On ruud quiet 80 the fault code says ignition failure
Fault code is flashing once, saying igniton failure 1hr lockout. what is causing this?
  • 499 Answers
Check for a bad hot surface ignitier, they generally will burn white hot and if bad may be cracked visibly with a grey area marking the crack.
the unit will attempt a trial period for ignition 3 times and if not succesful will lock out. a pressure switch to the induced draft motor may be unabe to sense the pressure due to moisture in a low spot in the tube connecting the induced draft housing to the pressure switch, more often the orifice on the inducers housings plugged by carbon and needs a tiny drill bit to **** it out clear. switch itself will fail too.
Posted on Feb 25, 2012
3 Suggested Answers
  • 1169 Answers
SOURCE: How do I change the filter for my RUUD Achiever
http://www.ruudac.com/products/ProductInfo.aspx?XSL_File=ruudac_products.xsl&Market=Residential&SectionVar=Heating&Category=Oil%20Furnaces
Go to this web site and check out you specific unit. should have users manual. Hope this helps
Posted on Sep 12, 2009
  • 127 Answers
SOURCE: I have a ruud quiet 80, everything works but the heat wont come on i cant find the reset button. pls help hvac man will be here in two hours my wife thinks I can't fix it no flashing lites
The only reset switches would be the roll out types, located around the burner assembly on the sheet metal surrounding the burners,a small button located between the two wires going to the switch is the reset for the roll outs. You can jump the "W" and the "R" terminals at the thermostat or the furnace, jumping the terminals at the furnace bypasses the thermostat, if it light's without the thermostat then the problem may be in the control wiring or the thermostat. If it does not work jumped at the furnace then there is another problem somewhere in the unit.
Posted on Oct 23, 2011
Error code= two red flashes, lockout/ no flame
Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...
www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com
7 Tips and Tricks to repair your Furnace DIY - YouTube
? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check
Jan 23, 2016 | Heating & Cooling
MY YBR ENGINE MANAGEMENT LIGHT FLASHES 3 SHORT FOLLOWED BY 3 FAST
That indicates fault code 33 which is a faulty ignition coil
Fault code 12 - Crankshaft position sensor
Fault code 13 - Intake air pressure sensor
Fault code 14 - Intake air pressure sensor
Fault code 15 - Throttle position sensor
Fault code 16 - TPS
Fault code 19 - No signal from ignition to ecu
Fault code 22 - Intake air temp sensor
Fault code 28 - Engine temp sensor
Fault code 30 - Tip over sensor
Fault code 33 - Igniton coil
Fault code 39 - Fuel injector
Fault code 41 - Tip over sensor
Fault code 44 - Read write error ECU
Fault code 46 - Power supply error to FI system
Fault code 50 - Ecu malfunction
Jan 08, 2015 | 2009 Yamaha yBR125
Burners turn on for 10 sec and shut off
going out on safety. either high limit or failure to detect flame.
Dec 14, 2013 | Ruud Central System Air Conditioner
Glowworm 24hxi combi boiler fault codes
it's an ignition fault (lockout) failed to light.
cause:
no gas
insufficient gas
incorrect gas valve adjustment
electrode ignition lead defective
electric igniter defective
check air inlet duct
check connections to igniter unit.
most common cause is igniter is defective (looks like a spark plug)
if you can hear a clicking when boiler goes to ignite, then it will be igniter at fault (no spark), check lead going to igniter (for any deterioration, looks like a ht lead). if all ok. change igniter.
hope this helps?
Jan 22, 2012 | Kitchen Ranges
Hi, the lights on my circiut board are flashing the one on the left is on all the time and the one to the right of it flashes two times and then waits and then flashes two times again
Error Codes
A green LED indicates system faults
Steady On: System OK
Steady OFF: Board control fault or no power applied
1 Flash: Ignition failure (control in one-hour lockout)
2 Flashes: Pressure switch fault, fails open (switch is
stuck open)
3 Flashes: Limit switch open (main or auxiliary)
4 Flashes: Pressure switch fault, fails closed (switch is
stuck closed)
A yellow LED indicates flame status
Steady on: Normal flame is sensed
Flashes: As flame weakens, frequency of LED flashes
increases
hope this is helpful.
Dec 21, 2010 | Ruud Central System Air Conditioner
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
1F Error Code on Hayword Heater
IF stands of igniton failure. Many things can cause this. Most notable, is a clogged or dirty burner orifice. The two middle ones are the most important. But i would clean them all out. They remove with a 5/16" wrench. Improper gas pressure could also cause this. However, you need a special tool, a manometer, to read this.
May 05, 2010 | Hayward 250kbtu Ng Pool Heater - Inground
Armstrong upflow,unit works intermittent problem,call for heat nothing happens,error code of 5 blinks then 6 blinks. i have no manuel, and the panels dont have the codes on them. anyone have access to the...
Armstrong
FAILURE CODES
LED Status Fault Description
Off
No Power to the System Control
Steady Flash (11 or more flashes with no pause)
Normal Operation (Standby or call for heat)
2 Flashes
Pressure Switch Closed When It Should Be Open
3 Flashes
Pressure Switch Stuck Open 30 Seconds or Longer After Call for Heat (System in 5-minute delay mode before next call for heat). On/off switch in "off" position during a call for heat will generate this code.
4 Flashes
Open Limit Switch or Limit Switch Circuit
5 Flashes
Flame Sense Signal Sensed Out of Proper Sequence
6 Flashes - pause - 1 Flash (see Note 1)*
Soft Lockout Type 1 (Failure to light within 4 trials for ignition)
6 Flashes - pause - 2 Flashes (see Notes 1 & 2)*
Soft Lockout Type 2 (Flame sense lost during run)
6 Flashes - pause - 3 Flashes (see Notes 1 & 2)*
Soft Lockout Type 3 (Pressure switch opened during run)
6 Flashes - pause - 4 Flashes (see Notes 1 & 2)*
Soft Lockout Type 4 (Limit or limit circuit opened during run)
6 Flashes - pause - 5 Flashes (see Note 1)*
Soft Lockout Type 5 (Flame has gone away after Error Code 5)
6 Flashes - pause - 7 Flashes (see Note 1)*
Soft Lockout Type 7 (Self-check failure)
10 Flashes* - SV9520H8034 only
Line Input Voltage Polarity Reversed
Dec 12, 2009 | Coleman Heating & Cooling
Meaning of rudd furnace trouble codes
Error Codes
stuck open)
stuck closed)
increases
Dec 12, 2009 | Heating & Cooling
Heating & Cooling Logo
59 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen