3 year old Beckett AFG with Clean-Cut system. New inline filter new strainer, new nozzle, flame looks correct in pattern always. Flame does not sputter prior to shut-off. I did notice that when it shut off though the motor kept running for some seconds(maybe 5 seconds)which is unlike when the motor shuts off as in a satisfied call for heat. Burner shuts down. Sometimes will run for 2 or 3 hours all normal and other times will shut down after running 15 minutes. Green led goes to "lockout" mode - 1/2 second on - 1/2 second off. I blew 60psi backward into the fuel supply line to clear a possible restriction. No change. Cleaned the eye, no change. I suspect a bad R7184B that is maybe heating up and failing. Do these units ever have fuel cut solenoids fail? This is ruining several nights already with 35 degree weather. I run down and push the reset button and sometimes I get heat for an hour sometimes for 15 minutes more before all goes quiet. There is a seperate new 50 gallon hot water heater also with a beckett burner which never fails and has never needed a reset so it is not an oil supply problem and have seen them both run together with no failure happening as well. What is it?
Called Beckett at 1-800-OIL-BURN and explained the problem. They told me that the solenoid on the oil pump (Clean Cut) was the cause. I purchased a new pump for $50 at the local plumbing supply and installed it. Problem solved.
Posted on Nov 23, 2008
2 Suggested Answers
  • 13 Answers
SOURCE: Honeywell Beckett Oil burner locked out.....just
is a single pipe oil line or a double pipe
Posted on Nov 04, 2009
Intertherm mobile home furnace
Ok. First of all what I'm understanding is that your primary burner control is tripping off... generally this has nothing to do with getting hot unless it is mounted close to the burner (the primary control is a circuit board that read resistance from the photocell -cad cell- to prove the flame...and if it gets hot, like any circuitry, could cause problems). If it is mounted close to where the actual controller is getting hot, then build a spacer out of sheet metal. If it is not tripping because of heat, its tripping from not reading the light of the flame via resistance... hence you have to lift the Ignition transformer to access the cad cell, & clean the glass front. (Cad cells doen't usually go bad) Pull the burner, and make sure it has the right nozzle rated on the burner assembly and furnace tag. The nozzle has a gallons per hour & spray pattern degree & number representing solid, hollow, semi-hollow, etc. I recommend semi hollow if you can't find any info on it, but make sure the gph correlates with the btu's rated on the furnace. The electrodes of the ignition transformer need to be positioned correctly for proper ignition. Make sure the fuel pump is tied to a two pipe system so the pump takes no time to prime. Supply & return should be piped with 3/8 copper flare fittings with no leaks. Also make sure the inline fuel filter cartridge is cleaned.
Now if the motor is tripping the motor reset, then it is trying to overcome the resistance of the pump...a 2 pipe system will help this, & making sure the motor is not mounted crooked. Take an amp draw on the motor while it is running and comparing to RLA rating on the motor tag to your actual amps can show you a lot.
Dec 02, 2013 | Heating & Cooling
Getting poor intermittent flame. I changed out my
It sounds like there is a leak in the suction side. Be sure all connections are tight and you replaced all gaskets etc. I am not familiar with your system but hopefully this helps.
Sep 30, 2013 | Suntec a1va-7112 pump,oil burner
When i take the top of my reddy hearter off it will start right up . but when it is on it will not start>
A worn nozzle creates a spray pattern, where a good nozzle creates a fog.With a coarse spray pattern poor combustion results in an off colorflame, . The photocelldoesn't like the color, sends a signal to the computer whichshuts everything down. That's the job of the electronics. On HSI ( hot surfaceignitor) heaters it is all about correct flame color , not just flame. The part where you write "If I remove the cover again it runsfine" is a symptom of a bad, worn, or restricted nozzle (generally).Remember- the ignitor only stays red for 5 seconds, then the flame keeps itselflit. The nozzle's pattern is a cone. Lift the lid & the pattern widens(aerodynamics) - replace the lid and the cone narrows & possibly distortsthen the flame goes out. This nozzle rule will only apply if everything is correct as far asfuel delivery applies. The pump pressure must be correct- not almost correct.Set the pressure with a low-pressure gauge that registers12-15 psi max. A gaugewith a higher scale just will not read close enough to satisfy the system. If the pressure is not correct, the aboverule will not apply. Instructionsfor setting the pressure can be viewed at http://reddyparts.com/pressure.htm. In addition, a fan can cause the same problem if damaged ormis-matched to your specific model. I must mention that any air leaks onthe pressure side (or vacuum leaks on the fuel line, for that matter) betweenthe pump and the nozzle will create a rich/lean mixture at the combustionchamber, creating an off-color flame.
Mar 27, 2011 | Reddy HEATER R115 115,000-BTU PORTABLE...
I have a 5 year old RUDD heater. Burner turns on for 5 seconds then shuts off. Air filter was plugged. Replaced last week and thought prob was solved. Prob is back now. Tried pulling new filter out a...
Hello,Make sure the flame sensor is clean near the burners, The flame sensor is a metal rod that is on the opposite side of the ignitor. To clean the flame sensor you will need some steel wool, turn off power to the furnace and remove the flame sensor and clean it with the steel wool. After cleaning reinstall it and turn power back on to furnace.
Feb 28, 2011 | Heating & Cooling
Torpedo heater shuts off after several minuets, will not start again 5-6 minuets
These heaters require some preventative maintenance from year to year and here is my routine. There is a flame sensor in the burning tray, these collect carbon deposits, dust and dirt, and occasional insect nesting area. Locate the flame sensor by removing the top half of the heater, now remove it and clean with windex and soft terry cloth rag. Replace sensor and be sure it has an unobstructed view of the flame. Fuel is next, with the top still off locate the fuel nozzle, remove it and the say you can not clean these but I find that carb cleaner, q-tips and a tooth pick work just fine to clean them. Now when you remove the nozzle there is a screen filter directly behind it, these can corrode over storage so clean it too. Now inspect fuel lines for cracks, holes and dry rot. Put fuel system back together and the top on. The fuel line comes down thru the side panel and thru a filter then in to the tank. Remove side panel, locate fuel line, remove the filter and clean with a compressor and air gun. Blowing air thru the filter backwards will clean these right out. Put it back in line, put side panel back together. Next is the air filter on the inlet of the pump, they are foam. Clean this and dry it real good then put it back. Really look in the fuel tank to make sure you have no water,rust, or any other contaminants in the tank, fill with new fuel and you are ready for heat. Sounds complicated but really isn't, take your time and in an hour you will have this heater running like new.Good Luck
Dec 23, 2010 | Dayton E50 Heater
Toyostove won't burn. changed the tank filter... any Ideas?
You didn't give a lot of symptoms to work with so I'll cover a lot of possible causes.
Does it light at all? If you don't see any flame when it tries to light you need to check the igniter. You can do this with an ohmmeter. It should be somewhere around 17 ohms. You can also check the voltage where the igniter connects to the circuit board. It should be 120vac. If you don't have 120vac there your problem could be the circuit board.
Does it light then go out? This could be due to a fuel flow problem. Does the heater making a ticking or thumping sound before it cuts off? That is the sound the fuel pump will make if it's not getting any fuel to it. There is a strainer in the fuel sump that could be clogged or there may be an air bubble in the fuel line. Make sure you cut the fuel off at the barrel before you try to check the strainer. Did you vent the filter when you changed it? Another possibility for this would be a dirty flame rod. Unplug the heater before you attemt to clean the flame rod. You can clean it with some steel wool or fine sandpaper.
The fuel nozzle could also be clogged with carbon. You can remove the fuel pipe and use an allen wrench or anything that will fit into the hole and use it to clean the nozzle. Just insert it an inch or so into the burner, not much further.
Make sure you hear the blower start when you turn the heater on. You would get an EE 8 code if it wasn't.
Let me know if this helps or if you need more help.
Nov 19, 2010 | Stoves Heating & Cooling
Beckett burner; I notice small particles of soot under stack vent
The soot can be caused by a number of reasons, if it was recently cleaned, I would wonder if the service tech just left a little mess behind. If you are reasonablely sure that is not the case, one cause could be a faulty pump. Inside the fuel pump is a pressure regulating valve, that is responisible for pump pressure and cut off. If the valve is failing, and not giving proper cut off, then a small amount of oil will drip into the chamber (called "after drip") and upon start up this oil burns incompletely causing a soot build up. A delay valve often masks the problem by providing the positive shut off electronically. Another problem/cause could be impoper adj. of the burner during the tune-up. On a final note, with equipment that old, it would be a good idea to start looking into a newer, more efficient system.
Apr 10, 2009 | Leviton White Decora Oil Burner Rocker...
165,000 forced air reddy heater
It would help if I knew the model of heater because there are 2 different technologies that are used in Reddy Heaters. Having more information could affect my answer.
Generally, if a heater runs with the lid off but shuts down with the lid on, its a sign that either the air pump pressure is not to specs or the nozzle is restricted or worn out. Desa International, the manufacturer, recommends annual replacement of the nozzle, but this is arguable, depending on the age of the heater.
I am pasting a document that I've had around for awhile, that may help:
"A worn nozzle creates a spray pattern, where a good nozzle creates a fog. With a coarse spray pattern poor combustion results in an off color flame, . The photocell doesn’t like the color, sends a signal to the computer which shuts everything down. That’s the job of the electronics. On HSI heaters it is all about correct flame color , not just flame.
The part where you write "If I remove the cover again it runs fine" is a symptom of a bad, worn, or restricted nozzle. Remember- the ignitor only stays red for 5 seconds, then the flame keeps itself lit. The nozzle's pattern is a cone. Lift the lid & the pattern widens (aerodynamics) - replace the lid and the cone narrows & possibly distorts then the flame goes out.
This nozzle rule will only apply if everything is correct as far as fuel delivery applies. The pump pressure must be correct- not almost correct. Set the pressure with a low-pressure gauge that registers12-15 psi max. A gauge with a higher scale just will not read close enough to satisfy the system. If the pressure is not correct, the above rule will not apply. Instructions for setting the pressure can be viewed at http://reddyparts.com/pressure.htm.
In addition, a fan can cause the same problem if damaged or mis-matched to your specific model.
I must mention that any air leaks on the pressure side (or vacuum leaks on the fuel line, for that matter) between the pump and the nozzle will create a rich/lean mixture at the combustion chamber, creating an off-color flame."
Good luck, I hope this helps.
Dec 03, 2008 | Reddy Heater-30-55,000 BTU Variable
I have a riello burner for my central heating system. When i turn the heating on the burner ignites for a few swconds and then goes out.... the burner tries to re-ignite and the same happens. I have...
Replace the nozzle, don't try and clean it. After the burner runs a few seconds, do you have to reset the control (red button) before it will start again? Does it sound like there is a pulsation in the flame when it starts or it is running out of oil? You may have a bad ignition control. Start with the small stuff, nozzle, strainer filter, oil tank filter and then work to the more complicated.
Aug 01, 2008 | Heating & Cooling