Question about Haier Energy Star ESA3183 Air Conditioner
Heat Pump/Furnace Trip Circuit Breaker
My system will run for a while, heating nicely, and then suddenly trip the circuit breaker on the furnace. Occasionally it also trips the circuit breaker in the main panel for the heat pump. I have paid almost $300. to have the Heating and AC company check this out, and they cannot find anything wrong. Perhaps I have been asking the wrong folks? It does not due this upon start-up; just seems to heat for a while, and then randomly kick off. The Heating AC folks just wanted to sell me a new system, but it seems to me that if this is all that is the matter, it should be something that can be repaired. The system is getting up there, about 14 years old, but has been very well maintained, and had a new defroster put in last year as well. Can you help? I hate to call someone else, and incur another $100 service charge with no fix! Thanks so much.
  • 2 more comments
  • nancydb Oct 22, 2008
    Hello, and thanks for the response! Here's the answers I could find out: The furnace max overcurrent (Carrier brand) is 3.0. Protection 15. Max amp fuse 50/60.
    There are two 40 amp fuses (tied together) at the panel for the Heat Pump. There is also two 50's (together) for the furnace in the garage (also at the panel.) What tends to blow are either the breaker directly on the front of the furnace itself, or that one plus the two 40's for the Heat Pump (NOT just the one for the Heat Pump, which makes me think that it is when the heat pump and furnace are working together.)
    Interesting thought about the defroster ....I can't recall if this was happening prior to that being replaced.
    On the heat pump itself (also Carrier) I read: Max Fuse 40; Breaker 40; Min Circuit Amps 23.3.
    I did not take apart the panels on the heat pump to see about the defroster rating...would this be accessible if I did?
    There doesn't seem to be a pattern when tripping. This morning it ran for about an hour, then tripped. Then ran for 3 hours without tripping. Last night, 1/2 hour then trip. It is all over the place.
    When the service tech was here last year, he checked to be sure that there were no spikes in power at the furnace. I was concerned as well because our electric bill went through the roof when this began happening. I am thinking now that it could perhaps be a circuit board issue, and that he should have changed out the circuit board on the outdoor heat pump unit, especially given the quadrupling of our electric bill. What do you think?
    I SOOooo appreciate your assistance on this. Thank you!
  • mht123 Nov 28, 2008
    I am having the same problem in cold weather.
    Our Goodman 12 year old (3 ton) heat pump "on heat" runs for 10-20 minutes (we get warm air) BUT then blows the circuit breaker switch in the house (Not outside fuses).
    This heat pump is a heating (and cooling) unit for the upstairs bedrooms only - and is frequently not used, so we just discovered this problem?
    My guess is that the unit starts to work-gets warm- but for some reason starts to pull too much electricity and triggers the circuit breaker? Why do you think? 703-200-7469
  • glenball Jan 13, 2009
    I have a similar problem with an Amana heat pump. It is only 3 years old. This past summer the outside breaker tripped, it was reset and no problem. However, this past November with no particular pattern the breaker would trip after several hours or less or it may go for days. After inspecting the outside unit I discovered that a lead had not been secured properly to the contactor allowing the connection to arc. This was evident from the dark and chard wire and the dark color of the contacts. I have replaced the contact but this has not solved the problem. Within several hours of replacing the contactor the breaker tripped again. I am now at a loss!
  • alaspitfire Mar 25, 2009
    I have a similar problem but I notice it now when the weather is colder and the heating elements have to kick in.....it runs for about 30 minutes and the circuit breaker trips. I am being told it might need new heating elements. How much are new heating elements for an older Rheem.....just an approximate cost anyone?
Check the set screws at the panel and the furnace. May be a poor connection. Happened to mine... probably the installer.
Posted on Dec 05, 2009
My system will run for a short period and then suddenly trips the circuit breaker in the main panel for the heat pump.
I have a Goodman - 3 ton system about 8 - 9 yrs old. I'm being told that I need to replace the heat pump/air conditioner compressor?
What do you think?
Posted on Dec 07, 2008
  • 417 Answers
A few points of clarification;
What is the furnace circuit breaker rating in Amps?
What is the heat pump rating in amps or kW?
What is the defroster rating in Amps or KW.
How long has it been doing this vis a vis the insatallation of the defroster?
Is there any pattern to the tripping i.e does it happen when a fan starts or stops?
Posted on Oct 22, 2008
  • ashburton Oct 23, 2008
    Here are some thoughts on your situation;
    The breaker is furnace and heat pump breakers seem to be tripping on overload rather than earth fault. It's unlikely to be a cicuit board fault.
    If your electricity consumption has quadrupled some thing is running more constantly than before. Does this relate to the time the new defroster was installed?
    Regarding the defroster rating iI wouldn't take anything apart to check it but can you get the information from another source e.g the paperwork or the installer as it seems to me this could be causing you problem.
  • David Wagner
    David Wagner Mar 06, 2013
    I have the same problem. but mine only trips once every 2 weeks. a 60 amp breaker and only 30 amps going across the breaker. the 60 amp breaker in the unit does not kick off. which confuses me. they are in series with each other. I figure both should breakers should kick
Any ideas as to why the panel breaker for my Goodman CPE24-1AB heat pump would immediately trip when the air conditioner is turned on?
Without looking up the specifications for this heat pump, I cannot be certain, but I expect the operation to provide cooling may require more power than when heating. You probably can find the specifications online for this unit. As you probably know, power is measured in watts and is calculated by voltage times current. This also is likely to be 240 volts operation. If you take the specified power on cooling and divide by voltage (240), that will indicate the current in amperage that will be required to start it. Your circuit breaker is set for current and needs to be a higher current than is required. If that is the problem, you can buy circuit breakers at Home Depot or Lowes. You have to remove the front panel of your breaker box and snap out the circuit breaker. To be safe it would be good to turn off the main breaker switch before you open the front panel and remove the circuit breaker for the heat pump. Should your calculation of current required be less than the rating of the circuit breaker, that implies a malfunction of the heat pump in the cooling mode and would require a service call to the local representative of the heat pump manufacturer.
May 16, 2014 | Goodman CLQ36AR49 Air Conditioner
I have a new furnace and the breaker keeps tripping (20/30). It is a bryant westinghouse box. I think 200 amphes
1) You got a FIRE truck coming.
2) Wire is too small.
Problem is NOT circuit breaker.
3) Both 240Volt appliances on same breaker is a hazard, especially if space available in 200 amp service panel for more breakers.
4) Usually each 240V appliance has separate breaker.
5) Circuit breaker trips because of High heat on the wire.
If wire gets hot, it will start a fire inside the wall.
Electric code requires wire-size match breaker-size.
6) If you put larger amp breaker on same wire that is getting hot, then wire will get hotter.
Result: FIRE truck middle of night with folks jumping out window in glass-cut bare run across yard.
7) Each appliance has volts and watt rating on label.
EVERY appliance has label.
8) For example stove might be rated 8000 watts and 240Volt.
8000 watts divided by 240 volts = 33.3 amps
Stove would require 40 amp breaker and 8 gauge wire.
9) How to figure it out:
http://waterheatertimer.org/Color-codewire.html
http://waterheatertimer.org/How-to-install-a-subpanel.html
10) Do same calculation for new furnace.
12000 watt furnace divided by 240 volts = 50 amps.
Use 60 amp breaker and 6 gauge wire.
11) Summary: fixya wants you to be safe, and buy stuff showing in the ads.
Use a bigger breaker ONLY when bigger wire is also installed.
Call furnace installer, the installer should know to check safe wiring before installing.
Nov 04, 2012 | Bryant Westinghouse Bqc Quad Circuit...
Breaker trips after bout 5 minutes
Breakers trip because of heat.
When heat from wire exceeds breaker rating, it trips.
Something is causing heat on the wire, wire is too small for the amp draw, there is short circuit, or breaker is bad.
Replace breaker and/or test wire.
Put amp-meter on wire and read amp draw through wire.
Amps cause heat. That's why high voltage lines from power station are high-volt-low-amp so there is no heat loss with long distance transmission, until transformer at home converts electricity to lower volts and high working amps with enough power to run electrical devices.
Same is true for AC and DC circuits.
If amp reading on wire exceeds rating on breaker for length of time, then breaker will trip.
The fact that the breaker lets current (amps) to flow for a period of time before tripping is because the breaker is probably rated for slow-acting, or it takes a while for amp draw to heat the wire.
Following image shows amp-meter that clips over wire to get amp reading.
http://waterheatertimer.org/pdf/Which-is-best-gas-water-heater.pdf
Oct 31, 2012 | Electrical Supplies
Who made the the idea?
Please check the currents draws and check your breaker size. If your furnace always trip off, check the system for malfunction. Normally manufacturer install the breaker with specific standard to protect your furnace from damaged
Feb 05, 2011 | Electric Circuit Breaker Kit for Furnace
Have Challenger Type C 2100 circuit breaker in residential home electrical panel. Manually turned to off position and now cannot turn back on. Pops back to off position. Also says HACR type and common trip...
First HACR is heating, air conditioning,refrigeration. So in other words you could use it on an electric furnace or air conditioning.
IS this the main breaker for the panel? or for and electric furnace. I'm assuming its for the furnace, perhaps back up heat for heat pump. See if there is another disconenct on the furnace, turn it off and see if the breaker resets. IF so you have a short or overload in the furnace.
If' it IS the main for the panel, turn off all the other breakers in the panel, and try to reset the breaker. If that works, turn the other breakers back on one at a time. IF it "POPS" then it is tripping. Don't keep resetting, find the problem.
Jul 19, 2010 | Challenger Connecticut Electric UBITB-A230...
30 amp breaker trips intermittently
It sounds like this circuit breaker is worn out and needs to be replaced. good luck
Jan 19, 2009 | Siemens 2 pole 30 amp breaker
Furnace keeps tripping circuit break
Furnace. To confirm use an Ampprobe or other brand ampmeter and see how much current is being drawn. If it is more that 80% of the breaker rating, it si for sure the Furnace.
Jan 10, 2009 | Haier Energy Star ESA3183 Air Conditioner
Electric furnace wire heating up
you should have a 3- conductor # 6-3 copper wire running to this 60 amp breaker @ the furnace to the panel if this is not the case you should replace this with a # 6 as of now as it is a fire hazard as it is and needs to be fixed at once , # 10 -2 wire is only good for 30 amps and a 60 amp breaker will not trip under fault condition and you could have a fire , if you need further assistance on this let me know and i will try to help
Jan 09, 2009 | Electric Circuit Breaker Kit for Furnace
Haier Energy Star ESA3183 Air Conditioner Logo
5,910 people viewed this question
Top Haier Heating & Cooling Experts
Tom Chichester
Matt
Matt
Level 1 Expert
Vincent Schnittert
Vincent Schnittert
Level 1 Expert
Are you a Haier Heating and Cooling Expert? Answer questions, earn points and help others