Ducane furnace code 3 pressure switch . no blockage . switch ohm reading good, replaced broad. checked volt reading on call for heat from the broad and both volt reading on both broad is much less than 120 volts. on hsi glow system lock out after 3 tries

Posted by on

1 Answer

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    Superstar:

    An expert that got 20 achievements.

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

  • Ducane Master
  • 2,458 Answers

Pressure switch is bocked inside try a small drill bit to clean down the connection tubes and blow it out after , check hoses are not blocked or split ,

Posted on Feb 18, 2012

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Furnace will not stay lite, flashes pressure valve closed


Too much or too little pressure. Check for air blockage or an ice blockage inside or outside the house. Were flames good color when lit?

Nov 12, 2014 | AO Smith Miller / LSI / Home / Nordyne...

2 Answers

Brand New Ducane Furnace with Multiple Error Codes


Check your drain line. It appears that water is not draining and backing up into the furnace. Is there a drain trap? If not or if there is no vent on the drain line there can be a vacuum created when the furnace is running and it actually pulls water back into the furnace and when the inducer shuts off it releases the vacuum allowing the water to drain.

Dec 17, 2012 | Honeywell Furnace Air Pressure Switch...

1 Answer

I have a goodman furnace GMP100-4 REV B..about a year ago it was not working. The fan would start but it would not ignite. We found out we need a new ignitor and it was a good quick easy fix. Now a ye


Any light flashin on the control board? If not then look for a small fuse blown on the board. See lights a flashing count them flashes

A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

Nov 29, 2011 | Goodman Heating & Cooling

1 Answer

I have a Goodman GMP 125-5 furnace. It had a 3 light code i replaced the presure switch now it is giving me a 1 light code please help


A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
themobilian_3094.jpg

Oct 28, 2011 | Goodman Heating & Cooling

1 Answer

I have goodman GMP series furance the furnance and gas comes on and fires up then goes out flame sensor is good what else could be wrong


Improper ground from control to burner.
Incorrect electrical wiring, check polarity.
Tubing partially clogged between inducer and proving switch.

A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

Oct 18, 2011 | Goodman GMS90703BXA Heater

1 Answer

Suddenly not working im not sure if there even is a pilot to be lit


Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

Feb 03, 2011 | Goodman Heating & Cooling

1 Answer

My central heating is on lockout and the burner is with red light


A sampling of various codes on a furnace

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your Goodman furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

Dec 02, 2010 | Heating & Cooling

1 Answer

Coleman home heater stops working fault code "limit switch open"


How do you test a pressure switch and other limit controls?
This is for people who are experienced with electrical equipment and the use of a Volt Ohm meter. *Please never by pass a pressure switch or limit control. The pressure switch and limit switches are there for your safety. You would test by setting your volt meter to "Volts AC" and test the rollout switch by placing one meter probe on one terminal of the rollout switch and your other meter probe to a good ground. Have the red probe touching the top terminal of the rollout switch and the black probe touching a ground (body) of the furnace. You should be getting 25.85 volts which means the rollout is good on the top terminal. I would next test the bottom terminal of the rollout by touching the red meter probe to the bottom terminal on the rollout switch and the black terminal to ground. If I get 25.85 volts on the bottom terminal the rollout is good. If I do not get any voltage on the bottom terminal then the rollout has tripped and can be reset (if equipped) by pressing in on the little button or replaced. If your rollout switch is tripped you probably have a stopped up heat exchanger or a leaking heat exchanger. I would recommend calling in a service technician to find out why the rollout switch tripped. If you have an open limit control either the furnace has over heated or the limit has gone bad. Problems that would make a limit open up would be dirty filters, dirty evaporator coil causing a restriction in the air flow or a slow blower motor (check the capacitor on the blower motor to make sure it is good). A weak blower motor capacitor will cause the blower to run slow and eventually fail. Pressure switches, and limit switches can be tested with a meter in the same manner. With the furnace calling for heat you can test each of the terminals on the pressure switch to ground to make sure the pressure switch is closed. You should be getting between 24 to 28 volts from each terminal to ground if the pressure switch is closed. If the pressure switch is open you either have a stopped up vent, drain line (if you have a condensing furnace) or bad pressure switch.

Nov 27, 2010 | Coleman Heating & Cooling

3 Answers

Ducane high efficiency propane furnace, pressure switch problem


A short cycle heat cycle indicat a pressure switch replacement was needed. This did not fix the problem. the problem was in PCV line since the end was filled with slugs and cause the line to backup with water. When this happen the system would stop asking for gas. the water would leak out and it would restart. The problem was fixed by cleaning value at end of PCV. This released the water, two quart of water, that was back up causing problem. Curious if a filter change indicator was providing a clue that was missed?

Jan 28, 2009 | Ducane 436 inch 2 - 2 burner Grill

Not finding what you are looking for?
Grilling Logo

Related Topics:

548 people viewed this question

Ask a Question

Usually answered in minutes!

Top Ducane Grilling Experts

paulcarew

Level 3 Expert

2458 Answers

yadayada
yadayada

Level 3 Expert

75077 Answers

Dan Webster
Dan Webster

Level 3 Expert

8220 Answers

Are you a Ducane Grilling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...