Question about Goodman GMS80904BNA Open Flame Mid-Size Heater
Gms80904bna i have a furnace that has 120 volts to board and transformer. 24 volts to the r terminal on board but i have no 120 volts to the inducer motor. i have tested at the motor and the board but no voltage. is my circuit board bad or am i missing something?
    Problem Solver:
  • 15 Answers
Since you have 24VAC, put a jumper between “R” and “W”, you should hear a relay click from the control board, this is for the inducer motor, if you don’t have 120VAC at the board, you have a faulty control board, it’s the same scenario if you do NOT hear a click.
Hope this helps
Posted on Dec 03, 2008
Could a limiter circuit interupt the transformer from getting 24 volts to open the furnace valve?
Transformers typically supply 24v to the circut board, controls, and safety switches. 120v supplies the fan motor. limit switch is a safety switch and is part of the startup/ignition sequence. If the limit switch is tripped then there is a problem with your furnace that should be managed by a qualified professional in your area, or risk damaging your furnace, and perhaps causing a fire. Hope this clears things up.
Jan 01, 2015 | Heating & Cooling
Do not get 24 volts from 120/24 volt transformer how test it?
Yes. There could be a couple of high limit safety devises in the circuit that can open the circuit to the gas valve. Pending your furnace type If your thermostat is calling for heat and the furnace tries to start your transformer is working. High limit safety controls are normally closed. If you have a open limit switch you will not have any continuity through it using an ohm meter or if you test it with a volt meter you will have 24 volts across the terminals of the safety devise. Other problems can be pressure switches, hot surface igniters and control boards. most newer furnaces have a control board that will flash a light code to help trouble shoot the system. Count the flash pattern and look on one of the furnace doors for the flash code directory.
I have a programmable White Rodgers thermostat. I noticed that the room was getting warm and when I checked the thermostat the display was blank. there are no batteries. I believe it runs on 24 volt...
Hello, the thermostat reveives 24 volts from the transformer located in tne furnace via the R terminal. If there is no display on the thermostat either you are not getting power from the transformer, the thermostat itself is bad. If you have a multimeter check for 24 volts at the r and c terminals on the integrated control boatd on the furnace with the door switched taped down, if no 24 volts then the transformer is bad. If you have 24 volts then most likely your thermostat is bad. Also, if there is. 5 amp fuse on the control board check it out, sometimes they go out if there is a short in the thermostat wiring.
Jun 12, 2011 | Heating & Cooling
I have a dayton 3e228d wont fire up tried jumpin the t-stat still nothing
Hello, the first thing is determine if you are getting 24 volts at the W and C terminal on the intergrated control board on a call for heat. If not I would suspect a bad transformer. if you are getting 24 volts but the inducer motor is not running than check for a 120 volts at the inducer motor if you are getting 120 volts to the inducer and it does not start than it is bad and must be replaced. however if you are not getting 120 to the inducer than most likley your control board is bad and must be replaced.
Mar 10, 2011 | Heating & Cooling
It does not appear that my Carrier Infinity 96 is supplying the 24Vs required to my humidifier. Is there a swich on the control board that needs to be on or off to enable the humidifier power?
Hello, the control board supplies 120 volts to a transformer and then the transformer steps it down to 24 volts. check to see if you are getting 24 volts at the transformer if not then turn off the furnace and check the Resistance of the transformer, you should read resistance if not the transformer is bad and must be replaced. If you are not getting 24 volts and the transformer checks out good then a problem could be the wires going from the board to the transformer or portion of the control board is bad.
Feb 18, 2011 | Heating & Cooling
After blackout, furnace won't come back on. Checked breaker
Sometimes a blackout can cause a surge to your unit. You will need a volt meter to test the transformer. But first, look for an auto type fuse, pull it and check it. If it is fine, test for 24 volts at the transformer.
Feb 02, 2011 | Goodman GMS80904BNA Open Flame Mid-Size...
Nothing will run. have 120 volts befor transformer nothing any where else
you need to make sure you have 24 volts out of the secondary of the transformer. if you do, make sure that your thermostat is calling for cooling. you'll have 24 volts between the y and c terminals on your board at the furnace.
May 16, 2009 | Ruud UBHC Air Conditioner
be sure the fan setting on the stat is set for auto, not on. in this mode the fan should only run when there is a call for cool or heat.if the fan continues to run check at the control board to see if you are getting 24 volts low voltage between green and common. if you are then the stat is bad. if youaren't then your electric control board is possibly bad. a lot of gas furnaces fall into a failsafe mode when a sensor or function fails and the blowers stay on 24 7. you may well have several problems from what you are saying. if you turn everthing off and start a new cycle for heat the first thing that should fire up is the induced draft motor , then the ignotor, then the gas valve. you can check each item with a meter , generally 120 volts to the induced draft motor, then 120 volts to the ignitior, the 24 volts to the gas valve. then ignition and 120 volts to the motor. most furnaces have a heat terminal and a cool terminal on the board. common to heat should get 120 volts on a call for heat after the sequence of operationb has taken place. 120 volts should be sent to cool terminal on a call for cool. a continueous blower is a sign of a failed safety. perhaps the motor failed and the safety opened and the motor was replaced but the safety never reset?. look at all the little micro temp sensors around the burner. they are like little breakers and need to be pushed in to reset . usually like a little stem that pops out from a metal or plastic dic. some are size of a quarter, some the size of a dime.
Oct 29, 2008 | Heating & Cooling
A carrier furnace
check the relay
the primary should have a low resistance
there should be a distinct click when 24 volts is applied to the primary
the secondary should be conductive when the primary is energized (contactors can corrode)
not a solution something to check
Oct 02, 2008 | Heating & Cooling
Heating & Cooling Logo
142 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others