Question about Goodman GMS90703BXA Heater
Gas does not stay on.
My heater runs successfully through the sequence of operations but when the gas ignites it immediately shuts the valve. My flame sensor has been replaced and I recently replaced the control board.
    Problem Solver:
  • 17 Answers
The unit uses "flame rectification" (basically it is sensing a pulsing dc current) to sense the flame and is very sensitive to bad/poor ground and also to a dirty flame sensor. The gas ignition does not shut off the valve ...the board is not sensing the current thru the flame so its reading a "no Fire" fault and shutting down.
Clean the flame sensor with sandpaper till its brite and shiny and check all connections to make sure they are tight and very clean, especially the ground to the board and also to the furnace itself (sometimes we have to actually drive a ground rod near the furnace itself or use some other means to make sure that a proper gorund is achieved).
If still have a problem; I would try another board, the flame sensor is just a piece of solid stainless alloy wire so its really not necessary to change it unless the ceramic insulator is cracked.
Before you buy another board, I would suggest that you have a pro look at it.
Posted on Nov 16, 2008
Heater comes on then shuts off plenty of water flow
check pressure switch and flame sensor
Mar 03, 2015 | Raypak Pool & Spa
My York furnace sometimes doesn't completely ignite
A noisy inducer probably is headed for replacement.
The igniter can produce a healthy glow and still be defective. Mine had to be replaced with a new, improved one.
The thermocouple could be defective even though it seems to open the gas valve when it should.
The heat sensor in the bonnet could be defective. That controls main blower operation.
The heat exchanger could be cracked.
Jan 10, 2014 | Heating & Cooling
The heater ignites well, but if it gets a clear blue flame (and it burns very quiet), the thermocouple will glow red and the heater stays on, but when it gets a opaque blue flame (it makes a sound when...
I would start by replacing the thermocouple. It is suppose to keep the gas valve open when in operation. If the mercury in the thermocouple dries out it won't keep the gas valve open and thus the flame goes out. If that does not work then you have a gas valve problem.
May 05, 2017 | Reddy HEATER RLP30 30,000-BTU PORTABLE LP...
Rheem Rudd G91-200 will not start. After waiting 10 minutes, it does fire up for about 2 minutes, then it locks out. Bad gas valve?
ive never seen one of these water heaters but most gas apps have a thermo-couple which the ignition flame needs to heat the top of.if the ignition flame is missing the top of this the main gas valve will shut off.it may just be a bit of dirt in the flame director.which aims gas at the couple and main gas burner.hope ive helped.good luck
Mar 16, 2013 | Rheem Tank Water Heater G91-200, 91 Gallon
Gas Dryer Ignition Issues
did you try bypassing the cycling t-stat also?
Aug 25, 2012 | Samsung Dryers
Heater turns on and heats garage to set temperature, than shuts off. when the temperature drops, the unit kicks on again. everything starts working again but only for a few seconds and than shuts off. it...
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor.If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 11, 2010 | Mr. Heater Natural Gas Garage Heater -...
Looking for sequence of operation for a lennox mid efficient furnace
When there is a Call for heat, the control delays ignition until combustion air
Blower operation has been proved and pre-purge period
Has elapsed. It then opens the gas valve and generates a
Spark to ignite the burners. Trial for ignition lasts for 7 seconds.
At the same time, the control begins monitoring the
Flame sensor. If the flame current is too weak (less than 1
Micro amp) or if the burners do not ignite (within the 7 second
Ignition trial), the control will shut off spark and the combustion
Air blower and de-energize the gas valve. Flame
Current should be between 1 and 5 micro amps to keep the
Gas valve open.
The control will attempt to ignite the burners up to two more
Times. Each time the control restarts the ignition sequence,
It begins with a 45 second pre-purge. If flame is not sensed
After the third trial, the control locks out. Lockout means that
The control shuts off the gas valve, spark and combustion air
Blower for 60 minutes. At the end of 60 minutes the control
Completely resets and will attempt ignition up to three times.
The control can be manually reset before the end of 60 minutes
By momentarily turning off power to the unit.
here is a link to an operations manual
http://0190acd.netsolhost.com/manuals/80MGF_Series.pdf
Nov 25, 2010 | Heating & Cooling
Heater will not light,ignighter glows,fan comes on,wont light,then shuts off
If your igniter comes on but no ignition, that eliminates the possibility of a bad or clogged pressure switch, high limit or flame rollout switch. Sounds to me like you have a control board, or a gas valve going bad. Could even be some loose, corroded, or faulty wiring. Before the igniter comes on the furnace does a self diagnostics to ensure everything is working, or the furnace will not make it to the igniter sequence. Inducer motor, pressure switch/s, limit controls are closed…then comes on the ignitier, gas valve opens, pilot runners and burners ignite, flame sensor detects the flame, blower comes on and all operations are working.
Hope this helps
Nov 30, 2008 | Heating & Cooling
get a volt meter and check and see if you loose 24 volt power to the gas valve then make sure your grounds are goodif thoose are ok check for a 24 volt drop on transformer
Nov 16, 2008 | Goodman GMS90703BXA Heater
Goodman GMS90703BXA Heater Logo
139 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others
