprilaire 700 Humidifier
Dec 24, 2007 | Aprilaire 700 Humidifier
Feb 18, 2007 | Aprilaire 700 Humidifier
Aprilaire 600 Humidifier Logo
344 people viewed this question
Top Aprilaire Humidifiers Experts
Paul Carew
Mack Baxter
1STHVACMAN
Are you an Aprilaire Humidifier Expert? Answer questions, earn points and help others