Ruud 90+ Model UGRA 10EZAJS is started up in the the morning by setting the tstat to 66 F (actual room temp 59-60 F). Furnace starts and runs fine for a long time (30-40 minutes) as the home temperature climbs to about 63 F - 64F. Then the furnace goes through what appears to be a reset where the flame drops out, the air circulates for a few minutes then the flame tries to come back on. The gas valve cycles open/closed several times but only a partial flame comes up. After several tries the furnace goes into safety lockout and will stay down for 30 minutes. Then the furnace restarts and runs fine the rest of the day. The problem only appears in the morning at first startup. I thought it might be an overtemperature issue. I checked airflow and it is at around 1500 SCFM. Gas (propane) pressure is good. Flame sensor was replaced, gas valve is new. Orefices and gas distribution tubes are clean. Pressure diaphragm switches are new. Furnace filter is clean.
  • 1 more comment
  • Robert Kulick Feb 12, 2012
    Removed and sanded flame sensor. Yellow light came on several seconds after ignition. I will observe the furnace further over the next few days to see if that solved the trip out problem.
  • Robert Kulick Jun 09, 2018
    There were multiple issues at play.
    First the condensate drain was clogged and the condensate trap as well. Had to disconnect condensate hoses and blow out any blockage. Then I flushed with hot water. Then I added a small shot of bleach to keep bacteria from growing in the lines.
    Second the Condensate buildup flooded the pressure switches used to sense if the purge blower was operating. I had to clean these out and reinstall the switches
    Third the wing tips between each burner flam were dirty so the flame would not propagate to the flamerod. I had to remove the burner assemply and remove any soot from the wingt placing a razor thru each wing tip slot.
    Now the furnace works perfectly. No control board issues either.
Check for condensation buildup in the Induction Blower housing. The condensate tubes or canister may be blocked and causing the diaphragm switch to trip the unit out causing the burners to shut down.
Posted on Nov 09, 2012
    Top Expert:
  • Ruud Master
  • 8,673 Answers
When unit fails check gas pressure maybe too much demand
Posted on Jun 20, 2018
  • 3 Answers
I would change the thermostat it maybe the issue if that doesn't help check the control board on the furnace
Posted on Feb 11, 2012
    Thermostat is working fine. On startup the IFC board shows 2 green lights (OK & PWR). After about 15 minutes of continuous heating the yellow (flame light) comes on. I have seen the flame come up on a partial burn on occasion. When that happens the gas valve shuts down and the cycle repeats. On the 2nd try there is a full burn and the furnace blower kicks on. Gas pressure is 10-11"WC (propane).
I have 1f86-344 White & Rodgers thermostat that both the heat set temp and the actual room temp read 63 degrees it is actually 69 degrees on 4 therms at same location. Is there a charge for answer?
download the manual. step 6 will let you calibrate the tstat up or down 4 degrees max. does get you closer, be sure to seal hole in wall where wire comes through. possibly use air duster on tstat internal parts.
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
Apr 09, 2018 | Heating & Cooling
Can Rudd Model # UGRA-10EZAJS be converted from natural gas to LP gas?
all gas units can be converted between gas types
the main changes are the jets and the air shroud positions
it is a job for an accredited gas fitter and not for amateurs
Nov 10, 2015 | Kitchen Ranges
What is the AFUE of my Rudd Achiever 90 Plus with model number UGRA-07EMAES
Per Rudd's website and also as the name implies, the min rating is 90. The 90+ can be as high as 93 but is stated as "plus" to cover the many possible installation scenarios which will impact overall efficiency of the unit.
Sep 11, 2014 | Heating & Cooling
Remote is inaccurate
did you change the batteries ?
Dec 07, 2013 | Mitsubishi Heating & Cooling
Is a 8 yr old furnace never out of the box the same as a new 2012 furnace same model?
Its not the same but the manufacturer should honor the warranty if you are the registered owner
Jan 28, 2013 | Heating & Cooling
I have RUUD furnace with build in coil for air conditioner and Weather King compressor outside of my condo. ALL EQUIPMENT IS 4 YEARS OLD I didn't have any problem with heat at winter, but in summe
When you remove the panel to the unit it turns off the power to it. The reinstalling the panel will reconnect power and allow the unit to reset. So the cheapest and easiest thing you can try is to replace the thermostat. Make sure you see how many wires you have connected to your existing tstat and buy near the same thing. It's possible that the tstat is acting up, not allowing the unit to cool when the temp demands. And turning off power is resetting the tstat as well as the unit. It will be hard to troubleshoot with the info provided so a new tstat will be worth a shot. Hope this helps!
Apr 07, 2017 | Ruud Matching Split Air Conditioner
RUUD 90 Nat Gas unit, >15 yrs old. T-stat calls for heat, nothing happens. I can place the fan in manual ON, & after a few mins. the warm air starts to circulate. If I leave the fan in auto, the...
sounds like you shorted out the heat anticipator in the tstat. try jumping red to white at the tstat wiring terminal and have a friend stand near the furnace to see if it cranks up immediately. if it does the problem is more than likely in your tstat. be sure to blow out any dust in the workings of your tstat. this is 24 volts and shouldn't hurt you but try not to short it out to the common or other wires.
Nov 24, 2009 | Heating & Cooling
I have a Ruud 90 Plus Model UGRA furnace and blower starts immedi
NO BECAUSE THE BOARD IS TELLING THE FANS TO STARTARE THE CONTACTS FUSED TOGETHER OR STUCK IN THE CLOSED POSISTION CHECK THIS FIRST
Aug 10, 2009 | Heating & Cooling
Message: "in recovery"
the "in recovery mode" is refering to a thing called energy recovery management its one of the features on your tstat what it does- when you are using the program on your tstat the "in recovery" starts your unit early so if the tstat is set to be 70 degrees at 8 in the morning when 8 o clock hits it will already be 70 degrees in your house you can turn this feature off if you want in the installation setup codes
Jun 24, 2009 | Honeywell Programmable Thermostat Heater
Ruud heat pump outside unit trips circuit breaker
Check your wiring between the contactor and compressor for a short to ground, or check the compressor windings for short to ground.
With the Tstat off, the contactor should be open so the only way for the compressor to be trying to do anything is if the 110 volts from the unbroken side are traveling through the compressor to ground. Since 110v is not enough to run it, the overload is kicking it out, cooling off, and repeating the cycle. When you kick on the Tstat, the contactor is supplying voltage directly to ground without going through the resistence of the compressor windings and kicking the breaker.
Post back and let me know what you find.
Nov 20, 2007 | Ruud Central System Air Conditioner