Won't srtart When I turn on the power, the inducer comes on, the control board clicks, the ignitor bar glows, the board clicks again, and the ignitor bar stops glowing. It seems like the gas valve isn't opening to allow combustion of any kind
  • Anonymous Nov 21, 2008
    Hello... I like jonsdsl simplification... My problem WAS similar... What I mean by WAS is that last week I had the same problem but this week when I got back to checking out the furnace it did act the same as last week for the 1st 2 times I started the furnace; the induction fan would run then the hsi glowed but, it seemed the gas valve would never open (no solenoid sound) which is the same as last week and it seems to be the same as Saulc's...
    When placing my hand on the solenoid (gas valve) it didnt seem to click as you would expect... NOW I don't get any of these, all I get is the red light on the board lights (steady no blinks) and I can feel/hear the transformer humming... No induction fan or hsi glowing... Am I looking at a board as well??? Is there a way to test the board??? What is the cost of a board??? I should have mentioned my furnace is an 80% Goodman about 10 -15 yrs old) I would appreciate any input... Thank you, John
    Problem Solver:
  • 17 Answers
Check at the gas valve to see if you are getting power to the terminals after you hear the click shortly before the ignitor stops. If no voltage ...replace the board.
Sequence is
induction fan on, if pressure switch is reading ok condition---->
Ignitor is powered for up to 20 seconds (depends on model) ----->
Gas valve is energized ----> if flame is present everything just works away, if no flame in 3 seconds sequence starts over for set number of tries or continuously (again depending on the model)
Hope this helps
if 23/27 volts is present at gas valve then replace valve but bad valve is not very common usually, its the board.
Posted on Nov 14, 2008
Furnace was working fine and just stopped working...it reacts to raising the thermostat but doesnt actually flame on
This is probably a ignitor.
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Please leave feedback... Thanks...
Jan 28, 2011 | Goodman GMS90703BXA Heater
My heater isn't blowing any heat. I hear the fan come in, and i think i hear the gas come on, but nothing comes out of the vents. The fan only comes on for a couple of minutes and then goes off.
Ok so here is a sequence of the heater lighting and the solution for your problem...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning. Please see the pictures below to help you identify a flame sensor.
Thanks and I hope this helps. Feedback apprec.
Jan 28, 2011 | Honeywell Electronic Programmable...
Doesnt blow any heat we checked all connections furnace clicks on but never gets warm we think maybe its the heating element but we are not sure how to get to it to check
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem.The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 19, 2010 | Heating & Cooling
I have a Arcoaire Gas Furnace (Model# GNJ100N12A1), that will not fire up. It has a White Rogers Digital Stat. First the Stat seems to be faulty, since it reads 70plus in a house that has a temp of 30...
Sounds like a faulty board. shut the power to the furnace off for a minute then turn it back on. Make a call for heat at the thermostat. The inducer should start and close contacts on a pressure switch . Once pressure switch closes the hot surface ignitor should glow red. Then the gas valve will open when the gas valve opens you should get fire till the stat is satisfied. If your concerned it is the jump out r to w on the board this will eliminate the stat. If you to reset the rollout switchs 3 timesyou're getting flame rollout and you either have a cracked heat exchanger or blockage in the exhaust piping or a bad inducer motor. Keep me posted with what you find!
Dec 15, 2010 | Heating & Cooling
Trane XR80 blows cold air. Inducer motor comes on, glow bar glows for few seconds than goes out and inducer motor shuts off. Immidiatly after the main blower comes on and blows cold air. Will blow until...
I know that it's easy to spend someone elses money but in my experience when you get one actig that erratic it's usually the control board. I would check all the wiring including thermostat. You never know you might get lucky. I hope this helps you. Thanks
Nov 29, 2010 | Heating & Cooling
I AM WORKING ON A CARRIER 90% FURNACE. IT WILL NOT FIRE UP. IT SHOWS A 34 CODE. THE IGNITOR DOES NOT ENERGIZE FROM THE BOARD. NO POWER COMING FROM THE BOARD. I HERE A CLICK AS IF IT IS TRYING BUT NO...
4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 25, 2010 | Heating & Cooling
Also my inducer does not come on
Problem: Draft inducer will not start, ignitor will not glow or gas valve will not open. Solution: Any combination of the above problem or problems could be caused by a bad furnace control board. I always troubleshoot and test the least expensive parts first, such as the pressure switch, limit switch and rollout switches to make sure they are all closed and operating correctly before I go to the control board. First, and most important things to remember is turn your electrical power off to the furnace. Most control boards are located in the blower compartment. Many control boards have a fuse located on them to protect the board from getting burned up if you have a short to ground. The fuse is usually a 3 to 5 amp fuse similar to the fuses that you might find in a car's fuse box.
Nov 04, 2010 | Heating & Cooling
OVEN WILL NOT (GAS) LITE
With the assumption you have a gas range with electric ignition and is fully powered (plugged in); the possible problem may be the "Electric ignitor/Glow bar".
When turning on the oven, do you see a redish (good) or yellowish (not good; replace) glow emitting from the very bottom or the oven/broil area?
There are typically 2 types of electric glow bar ignitors; Round and Square. Ignitors are actually fairly easy to replace, removing 2 mounting screws and cutting/splicing 2 seperate wires together. Is your ignitor "round" (circular - like size of finger ) or "square" (rectangular - like snickers candy bar)
If your ignitor is not coming on at all; this can be a couple things;
Defective Ignitor - Gone completely Bad - Out (Assuming your have full power 110v to ignitor)
Defective Gas Valve - Assist in passing 110V to Ignitor
Defective Control Board / Thermostat: Assist in passing 110V to Ignitor
FYI - As a safety measure, the ignitor needs to "come on and appear solid red" to properly pass power to gas valve; thus opening and allowing gas to pass through the burners and combust.
Jan 27, 2009 | Magic Chef 31203 Gas Kitchen Range
Goodman GMP075-3 ignition problem
Goodman gmp075-3 gas furnace and the flame cycles for 4 sec
Oct 01, 2008 | Goodman GDS80904BNA Open Flame Heater
OK, if the furnace is not lighting for even a few seconds, you have either a bad gas valve, bad wire, bad control module or no gas. The pressure switch is not the issue. Check all wires to the gas valve and look for 24 volts across them when the ignitor glows and you hear the click. Then test for 24 volts to ground. It could be a bad ground wire.