Question about Goodman GMS90703BXA Heater
GMT070-3A model Goodman furnace flame comes on then shuts off it has a single continous blink. I push in the switch the pilot lights up a few seconds and then the gas comes on and flames only for a few seconds and shuts back off, it trys to do this three times then quits. Its getting cold in here.
    New Friend:
Sounds like your flame sensor is dirty or it could be bad.
Posted on Dec 09, 2012
koolbreezes
  • 540 Answers
SOURCE: goodman gmp075-3 gas furnace and the flame cycles for 4 sec
JUST SAND THE FLAME SENSOR LOCATED IN FRONT OF THE LAST GAS PORT.
Posted on Dec 02, 2009
SOURCE: furnace filter on model gmt070-3a...
We had a similar question on our Goodman furnace, couldn't find where the filter goes.
Our furnace has two large metal covers that cover the lower and upper parts of the furnace in front, approximately 18 inches by 18 inches. The top one has a sticker that says "don't open equpiment, you may void the warranty". The filter is inside this compartment, at the bottom. You have to unscrew the screws that hold these two covers together, then just pull the filter out to change it.
I called the people who installed our furnace and aksed them if it really voids the warranty for us to open it up and they were non-comittal about it. Anyway, I opened it and changed the filter.
Posted on Jun 07, 2008
Therinnaiguy
  • 1420 Answers
SOURCE: flame sensor on a goodman heater
The flame sensor will be located either left or right of the burners and there will be only one wire leading to it. It is positioned so the flame hits it last. So if you watch your flame spread, it will be on the side last to see flame.
Posted on Nov 11, 2008
SOURCE: goodman gmp075-3 led blinks 5 times
After fighting this thing for 2 weeks, I changed out the circuit board tonight and I have heat!!!! Barnett Brass is where I got it. $100
Posted on Nov 14, 2008
  • 3600 Answers
SOURCE: I have a Goodman GMT070-3 furnace. When I turn it
if it is a fuel furnace the pump may have air in the system. here is a web site that will give you the information you will need to to help you fix the problem, there is a manual that will take you step by step to resove the problem, if you need more help understanding the troubleshooting of the system post to this e-mial you will get.
http://www.aircondition-units.com/pc-72-25-gms90703bxa-gas-furnace.aspx
Posted on Mar 15, 2010
I have a goodman propane furnace, model # GMPN080-4 that lights for about five seconds and then cuts off. It does this three times and then stops all together. Tried lightly sanding the flame sensor and it...
The goodman furnace will try and light three time before it faults out for safety reasons. Adjust the flame sensor so that it is closer to the flame or actually in the pilot flame. If the flame sensor is inside the pilot flame and still does not stay lit, your flame sensor is probably defective and should be replaced. You can get one at Ferguson's counter sales.
Dec 12, 2010 | Heating & Cooling
Furnace tries to light but misfires
Check the air filter.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Feb 26, 2010 | Goodman Heating & Cooling
I have a goodman furnace model#GMT045-3A. when I turn it on the electronic pilot works fine and the furnace will start and run about 30-45seconds then shut off. I followed the insructions for restart but...
Jan 26, 2010 | Goodman Heating & Cooling
When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can...
Nov 19, 2009 | Goodman GMS90703BXA Heater
Goodman GMP 125-4 one blinking light code. Gas valve has been replaced (at cost of $443). Didn't fix problem. Same co wanted $415 to replace circuit board. I did it myself for $99 part. Still same problem!...
One blink means it didn't light after a number of attempts. You replaced the circuit board and gas valve. Read on for some suggestions. On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Nov 18, 2009 | Goodman GDS80904BNA Open Flame Heater
Hello I have a goodman gas furnace
On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Oct 18, 2009 | Goodman Heating & Cooling
Furnace shut off after 3 time flame from pilot
Sounds like you may have a weak or bad flame sensor. If the circuit board does not sense a good flame it will not light the burners. Also if your furnace is 5 yrs or newer it should give you a fault on circuit board in the form of a blinking or a code itself.
Feb 15, 2009 | Goodman GMS90703BXA Heater
Goodman furnace blinked 1 time
Furnace attempted to start but failed after so manay tries. This may help you.
Sequence of operation, Gas Furnace.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
This is why we technicians earn the big bucks!
Dec 05, 2008 | Goodman GMS90703BXA Heater
Blower works but no heat
If in fact you have the above listed furnace, you do not have a pilot but electronic ignition. You will need to remove the front cover on the furnace, tape down the door safety switch and then have someone help you by turning up your thermostat to a very high setting. Watch and listen inside the furnace. There should be some blinking going on at the control board followed by a small blower fan starting up. Then after 10-15 seconds there should be a click followed by an orange glow viewed thru the viewing window to the burner section. In a few seconds the gas valve should click and the burners will ignite. There is a safety switch that will sense flame and then keep the gas going to the burners. If it does not sense it, it will shut it off within 10 seconds. If all is well so far, your blower will turn on in about 90 seconds after flame. There is a diagnostic code chart on the back side of the access door if you get an error code (blinking) on the control board.
Always check little things like air filter, condensate drain and broken or loose wires.
Nov 05, 2008 | Goodman GMS90703BXA Heater
Goodman GMPB-75-4 Rev 13
Is there a diagnostic chart either on the reverse side of the blower door or in your owners manual. It may help you to narrow down what is going wrong.
Operate the furnace with the access door off of the furnace and the blower door switch taped on. Watch the furnace and document what happens. Note if the flame starts but goes out in a few seconds and let me know what you experienced.
Nov 17, 2007 | Goodman GMS90703BXA Heater
Goodman GMS90703BXA Heater Logo
326 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others