Question about Goodman Heating & Cooling
Whining noise coming from furnace. Replace draft inducer twice and still noise.
WHEN FURACE CLICKS ON AND CALLS FOR HEAT THE WHINING STARTS THEN STOPS. CLICKS AGAIN AND CALLS FOR MORE HEAT AND THE WHINING STARTS AND CONTINUES UNTIL THERMOSTAT HEAT HAS BEEN REACHED AND SHUTS OFF.
hotuna
  • 288 Answers
SOURCE: Goodman furnace motor is dirty
The blower motor, squirrel cage (fan) and its housing can be removed as a whole part. Disconnect the wiring harness to the motor, remove the ground wire. Look for a couple of screws that mount the blower housing to the furnace. they will 5/16 head size and usually be at the top. The bottom slides into a metal notch on the frame. With a little work and maybe a few cuss words, pull the whole thing out. A shop vac or air compressor will remove the dirt. Some dirt may be determined to stay, so a stiff bristle brush may be needed. Replace in opposite way you removed it. If the whistle remains, check the duct work and metal panels, and anywhere there is a gap or tape. This may be the cause of the whistling noise, but cleaning the vent holes in the motor and the fan blades cant hurt and will help the efficiency of the system and increase the life of the equipment. If the whining is the little vent motor up top, then try oiling with a thin turbine type oil, or just replace it, as they are relatively cheap. If you are asking about cleaning the internal parts of the motor, I wouldn't recommend doing that. If there is an oil port on the motor housing, use the oil I recommended earlier. Most likely it has a sleeve bearing not a roller type, so that's about it.
Posted on Jan 12, 2008
Therinnaiguy
  • 1420 Answers
SOURCE: When my Goodman Gun125-5b furnace fires up the
Try and spray some mystery oil on the shaft. It may help. If not, you will be needing a replacement inducer.
Posted on Feb 18, 2009
  • 582 Answers
SOURCE: I have a Ruud 90 Plus Model UGRA furnace and blower starts immedi
NO BECAUSE THE BOARD IS TELLING THE FANS TO STARTARE THE CONTACTS FUSED TOGETHER OR STUCK IN THE CLOSED POSISTION CHECK THIS FIRST
Posted on Aug 10, 2009
gear001
  • 59 Answers
SOURCE: I have a Lennox Pulse furnace. It's making a
The bearings are bad. You need to replace the motor. Motor cost $75 to $125. Labor is on avg. $150 to $400 with an decent A/C Company . You can try to oil it but its not recommend by Lennox. That furnace at the time they build it was top of the line. Good Luck.
Posted on Oct 14, 2009
  • 232 Answers
SOURCE: need help with a goodman gmt070 furnace
it may be clogged at the barbed fitting on the induced draft motor where the pressuer switch tubing connects. take a paper clip and **** it out make sure you can stick it thru freely till you can feel the Inducer wheel then reconnect and try again.
Posted on Nov 05, 2009
How do I wire a induce fan motor
Induced fan motors on older units are wired through the high limit safety on the stack - in series. When the furnace calls for heat, the induced fan motor comes on and after a time the furnace will light.
Older units have a temp switch in the stack that rotates to bring on the burners and blower motor. . When there is a call for heat, the induced draft fan motor comes on and then the burners will light.
After the heat exchanger is warmed up the limit switch will bring the blower motor on. That's basically how it works - there are two circuits - one for the induced draft motor and the burners and the other for the blower and high limit.
New units have a plug on the board you just plug in.
A
Oct 04, 2014 | Heating & Cooling
Hi, I have a Goodman GMS80903BNA Furnace and recently what happens is that when the thermostat calls for heat the draft inducer motor starts. However, after this nothing seems to happen. I don't h
Youcould be loking at the pressure switch try jumping it out and see if it lights some times you can fool it in to working , check the hoses are tight and nor spilt or take a drill bit and just clean out the 2 ports where the hoses fit some times they get blocked , also check you air filter is clean and your fan
Dec 18, 2012 | Goodman GMS80903BNA Heater
My heater isn't blowing any heat. I hear the fan come in, and i think i hear the gas come on, but nothing comes out of the vents. The fan only comes on for a couple of minutes and then goes off.
Ok so here is a sequence of the heater lighting and the solution for your problem...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning. Please see the pictures below to help you identify a flame sensor.
Thanks and I hope this helps. Feedback apprec.
Jan 28, 2011 | Honeywell Electronic Programmable...
Hello there, I have a Goodman GMH951155DXAC furnace that I got in 2007. I have the following problem for the last 4 years: When the thermostat calls for heat the induced draft motor comes on and 30-40...
With furnace OFF ,Disconnect the top of the hose that leads to the
Bottom of Daft inducer Box, Now blow into it water will come out
of the drain hoses "condensation " this will shut the unit down if not drained. There must be a Trap on the side of the Furnace with water in it , to have positive presure to suck out condensation. This will fix problem. some installers forget to install this Trap that comes with Unit.....!!!! A little item
that will shut the whole system DOWN. :o)
Jan 06, 2011 | Goodman Heating & Cooling
Doesnt blow any heat we checked all connections furnace clicks on but never gets warm we think maybe its the heating element but we are not sure how to get to it to check
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem.The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 19, 2010 | Heating & Cooling
It seems the bearings on my Induced Draft Blower Motor are going out. The furnace runs for a bit then I can hear the motor seizing. It has been making whining noise for awhile but has gotten...
While you may be able to get just a motor it will not save you much. You will also run the risk of damage to the housing or fan(s) when you take the old one apart and try to install a new motor. Unless the new blower unit is several hundred dollars I would recommend you replace the whole assembly.
John
Dec 02, 2010 | Goodman B1859005 Induced Draft Blower...
Rheem 3204-80D furance. Turns on and fan starts. Then in about a minute the fan shuts off.
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Heating & Cooling
I AM WORKING ON A CARRIER 90% FURNACE. IT WILL NOT FIRE UP. IT SHOWS A 34 CODE. THE IGNITOR DOES NOT ENERGIZE FROM THE BOARD. NO POWER COMING FROM THE BOARD. I HERE A CLICK AS IF IT IS TRYING BUT NO...
4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 25, 2010 | Heating & Cooling
Amtrol Boilermate makes whining noise
I had also this problem before, same with buzzing sounds on my Amtrol Boilermate and all I had to do was to call the local dealer and they have got it fixed.
May 05, 2009 | Emerson Part UWL Chrome Ultrasystem water...
Janitrol/Goodman GMP075-3 Draft Inducer Fan Won't come on
most forced draft fans are powered by 120 volts . close to the fan is usually a plug that unsnaps. create a call for heat after turning off to clear safetys and see if your getting 120 to fan on initial call for heat. if you are then fan draft motor is bad, usually sold as an entire assembly replace exact as it came out. sequence of operation is..... stat calls for heat via common and white wire to furnace , 24 volts. ......board sences call and sends 120 volts to forced draft ........ motor runs and creates pressure on proofing switch,....... switch closes 24 to board and tells it draft fan is on......... board then energizes ignitor,....... after ignitior glows gas valve is opened and burner lights ........ either ignitor or seperate sensor rod tells board the burner lit........ and a few minutes later the fan comes on and hot air is blown out. if a step is missed or doesn't proof the furnace either trys up to three times to light or locks out. turning off power usually resets safetys and it will resume attempts to lite normally.
Oct 25, 2008 | Heating & Cooling
Heating & Cooling Logo
299 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others