Question about Goodman GDS80904BNA Open Flame Heater
I have a goodman gmp075-3 and it is flashing # 4 code
The blower on exaust will stay on and wont shut off the light blinks 4 times it says open limit switch
  • eclipseprodu Feb 02, 2009
    I'm also getting a flashing #4 code light but when my furnace is turned on, the cold air fan engages but not the rest of the system. The ignitor and exhaust fan do not engage at all. Can a bad limit switch cause the system to shut down completely?
This information saved was incredibly useful and I appreciate the shared knowledge. Thanks much!
Posted on Jan 21, 2009
    Problem Solver:
  • 15 Answers
There is a Primary High Limit Switch towards the middle of the furnace, it more than likely needs to be replaced, very common to go out only after a few seasons. Also, you could have a flame rollout switch tripped that will signal the same code, these switches are re-settable and are located on the outer, top and sides of the burner assembly, they’re about ½ inch in diameter with a red push button in the center and two wires “ usually purple” coming off of them.
Hope this helps
Posted on Dec 02, 2008
Goodman Furnace gms91155dxa not staying on. The system ignites, but shuts off after 3 minutes. 1 blink LED system light
100% sounds like an electrical problem, something is not allowing it to go into a duty cycle.
Dec 04, 2016 | Goodman Heating & Cooling
1993 goodman status light 4 times blinking
Witch blower is running, the inducer or the systems blower?
System blower could mean the the high limit is opening and shutting down the systems gas train, I would check this out first.
The other problem could be with the pressure switch for the gas train, it is supplied from the inducer motor, check to see if it is operating fully.
HSI boards do go from time to time, this sounds more like a system control problem.
Jan 24, 2008 | Goodman GMS90703BXA Heater
Goodman furnace GMP075-3 The thermostat was in the off position over night and sometime during the night, the induced blower and blower motor came on. The trouble light on board blinks 5 times. I checked...
Need your model # to check the codes but, this coming back on after turning the t-stat off is rare. You may have been in a lockout and the furnace re-started. Some furnaces try to start three times , then lock out. Time out, then re-start. The codes should be on your furnace blower door. Write back with this info and i could help.
Oct 12, 2011 | Goodman GMS90703BXA Heater
I turn the thermastat to heat on my goodman gms90904cxa and the inducer fan does not come on and after a couple of seconds the lights blink 3 times
Hello, a 3 blink pattern indicates a open limit switch. Most of the time a dirty filter, dirty blower wheel, weak blower motor, can cause the limit switch to open.
Oct 02, 2011 | Goodman Heating & Cooling
Have a gmp125-4 furance blower runs all the time checked themostat wires error code 1 blink then 2 then 3 then 5 furance works if you turn power off turn back on when heat kickes off blower comes on gives...
Sounds like limit switch issue. Furnace heats up, high temp limit switch opens, fan will stay on. GMP model is older and do not have the codes.
May be over fired, have airflow problem, to cause the limit to open.
Next time before shutting off power, try to find the limit, it has two wires that connect to a 1.5 x 2 inch card mount to the furnace fire wall. tap on it and see if the blower stops. If so replace the limit.
Sep 06, 2011 | Goodman Heating & Cooling
I installed a new goodman unit this past spring. It seems to work ok to good in the day time but the tempature is warmer so we do not need as much heat. At night I know the thermostat is coming on. I...
Heating Mode (Goodman Service Manual)
· The furnace control checks for an open main limit (this
limit is normally closed). If the limit is open, the furnace
will remain inoperable until the limit is closed. During
an open limit the circulating air blower will be
energized. The status light will blink four (4) times.
· The room thermostat reacts to a demand for heat.
· The control will then check to insure that the vent
pressure switch is open. If, at this point, the vent
pressure switch is closed the control will blink two (2)
times and will remain inoperable until this situation is
corrected.
· The venter blower is energized.· The vent pressure switch will close when it detects a
pressure in excess of its setting. If the pressure switch
fails to close the status light will flash three (3) times.
The sequence cannot continue until the pressure switch
closes.
· After a pre-purge of about ten (10) seconds the electronic
ignition device will be energized.
· After a slight delay the gas valve will open.
· The burners will ignite and the flame sensor will detect
the presence of flame. The ignition device will
deenergize. If the sensor does not detect the burner
flame, the gas valve will close and the ignition cycle
will be repeated for a total of three attempts. If, after
the third attempt, the presence of flame is not detected,
the furnace will go into a lockout condition for one (1)
hour. It will then repeat the ignition cycle. This one (1)
hour lockout and retry will occur indefinitely.
· Thirty (30) seconds after the main valve is energized
the circulating air blower will be activated.
· The furnace will remain in operation until the demand
for heat is satisfied.
· Once the demand is satisfied the venter will shut off,
and the circulating air blower will shut off after the field
selectable time off is attained.
· The furnace will remain dormant until the next demand
for heat.
Dec 03, 2010 | Goodman GMS80903BNA Heater
Red light blinks 4 times, will only cycle once
the high limit is sensing the internal temprature of the furnace.If your filter is very dirty or you have to many of the registers/dampers shut it will cause the temp. of the furnace to exceed its rating and the high limit will open the circuit and shut down the flow of gas. Your blower will then run until the furnace has cooled and the switch will close and allow it to come back on. This is bad for your furnace, make sure your filter is clean and you dont have to many registers shut. If you have run the unit without a filter the problem could be much more sever requiring blower wheel and coil cleaning and possibly a cracked heat exchanger.
Sep 12, 2009 | Goodman GMS90703BXA Heater
Goodman Model GMNT100-4 Auto Power Down and Up until Temp.
Keep in mind all furnaces and circuit boards are not the same. Look on the back of the door to the blower compartment. You should find the list of diagnostic codes. Look up four blinks it should narrow down the problem. Although from the discription you gave it sounds lie the high limit control. When a high limit appears to be acting up it DOES NOT mean that the high limit needs replaced. The high limit just may be doing its job. This means that the furnace is overheating. Check your filters. Are all of your registers open? Is your blower set on the right speed? Is your blower going bad? Is the blower motor capacitor bad? Is your evaporator coil restricted? Just changing a high limit switch does not always solve the original problem!
Good luck....
Apr 01, 2009 | Goodman Heating & Cooling
Heating & Cooling Logo
623 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others