Locating a high limit or rollout switch on a ADP garage heater
How do i "jump out" the switch?
  • Heating & Co... Master
  • 3,280 Answers
By pass the limit with some wire and two croc clips to form a bridge across the two connections
Posted on Feb 11, 2012
2 Suggested Answers
  • 3280 Answers
SOURCE: ADP Garage heater model CUHP - 45A-3 LED flashes 4
Hi jump out the switch high limit or rollout it should start up
Posted on Mar 19, 2010
Igniter isnt lighting
IF YOU LOST POWER WHEN FURNACE WAS RUNNING IT TRIPPED ROLLOUT SWITCHES AND POSSIBLY THE HIGH LIMIT . IN CENTER OF ROLLOUT SWITCHES IS A LITTLE RED BUTTON THAT YOU RESET . YOU CAN ALSO TRY FINDING HIGH LIMIT WITH POWER SHUT OFF TO FURNACE PULL BOTH WIRES OFF HIGH LIMIT AND USE PAPER CLIP TO JUMP BETWEEN THE TWO WIRES MAKE SURE YOU DONT SHORT OUT AGAINST ANY METAL WHEN YOU TURN BACK ON IF IT WORKS YOU NEED A NEW HIGH LIMIT SWITCH.
Jan 08, 2014 | Coleman 7990-319p Evcon Gas Furnace...
RAYPAK RP2100 HIGH PRESSURE LIMIT
check gas pressure then replace highlimit rollout switch if ok replace hi limits in header
May 04, 2012 | Raypak Rp2100 Digital 336k Btu Propane...
Heater clicks but does not ignite.
no spark ?? see if ignitor is clean , clean flame sensor check high limit on heater , jump out pressure switch see if this works or jump out limit , check you have gas to heater might sound silly but can happen
Jan 15, 2011 | Mr. Heater Natural Gas Garage Heater -...
Coleman home heater stops working fault code "limit switch open"
How do you test a pressure switch and other limit controls?
This is for people who are experienced with electrical equipment and the use of a Volt Ohm meter. *Please never by pass a pressure switch or limit control. The pressure switch and limit switches are there for your safety. You would test by setting your volt meter to "Volts AC" and test the rollout switch by placing one meter probe on one terminal of the rollout switch and your other meter probe to a good ground. Have the red probe touching the top terminal of the rollout switch and the black probe touching a ground (body) of the furnace. You should be getting 25.85 volts which means the rollout is good on the top terminal. I would next test the bottom terminal of the rollout by touching the red meter probe to the bottom terminal on the rollout switch and the black terminal to ground. If I get 25.85 volts on the bottom terminal the rollout is good. If I do not get any voltage on the bottom terminal then the rollout has tripped and can be reset (if equipped) by pressing in on the little button or replaced. If your rollout switch is tripped you probably have a stopped up heat exchanger or a leaking heat exchanger. I would recommend calling in a service technician to find out why the rollout switch tripped. If you have an open limit control either the furnace has over heated or the limit has gone bad. Problems that would make a limit open up would be dirty filters, dirty evaporator coil causing a restriction in the air flow or a slow blower motor (check the capacitor on the blower motor to make sure it is good). A weak blower motor capacitor will cause the blower to run slow and eventually fail. Pressure switches, and limit switches can be tested with a meter in the same manner. With the furnace calling for heat you can test each of the terminals on the pressure switch to ground to make sure the pressure switch is closed. You should be getting between 24 to 28 volts from each terminal to ground if the pressure switch is closed. If the pressure switch is open you either have a stopped up vent, drain line (if you have a condensing furnace) or bad pressure switch.
Nov 27, 2010 | Coleman Heating & Cooling
Heater not working
yor heater has 3 high limits and a flame rollout switch(aka thermal fuse). be advised that bypassing safetys is not recommended and is dangerous.these component failures are symptoms. we need to find causes.if limits are failing look at sooted or possibly a nest on your heat exchanger. if its a flame rollout problem look at obstructed burner or oriface.
Jun 22, 2009 | Pentair Minimax Ch 400,000 Btu Propane...
Arcoair central heat /air conditioning unit
The blower motor kicks on when there has been a 24 volt control failure.
This usually means that a limit switch has tripped.
Most likely that would be a high temp limit switch or a rollout switch.
First, make sure the filters are clean. and the evap coil is clean. If eaither are dirty/clogged, it will partially block airflow, causing the furnace to overheat, causing the high temp limit to trip.
A rollout switch typically trips for three reasons.
1 flame rollout into the burner compartment due to poor airflow.
2 overheating af teh metal plate the rollout is mounted to, due to dirty, old, rusted components.
3 a bad limit switch.
If your unit has an LED light, count the flashes and it will hepl popint out the problem.
(locate the wiring diagram/flash code list, and correspond the flash count, with the code.)
First, check filters.
Jan 14, 2009 | Heating & Cooling
Rollout Limit Switch Keeps Tripping
have someone check the gas presure most likely too high no more than 11