How do i byepass a goodman low pressure switch
  • 499 Answers
1st off you never bypass any device on a furnace! except to diagnose and in that case simply remove the wires and connect them! but leaving them that way generally wont work since the switch opens in of cycle and yours wont unless you play human pressure switch.
Posted on Feb 25, 2012
2 Suggested Answers
TheMobilian
  • 8220 Answers
SOURCE: goodman 95 %furnace keeps saying low pressure is
That thang might be sensing a lazy flame. In other words the flames took too long in the board's opinion to quit sensing the flame. Yall probably need to do pressure tap on the gas valve.
Here is a realistic look at goodman fault codes and what to check fer and I am assuming you are not a tech and don't know this already and am hoping it helps:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Now here is how it should all go down:
Bottom dollar: it all goes back to type of gas, the initial setup, the pressure tap. and how it is wired up to begin with.
This will give you an idea where to start I hope.
Posted on Dec 10, 2010
Condencer runs for 20 sec then off keeps repeting after 2 or 3 min goodman central system
Seems like it trying to start and then cuts out , possibly on overload. Try the machine on fan blow only , that will check the indoor unit to see if that is working. Then try cool or heat function while listening to the machine starting. If you hear a loud humming just as the fan starts, and then it cuts out, It could be a compressor issue. Possibly the start capacitor has failed.
May 27, 2015 | Goodman Heating & Cooling
WHERE IS THE Goodman GSZ130301 RESET BUTTON ON CONDENSOR
No reset button. As for low/high pressure switches they reset on their own when the problem is corrected. Usually low refrigerant.
May 03, 2014 | Goodman Manufacturing Goodman GSZ130301...
My goodman a/c is turning on and off
Hello, if he outdoor unit is doing this than it could be a pressure switch that is turning it on and off or a short in the tstat wiring. If the unit has a dirty condenser or low on refrigerant charge it can trip the pressure switch.
May 31, 2012 | Goodman CKL36AR36 Air Conditioner
Turn ac on condenser comes on for a few sec then shuts off
Some units have a low pressure safety switch, the freon charge may be low or the pressure switch is defective.
Aug 30, 2011 | Goodman CKL36AR36 Air Conditioner
Not cooling good
while the machine is running, partially block the outdoor fan until the high pressure reaches 270 psi, the low pressure should be 70 psi at this time. This should be true within 10 lbs.
Jun 24, 2010 | Goodman CLJ42AR49 Air Conditioner
Goodman model GMH95 no high heat
Some questions for you, did you adjust the Low stage gas pressure first and is is about 6" W.C.? Then did you adjust the High stage and is that about 10" W.C.? If the gas pressure is correct and the dip switch is on 2 stage, the unit should fire on both low and high fire for about 5 seconds then drop to low stage. If it does not, check the hoses going to the pressure switch for a leak. Test the high pressure switch when the unit tries to go into high stage to see if it is closing. Do not blow into the hoses or you will need new pressure switches. If it proves a closed switch, you will need to check for voltage at the gas valve. If you get none, replace the circuit board. If you get 24 volts at the orange wire hooked to the Hi side of the gas valve, you have a bad gas valve.
Oct 20, 2009 | Goodman Heating & Cooling
Pressure switch not closeing
check for freon leaks. there is a low limit and a high limit pressure switch.
Oct 17, 2009 | Goodman CLQ36AR49 Air Conditioner
GOODMAN CMA80905CXBA FURNACE. INDUCTION BLOWER NOT ENERGIZING. GETTING 3 "BLINKS" FROM DIAGNOSTIC LIGHT (LOW PRESSURE SWITCH OPEN). THE A/C WORKS & THE BLOWER FAN COMES ON WHEN THE STAT IS IN...
the pressure switch is closed before the draft motor closes it.the board is telling you that this is not right.pull the wire(either) off of the pressure switch to see if furnace tries to light.if it does,you should replace the pressure switch.