    Furnace will light, blower working as expected, heat is coming out of exhaust port but will cycle off and back on in a couple of minutes. After 3 attempt the furnace will shut down with AGS error.
    Here is what I have done.
    checked all wiring for breakages and fuses. All looks good.
    Had has gas company come out and replace meter and checked pressure at heater and we are good go go.
    Took out gas ports to check for spider webs and found one port with webs which I cleaned out.
    Cleaned filters (new last year)
    Checked pump pressure and looks good.

    Furnace is 5 years old with very little use.

    All I do doesn't fix this furnace. Any clues on how to fix

  • Anonymous Mar 02, 2012

    Pool repair guy found the issue. Was a problem with the igniter controller. Their is no test for his issue. He found an old controller in an old unit installed and all work ed. Runs great now.. the ignite cost abount 200 on ebay but his used one was 30 bicks.

×

1 Related Answer

john224

John Prohaska

  • 1378 Answers
  • Posted on May 03, 2011

SOURCE: on the jandy 400 lt


Per your owner's manual:


AGS

(automatic gas shut-down)


1. Oscillating pump pressure.

1. Clean filter or identify and repair cause of pump oscillation.

2. Low gas supply pressure.

2. Identify and repair incorrect supply pipe size or pipe line blockage.


Refer to qualified service personnel.

3. No flame at burners.

3. No flame at burners. 3. Identify and correct loose wiring connections, or problems with igniter, flame sensor, gas valve, or ignition control.


Refer to qualified service personnel.

For more info the manual is here:
http://www.jandy-downloads.com/pdfs/LXandLT_H02140B.pdf

John

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer
0helpful
1answer

On the jandy 400 lt its displaying the AGS code... what does that mean?


Per your owner's manual:


AGS

(automatic gas shut-down)


1. Oscillating pump pressure.

1. Clean filter or identify and repair cause of pump oscillation.

2. Low gas supply pressure.

2. Identify and repair incorrect supply pipe size or pipe line blockage.


Refer to qualified service personnel.

3. No flame at burners.

3. No flame at burners. 3. Identify and correct loose wiring connections, or problems with igniter, flame sensor, gas valve, or ignition control.


Refer to qualified service personnel.

For more info the manual is here:
http://www.jandy-downloads.com/pdfs/LXandLT_H02140B.pdf

John

6helpful
1answer

I have a Jandy Laars LX Pool/Spa Heater...when I try to heat it cycles three times then tells me to call for service...I feel heat coming out of the vent. The pool/spa is connected to a AquaLinks system...

If the unit is lighting then shutting off then repeating it isn't rectifying, means not sensing the flame. May have a bad flame sensor or ignition control. I'm guessing your AGS is indicated on the GUI also.
1helpful
1answer

Service AGS message is on the heater

Look here:

http://www.jandy.com/html/productsupport/

I hope this leads you to your answer.

Alternataively, you could contact your local distributor.
2helpful
1answer

The AGS "call service" light is on. Why?

AGS is automatic gas shutdown,
can be caused by problems with pump pressure, or low gas supply pressure .
Not finding what you are looking for?

217 views

Ask a Question

Usually answered in minutes!

Top Jandy Pool & Spa Experts

David Spradling
David Spradling

Level 3 Expert

13524 Answers

ZJ Limited
ZJ Limited

Level 3 Expert

17989 Answers

john h

Level 3 Expert

29494 Answers

Are you a Jandy Pool and Spa Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...