Here is the sequence I see.
I ask for heat. The combustion exhaust fan comes on. The ignighter glows. As the glow fades, I hear the gas valve clicking open but as if it is too late, it turns off, never firing the burners. I smell a hint of propane at this point.
However, if when I hear the valve kick on I BLOW THE GAS THROUGH, THE BURNERS IGNITE! - and the system stays on until the demand for heat is satisfied. But, next time, If I am not there to blow on it, the system attampts to light 3 x and on the last fail, the house blower fan comes on. I can only turn it off by cutting current to the unit. This also re-sets the unit to go through another 3 cycle attempt to fire.
It is as if the igniter and the gas valve are no longer in synck.
The error code is 2 flashes - system lockout (no flame) check line polarity.
Again, if I blow the gas to the fading glow of the igniter, the unit fires and continues to work just fine so I guess all the limiters and safery circuits are functional
The unit worked fine for years. Then a few times, we just turned the power off and it fired the next time. Now it seems the delay got worse.
Is there a way to re-set the cirquit board? any suggestions or revelations on what is wrong? Any questions to clarify my problem? Please ask. I have a multi-tester and can read wiring diagrams and usually manage to fix things myself. This time I need help. Thank you in advance for providing it.
Roadskiman
  • roadskiman Nov 24, 2008
    The burners were a litle rusty and so the gas did nopt travel well into the ignighter and flame did not light. I took each burner off, cleaned the fins, re-installed and all worked fine.
  • 96 Answers
Put your hand on the gas valve and see if the click of the valve is opening just before the ignitor goes off if it does your valve is going bad
Posted on Nov 13, 2008
The unit cycles through all levels and then displays Ignition failure, code B2. I replaced the flame sensor, the ignitor, and there is natural gas at the gas valve.
Sequence of operation for most Gas fired furnaces...
Demand for heat from t-stat
Control board demands combustion chamber purge
(IDM /induced draft motor if it has one)
Control board tests all safeties (this is usually via
the IDM wiring.)
Control board sends 24v to PV at the gas valve igniting
the pilot OR control board sends voltage to the
ignitor as in yours.
Control board sends 24v to MV at the gas valve.
Control board allows time for heat exchanger to warm
then calls for blower operation.
Your sequence of operation? Won't be the flame sensor unless ignion has been achieved. If the ignitor is working/glowing red? Is the IDM working? Make & model#?
May 26, 2015 | Heating & Cooling
Gas dryer won't light. Ignitor glows red and I can smell the gas, but no ignition. New coils didn't fix problem. Any ideas what to try next? Hamper full and wallet empty- please help!
Is your inducer fan coming on first? I know on a gas heat pump yu will hear the fan/inducer turn on for a few seconds, then the igniter will lite, then yu will hear it fire up, this is a safety feature sequence, no gas movement thru system, no ignition, also check the exhaust pipes for holes or cracks
Apr 19, 2015 | Dryers
I have a LG dryer model dlgx3002w not heating.
It sounds like you didn't install the ignitor properly. Try re installing the ignitor, because it's opening the gas valve saying it's hot enough to light, but if it's out of position, it won't create proper combustion.
Nov 23, 2013 | Maytag Neptune MDG6800 Gas Dryer
No heat, ignitor goes on burner goes on sometimes and after short time goes out. ignitor goes back on, but no burner. what up
If the flame sensor is not returning a good signal, the gas valve is shut off as a safety measure. I surmise that in this situation, the igniter is programmed to fire for a time to flare off any accumulated gas from the initial attempt to fire up the burner.
Check for the following: adequate combustion air supply (make sure inlet vents are clear), proper exhaust venting, flame sensor properly positioned and not cracked or otherwise broken, burner holes are clean and not caked over with combustion deposits (if the flame is uneven and weak right where the flame sensor is located, it will be treated as a failed ignition).
In the worst case, the gas valve is defective and unable to detect the flame signal. It's also possible that a thermostat is sending an overheat signal, but that doesn't account for the igniter sparking a second time after the burner shuts off.
May 19, 2011 | Maytag Neptune MDG9700A Gas Dryer
RHEEM RGLE-10EQAGS Gas Furnace - Intermitent. Fans come on, Hot surface Ignitor comes on, then sometimes Gas Valve opens and all is fine, Other times, gas valve doesn't open and Hot surface Ignitor goes...
The sequence is Igniter comes on, valve comes on, flame sensor senses flame. If no flame is sensed after 3 tries, a lockout occurs. If you have a volt meter, check for 24-27 Volts AC coming to the gas valve, if your getting voltage to the valve but no gas, your gas valve is defective. It could be a intermittent problem, no matter, still a bad valve. if no voltage to valve, defective circuit board.
Dec 29, 2009 | Heating & Cooling
Have a Goodman GMT070-3B which the vent motor seems to be sticking. I took apart and cleaned the brushes and reassembled. The furnace will come on only after what seems like the vent motor comes up to...
The whole assembly must be replaced.
The sequence of operation is -
Combustion fan purges the heat exchanger. A pressure switch verifies combustion air fan is running. Usually a 30-45 second purge before the hot surface ignitor glows, or the spark ignition starts.
Gas valve opens after 10-15 seconds and main burners light. Control board monitors for flame and shuts gas valve after 2-3 seconds if main burner does not light.
If burner does not light, some boards repeat this for 3 tries, then locks out and is reset by cycling power.
Air blower comes on after another 30-45 seconds after main burner ignition.
Times may vary based on the specific controller board. A flow chart and timing sequence should be located somewhere on the unit, usually in the fan compartment.
Dec 16, 2009 | Goodman GMS90703BXA Heater
When turning on my Quadra Fire 1000, turn up the thermostat the orange light should come on signaling that it is calling for heat, but the only thing that runs is the combustion blower. What to check?
Hi, I am not sure of the sequence of operation of this heater, but on most other heaters with a combustion motor on them, it will come on 1st. and then it will establish that the pilot is coming on , glow plug, or hot surface ignitor. I would check this to see if what ever ignites it is coming on next. This would be the sequence of a heater. Good luck,
Shastalaker7
Nov 24, 2009 | Heating & Cooling
Furnace gas valve wont open (roll out switch failure)
Sequence of operation, Gas Furnace.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
This is why we technicians earn the big bucks!
Dec 04, 2008 | Goodman GMS90703BXA Heater
Won't srtart
Check at the gas valve to see if you are getting power to the terminals after you hear the click shortly before the ignitor stops. If no voltage ...replace the board.
Sequence is
induction fan on, if pressure switch is reading ok condition---->
Ignitor is powered for up to 20 seconds (depends on model) ----->
Gas valve is energized ----> if flame is present everything just works away, if no flame in 3 seconds sequence starts over for set number of tries or continuously (again depending on the model)
Hope this helps
if 23/27 volts is present at gas valve then replace valve but bad valve is not very common usually, its the board.