Ducane furnace fault code 2
Furnace starts ignition cycle stops with fault code 2 = flame failure lockout.
mrgrzz
  • 88 Answers
SOURCE: Where is flame sensor on my old oil furnace?
Thanks for your question,
The flame sensor eye is located just under the transformer, it is looking straight down the burner assembly to where the burner chamber is at, you will have to remove the entire assembly to get to it, first make sure the power is off, remove the transformer, then remove the entire burner assembly from the furnace cabinet, once removed you can see the flame sensor window, use a clean oil free cloth to clean it, it would probably be a good idea while you have it out to replace the burner nozzle, as over time they will clog, I hope this helps you fix your oil burner, let us know and rate this please, thanks again,
mr.grzz
Posted on Jan 27, 2009
  • 3 Answers
SOURCE: flame rollout sensor keeps tripping
The flame rollout sensor is a rather important safety feature that ideally only trips when there's an overtemperture outside of the combustion chamber. I'd encourage you to get a better quality tech in ASAP to check for a cracked heat exchanger, gas overpressure, restricted airflow (changed the filter lately?), maybe a blocked condensate drain if this is a high efficiency furnace. If the sensor was replaced and it's still tripping, you've got a potentially dangerous overheating issue that you don't want to try to bypass.
Posted on Mar 20, 2009
koolbreezes
  • 540 Answers
SOURCE: goodman gmp075-3 gas furnace and the flame cycles for 4 sec
JUST SAND THE FLAME SENSOR LOCATED IN FRONT OF THE LAST GAS PORT.
Posted on Dec 02, 2009
kingbrizzle
  • 407 Answers
SOURCE: Fault Code on Dayton Gas Furnace
This happens when the furnaces tries to light to many times and doesnt succeed. If you stand in front of the furnace while it is coming on, you will be able to hear the problem. If its an electronic start, there will be a clicking sound, followed by the gas valve opening to start it. If it has a pilot light, make sure it is lit, then listen for the gas to come out, it will make a hissing sound. If no gas is coming out, first double check to see if the gas is turned on to the unit, if it is, then its possibly the gas valve. Oh, if it is electronic, and you hear gas, but dont see a glow inside the furnace, or no glow or gas, it could be the ignite. Hope this helps.
Posted on Dec 28, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: 80% ducane furnace makes several attempts to
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Check for 24 volts across the gas valve terminals!
Posted on Mar 04, 2010
Error code= two red flashes, lockout/ no flame
Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...
www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com
7 Tips and Tricks to repair your Furnace DIY - YouTube
? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check
Jan 23, 2016 | Heating & Cooling
Tractorman44 thanks but misunderdstood husband! When thermostat turned up the fan comes on before flames ignites. Plenum heats and furnace runs.
If the fan comes on first, then the flame ignites, it USUALLY indicates there is a problem in the ignition process of the furnace. Most new manufacturers have the adjustable 'time off' sequence for the blower, and most initiate a call for the blower to run within a pre-determined amount of time AFTER a call for heat has been established. ALSO, and this is where I think the problem is, the ignition sequence starts immediately upon a call for heat. If there is a heat ignition failure, it will attempt a restart. USUALLY, they allow 5 restarts within a certain timeframe then the circuit board locks out the heat sequence until it is reset by cycling the power or cycling the thermostat manually.
What I think is happening with yours it that your ignition sequence is experiencing a 'flame failure' upon a call for heat....then it re-establishes the ignition sequence, which takes another 30 to 45 seconds. During this time, the blower automatically starts (because the allotted time has expired) and blows COLD air because of the initial flame failure. In the meantime the ignition sequence establishes a flame on the second or possibly the third try and then you feel the warm air.
IF this is the case, ultimately what will happen is that the furnace will continue to experience 'flame failure' and eventually fail to the point of 'flame failure lockout' and you will have no heat, but the fan could possibly run continuously.
At any rate, without being able to be there to troubleshoot and test components physically, this is just a calculated and reasonably reasonable guess. What it is telling you is that you probably need to contact a reputable, reliable service organization to give your furnace a good going over before it lets you down on a good cooooold night!!!
I hope this helps you understand the basics of what happens within the system and bear in mind, this is a 'generic' sequence and possibly NOT the exact sequence of your particular furnace.
Oct 01, 2015 | Heating & Cooling
Amana Air Command 90 furnace LED light blinks 3 times pause 3 times
TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.
2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.
3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.
4 BLINKS Open limit switch Verify continuity through rollout switch circuit.
5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.
6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.
8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.
9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.
10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.
12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
Nov 11, 2013 | Patton Electric Patton PUH680-U Electric...
Ducane furnace is always problem with gas valve lockout at fault code blink two times.
use sand paper clean that flame sensor that should take care of your problem
Dec 28, 2012 | Heating & Cooling
This is a Dayton gas furnace model GF9S120D20UP11H and i am getting a flash code of ignition lockout due to recycles. how do i fix it? i have taken all the filters out and washed them and also checked...
Usually a lockout code means it tryed so many times and then it locks out or stops. First, when a furnace is locked out you have to kill the power to the furnace to reset the lockout. I don't know this furnace but there are manual resets around the burner called flame rollout switches that have buttons in the middle that have to be pushed back in. Also the power vent has to come on when the furnace gets the signal from the thermostat. This is proven by a flow switch with a rubber hose on it. The next step is a 30 sec. purge, then the igniter glows or sparks and then the main burner comes on.
The other switches are hi limit on the front wall of the heat exchanger. That might get you started. If you have anymore questions rspiak1@cogeco.ca
Jan 13, 2011 | Dayton Gas Furnace Heater
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
Fault code says pressure switch lockout
This more often than not, indicates that your pressure switch is gone and needs to be replaced. Watch the YouTube video for a fuller explanation and heed the warning to use OEM parts! Gas Furnace Pressure Switch Failure and Replacement Amazon com gas furnace parts
Feb 06, 2010 | Heating & Cooling
Armstrong upflow,unit works intermittent problem,call for heat nothing happens,error code of 5 blinks then 6 blinks. i have no manuel, and the panels dont have the codes on them. anyone have access to the...
Armstrong
FAILURE CODES
LED Status Fault Description
Off
No Power to the System Control
Steady Flash (11 or more flashes with no pause)
Normal Operation (Standby or call for heat)
2 Flashes
Pressure Switch Closed When It Should Be Open
3 Flashes
Pressure Switch Stuck Open 30 Seconds or Longer After Call for Heat (System in 5-minute delay mode before next call for heat). On/off switch in "off" position during a call for heat will generate this code.
4 Flashes
Open Limit Switch or Limit Switch Circuit
5 Flashes
Flame Sense Signal Sensed Out of Proper Sequence
6 Flashes - pause - 1 Flash (see Note 1)*
Soft Lockout Type 1 (Failure to light within 4 trials for ignition)
6 Flashes - pause - 2 Flashes (see Notes 1 & 2)*
Soft Lockout Type 2 (Flame sense lost during run)
6 Flashes - pause - 3 Flashes (see Notes 1 & 2)*
Soft Lockout Type 3 (Pressure switch opened during run)
6 Flashes - pause - 4 Flashes (see Notes 1 & 2)*
Soft Lockout Type 4 (Limit or limit circuit opened during run)
6 Flashes - pause - 5 Flashes (see Note 1)*
Soft Lockout Type 5 (Flame has gone away after Error Code 5)
6 Flashes - pause - 7 Flashes (see Note 1)*
Soft Lockout Type 7 (Self-check failure)
10 Flashes* - SV9520H8034 only
Line Input Voltage Polarity Reversed
Dec 12, 2009 | Coleman Heating & Cooling
Meaning of rudd furnace trouble codes
Error Codes
A green LED indicates system faults
Steady On: System OK
Steady OFF: Board control fault or no power applied
1 Flash: Ignition failure (control in one-hour lockout)
2 Flashes: Pressure switch fault, fails open (switch is
stuck open)
3 Flashes: Limit switch open (main or auxiliary)
4 Flashes: Pressure switch fault, fails closed (switch is
stuck closed)
A yellow LED indicates flame status
Steady on: Normal flame is sensed
Flashes: As flame weakens, frequency of LED flashes
increases
Dec 12, 2009 | Heating & Cooling
GMP050-3 heater, gas turns on and lights for 5-7 seconds and just as thr igniter goes dim the gas shuts off. after 3 cycles the erd LED flashes on/off at a 1.5 seconds on and 1.5 sec off Gary
After the gas turns on, it is the flame sensor's job to see that ignition took place and send 24v to the gas valve. If it does not do this, the gas valve shuts down as a safety precaution. After 3 tries, the furnace will go into "lockout" and will not let it attempt to start again. The lockout can be resolved by turning off the power to the furnace for a couple minutes and then turning it back on. Sounds like the real problem is a faulty flame sensor not sending 24v to the gas valve. Sometimes they can be cleaned with a piece of sandcloth. This will cure failure to recognize the flame due to carbon build up on the sensor. Otherwise, the sensor will need to be replaced. Hope this helps!
Dec 16, 2008 | Goodman Heating & Cooling
Heating & Cooling Logo
836 people viewed this question
Top Heating & Cooling Experts
Paul Carew