Question about Goodman PHKJ048-1 Air Conditioner
Goodman PHJK048 Heat Pump Package
I've seen you answer many questions on the FixYa board concerning Heat Pumps and AC. We recently bought a house that has a Goodman PHJK048 Heat Pump package. It cools wonderfully and heats perfect. My question is, I've never owned a heat pump before. I'm in alabma and recently we've been having low overnight temps, around 32. I set the thermostat at bedtime to 68. The unit seems to run alot at night, and when I feel the air thru thet vent, it seems like about 68, and it seems to get noiser at night as it gets colder outside. I can bump up the thermostat and the AUX comes on and I get instant heat. Just wondering if a heat pump actually heats or cools the air at the same temp as the thermostat setting. Also, I've heard it make a loud noise as " I think" it is defrosting the coils late at night or early cold mornings. My main concern is it seems to run quite a bit when it's on heat with the temp set to 68 and when it's real cold the compressor seems to make more noise than usual. Thanks for any info you can profide.
  • 182 Answers
Ok...where to ....the thermostat is just a switch.It will tell the unit to run or not run.if you measure the temp with the heatpump running,the air is warmer than 68 but it feels cool to you because your body is 98.6.The unit will run more often and for longer periods when the temperature drops outside for a few reasons.First,your house has more of a load to heat,meaning you have more heat loss because of the difference in temperatures outside and inside.Second,your heat pump pulls heat from the outside air.The colder the air outside,the less btu's for it to pull.If you have anymore questions Hope this helps,Dave
Posted on Nov 11, 2008
Thermostat wiring terminals and colors
R - The R terminal is the power for the thermostat. This comes from the transformer usually located in the blower section for split systems but you may find the transformer in the condensing unit. For this reason, it is a good idea to kill the power at the condensing unit and the blower section before changing or working on the wiring at the thermostat. If you have a package unit then the transformer is in the package unit.
Red for the R terminal.
RC - The RC terminal is designated for the power for cooling. Some HVAC systems use two transformers. A transformer for cooling and a transformer for heating. In this case the power from the transformer in the blower section would go to the thermostat terminal. It should be noted that a jumper can be installed between RC and RH for a heating and cooling system equipped with a single transformer.
Red for RC terminal.
RH - The RH terminal is designated for the power for heating. See RC above for an explanation. It should be noted that a jumper can be installed between RC and RH for a heating and cooling system equipped with a single transformer.
Y - This is the terminal for cooling or air conditioning and goes to the compressor relay. Typically a thermostat wire pull is made to the air handler on split systems and then this wire is spliced for the separate wire pull which is made to the condenser. Some manufacturers put a terminal board strip near the control board in the air handler so a splice is not needed.
Yellow for Y Terminal.
Y2 - This is the thermostat terminal for cooling second stage if your system is so equipped. Many systems only have a single compressor but if you have two compressors which should only operate off of one thermostat then you need the Y2 thermostat terminal for second stage cooling.
*The most common color I've seen used for this terminal and wire designation is light blue but this varies and is completely up to the installer what color to use. Most installers use the color coding as noted but be aware that some do not use the thermostat color coding.
W - This is the thermostat terminal for heating. This wire should go directly to the heating source whether it be a gas or oil furnace, electric furnace, or boiler,
White for W Terminal.
W2 - This is the thermostat terminal used for second stage heat. There are gas furnaces with low fire and high fire and some depend on control from a two-stage heating thermostat with a W2 terminal. Heat Pumps use staging for auxiliary heat and need a W2 terminal.
*The most common color I've seen used for this terminal and wire designation is brown but this varies and is completely up to the installer what color to use.
G - This is the thermostat terminal used for the fan relay to energize the indoor blower fan. On a split system the blower fan is in the blower section while with a package unit the blower fan is in the outdoor package unit.
Green for G Terminal.
C - This is the thermostat terminal which originates from the transformer and is necessary to complete the 24 volts power circuit in the thermostat but only if the thermostat consumes electricity for power. Many digital thermostats require 24 volts for power so the common wire is necessary.
C stands for common and there is no universal color used for this terminal although black is the most common color I've seen.
O or B - These thermostat terminals are for heat pumps and the B thermostat terminal is used on for Rheem or Ruud and any manufacturer that energizes the reversing valve in heating mode for the heat pump. Most other manufacturers of heat pumps will utilize the reversing valve for cooling and the O thermostat terminal will be utilized for this purpose. This wire goes to outside heat pump condenser where the reversing valve is located.
Orange for O and Dark Blue for B depending on the installer of the heat pump and the manufacturer. If you have a Trane, Carrier, Goodman, Lennox, Ducane, Heil, Fedders, Amana, Janitrol, or any other manufacturer other than Rheem or Ruud you will be utilizing the orange wire for reversing valve. Rheem and Ruud will usually utilize the blue wire for reversing valve.
E - This thermostat terminal is for heat pumps and stands for Emergency Heating. If for whatever reason the heat pump condenser fails and it is necessary to run the heat there is an option on heat pump thermostats for emergency heating. Basically this simply utilizes the back-up heat source many heat pumps have to heat the home without sending a signal to the condenser to run for heat.
E - There is no universal color used for this thermostat terminal designation but this should be wired directly to the heating relay or the E terminal on a terminal strip board in the air handler or package unit if you have a heat pump package unit.
X or Aux - This thermostat terminal is for back-up on a heat pump and allows for auxiliary heating from the back-up heat source usually located in the air handler.
X or Aux - There is no universal color used for this thermostat terminal designation but this should be wired directly to the heating relay or the Aux terminal on a terminal strip board in the air handler or package unit if you have a heat pump package unit.
S1 & S2 or Outdoor 1 and Outdoor 2 - Some thermostats have this terminal and it used for an outdoor temperature sensor. The wire uses for this should be special shielded wire and completely separate form the other thermostat wires.
on Jun 06, 2011 | Heating & Cooling
Cracked water pump
You should be able to replace the housing if you contact the manufacturer.
Mar 12, 2014 | Utilitech 1-HP Cast Iron Shallow Well Jet...
Blower will not shut off on heat or ac or off goodman outside package
you have heat safeties and if one has gone out u will have the same symptoms there is usually one or 2 where the burners are at and usually one in the blower housing area they have 2 wires on them and usually round disconnect power and check for continuity thru them all if u have continuity thru all of them then ur blower relay contacts have stuck shut and will have to be replaced
Feb 24, 2010 | Goodman GPC1342H21A Air Conditioner
What's the difference between EM HEAT and AUX HEAT?
Sorry, neither of these answers are completely correct.
You have a heat pump (or the wrong thermostat). Let's assume you have a heat pump.
In air conditioning mode, it works like every air conditioner you have ever had, but...
In heat mode, it reverses its operation. Have you ever felt the air coming out of the outdoor unit of your A/C unit? It's hot, isn't it. And the air coming out of the indoor unit (out of the registers) is cold. Now for a heat pump to produce heat it simply runs the air conditioner in reverse and the heat comes out in the house and the cold is released outside. Neat, huh!
Here's the problem with heat pumps...when it is really cold outside the heat pump can't produce enough heat to heat your home. So it has an additional heat source called "Auxiliary Heat". This heat comes on automatically when the house doesn't get warm enough. The source of this heat is based on the region of the country you are in. North/Northeast generally have oil heat, other regions have gas, and still others have to use electricity to heat. In Texas, we usually use electricity as the supplementary heat on heat pumps. VERY EXPENSIVE!
Now the "Emergency Heat"...this is exactly as stated in Solution #2. This is manually turned on by YOU at the thermostat when your heat pump fails. This turns on the auxilliary heaters and turns off the heat pump (remember, the reverse air conditioner). Again, this can be quite expensive to run if your heat source uses electricity! Gas and oil may be cheaper. The emergency heat is only designed (normally) to keep the house livable (not comfortable) until the Heating Tech can get out to you and fix your heat pump.
Something else you should know. It is normal for a heat pump's outdoor coil to frost up during heating mode. It will detect this and go into DEFROST mode and melt the frost off the coil. While it is doing this, it will turn on the auxilliary heater to keep the air blowing in the house at a reasonable "warm" temperature, but it will not be as hot as normal. In fact, heat pumps produce a lower temperature heat than traditional heaters. So the air may feel cooler during heating than you are use to anyway. This is normal and is not a sign of a problem.
So what do you do: Set your thermostat to the temperature you want and set the controls for HEAT/COOL and FAN-AUTO/ON and leave the EMERG HEAT off unless your heat pump breaks.
As always, keep your filters clean and your outdoor unit's coils clean and free of debris.
Hope this explains your question for you!
Oct 16, 2009 | Ruud Central System Air Conditioner
We live in SC, have a Goodman 4 ton split system w
First of all is this unit a heat pump i'm not up on goodman model #'s if it is a heat pump reversing valves do go not a real common problem 1000.00 is excessive i would be inclined to get a 2nd opinion. plastic over the sand could create a condensation mold problem. Good luck. Tom
Jun 23, 2009 | Goodman CLQ36AR49 Air Conditioner
Goodman PC060-1B Package AC...Need Wiring Help
Depending on the size of your Electric heat you can use one set of wires because your unit does not run with the heat like the heat pump. The large set of wires going to the electric heat should be used. You may have to jumper a new set to the contactor. On Goodman unit come in L1 and L2 jumper to contactor. Very simple good luck. Rus
Jun 21, 2009 | Goodman Heating & Cooling
I have a goodman heat pump and all winter it worked fine, now i set it for ac and stil blowing hot air
The reversing valve may be stuck or it has a burnt solenoid coil. Also, check the defrost relay accross the contacts with an ohmmeter and see if it's bad. Goodman heat pumps also trip on high pressure. There's a resettable switch on some units with a red button. However, I think the problem is in the defrost circuit or reversing valve. If your electric heat is on, change the board.
Apr 27, 2009 | Goodman CLQ36AR49 Air Conditioner
Heating & Cooling Logo
307 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others