Question about Honeywell Heating & Cooling
I installed honeywell R845A 1030 as per diagram on its cover - hot blk to #1 and circl load to 3&4 and aquastat load to 6&5 putting the blk conductor of both load wires on the odd # terminal i.e. 3&5 -I only have juice across the line conductors and nothing on other two even when system is calling for heat--i took cover off same product someone else installed in this basement [on another identical gas fired hot water boiler] and the hot black was jumped across the 4&5 terminals and the blk conductors from the loads were tied to 3&4 and the neutrals were all tied together from the pigtail from the #1 line terminal - the owner of that apt said the system works fine for over 2 years - can some one straighten me out
  • 331 Answers
@living inthe50's
i think that a pictorial representation would be better as one cannot get the exact process.......
i would be really better if u could give the diagram .........
Posted on Oct 24, 2008
  • 3,037 Answers
The diagram is wrong as I believe you are grounding one, wire it exactly as you saw it wired in the other basement and let me know what happens. If you can post a picture of the diagram if it doesn't work, then I can see what is the difference better.
thanks and good luck
I have a hot water system that uses baseboard heaters with two thermostats. the pump is activated through a Honeywell R845A. Is the R845A the problem?
Using that thermostat on a boiler system requires a relay to be installed. like the Taco sr-501 or an Argo AR-822
Jan 27, 2016 | Thermostats Heating & Cooling
I have installed honeywell aquastat relay per instruction manual on my dunkirk xeb-4 lp boiler furance with honeywwell ignition unit s8610u but it wont ever start the exhaust fan checked everything several...
If aquastat wirings are ok, and control module had been set up properly, the the furnace should start.
Check if bypassing the control the furnace starts, if it starts then check aquastat wirings.
If it depends on the furnace, check the valve, the safety sensor and the ignitor.
Here is the guide to set up the Aquastat control:
Guide to Setting & Wiring Heating System Boiler Aquastat Controls
Sep 13, 2008 | Honeywell Heating & Cooling
I have a Weil mcLain Gold gas furnace and the Amtrol WH-7L hot water maker. I heat alot with an indoor woodstove and if the furnace is not being used I cannot get any hot water. However, when the furnace...
You should download & review the manual for Amtrol Boilermate products here.
Page 12 of the manual begins examples of wiring between the Boilermate and aquastat (also gas valve and multi-zone relay), that is usually mounted on the boiler. In order to use it correctly, you'll need to determine which aquastat (or other device) your furnace has. You should be able to locate this info on the inside of the aquastat cover. The Honeywell Triple Acting aquastat is very common and looks like this:
The cover is held by a single screw on the top, bottom or front (depending on the model you have). The inside should have wiring information along with the model number. Compare the model number with the wiring diagram for it in the Boilermate manual.
Make sure power is OFF before continuing.
Check that all wires are terminated and undamaged. Make sure terminal screws are not loose. Tighten any found to be loose.
The orange wires are connected to a switch that is normally OPEN but CLOSES to start the boiler when the hot water has cooled. It is also used to operate a "power vent" for a minute or two both before ignition and after flame out for safe pre and post purging of the combustion chamber of furnaces that lack a chimney.
Blue wires are connected to a switch that is also normally OPEN but CLOSES to start the boiler when the hot water has cooled. When the switch connected to these wires is CLOSED, ignition happens instantly. There is no delay for purge so when these wires are used to start a furnace, it should be one with a chimney - not a power vent.
For additional help with your particular installation, you will need to provide information concerning the wiring diagram in the manual that applies. Otherwise, there are simply too many variations to walk through.
I suspect that the switch(es) that are connected to the orange (or blue) wires - or the device (aquastat or multi-zone relay box) is not operating as expected to start the furnace.
The troubleshooting section of the manual that seems to apply best is the section: Boiler will not operate when calling for hot water on page 27 (if you want to try some of their suggestions while waiting for additional replies).
I hope this helps..
Nov 29, 2012 | Heating & Cooling
Fuse box for 1990lincon town car need a diagram lost cover need to no were the fuse are for the brakes
15 amp It could be two different fuses #1 which is on the bottom right(1st row) away from the circle or #7 which is in the second row middle
0(the circle)
8 7 6 9
4 3 2 1
Aug 18, 2011 | Dryers
First My sister inlaw has a 3/4 recirc line. used the by pass h&c under last faucet to use cold as recircu line. Note acutal 3/4recirc is in kitchen but even thou closer to water htr. it is last for...
I don't understand everything being asked, so add a comment any time.
Problem1 is excessive electric bill.
Suspect is new 120Volt Taco recirculation pump.
Look at motor nameplate for amps and watts and HP. Taco pump is usually robust 1/3 HP which is 252 watts or same as running four 60 watt light bulbs.
If pump runs 18 hours per day x 252 watts = 4536 watts or 4.5 Kilowatts per day
Buy a kill-o-watt meter that plugs into outlet, and plug Taco pump into the meter for 48 hours.
This will give you total watts used for that time period.
1000 watts = 1 kilowatt.
Electric bill is probably 12 to 20 cents per kilowatt.
So if Taco uses 4.5 kilowatts per day, that is $.54 to $.90 per day multiplied by 30 days.
So cost is $15 to $30 per month.
Problem2 is Taco runs too long.
Taco operates either by thermostat or by timer. You choose which mode by using slide switch that is usually located under the timer dial. Set switch to TIMER to use timer, and ON to use thermostat, and off to turn TACO off.
If Taco is set for thermostatic operation, the Taco might be defective. Or there could be crossover problem at single handled faucet.
Another problem could be air in the water line: install air vent.
Jul 17, 2011 | Taco 1/2" 006 BC4-TAC Circulator Pump/...
How do I wire a Honeywell R8182H and a R845A controls to a R7184A
use the h an the 845 1 zone to the h an 1 zone to the 845
Dec 17, 2009 | Heating & Cooling
Looking for simple wiring diagram to wire ******** aquastat
What are you fanning??? the fire?
Do you have a circulator that circulates when the water is up? Many controls have a AUX connection ... wire the AUX to your fan --- alaternatively, wire directly fron your circulator connection to the fan.
I hope I understood your question ...
Let me know what happens.
Oct 16, 2009 | Honeywell International Honeywell&...
My john wood hot water tank over flows through the relief valve every 3 - 6 months. The hot water is too hot and I can't seem to adjust the Aquastat L4103 on the hot water heater to a good temperature....
There should be plate on the front of the hot water heater tank.. Pop that off..
There might be some insilation to move and you should see a set screw for adjusting the temp..
If there are no indications for hotter or cooler - then do a 1/8 turn to a 1/4 turn counter clockwise..
Hope this helps !I
rate me good ;o)
Jul 14, 2009 | Honeywell Heat/Cool Thermostat
Durabrand Db1200 installation
As per our chat session I said I would be back while I search out your here is your information;
Aug 24, 2007 | Durabrand DB1200 CD Player
Heating & Cooling Logo
298 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
Paul Carew
vance jones
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others